Need some help venting a shed roof

Rolcor | Posted in General Discussion on February 14, 2016 06:57am

Hi All,

New guy with an old problem. We are have a little issue with condesation / water damage coming from our shed roof.

The roof is a 2/12 cathedrale with spray foam insulation. We had intended to spray foam tight to the underside of the roof sheathing but just prior to pulling the trigger our insulator informed us that the City of Calgary requires a 1″ air gap between insulation and sheating. For no good reason, as far as I’m concerned. However, after considering the expense of “correcting” it after the fact if the codes officer did come down on us we opted to install the 1″ air void by spacing ridgid insulation down from the sheathing.

Most of the roof is porperly vented at the fascia and the ridge but one section is a shed roof with windows above and I couldn’t come up with a decent solution. So, I did nothing while I considered the options. We are now having some water damage issues around the windows in the wall below this roof. It only occurs during freeze thaw cycles and I’m quite sure that we are just getting condensation / icing on the roof nails / underside of sheathing and then melting when the roof warms. I dont think that we are driving any condensation from the house into the air void space as we have 6″ of spray foam and vapour / air barrrier between that and the drywalled ceiling.

I think I have two real options. First, spray foam the void. Second, try to get a vent in at the top. 

I’ve attached sketches of the exisitng condition and what I think may work as a vent (and a photo of the roof) Hoping to get some input / feedback from the pro’s here. Thanks, Ro

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. calvin | Feb 14, 2016 08:26pm | #1

    Ro

    Are you confident with the existing roof/wall flashing and the window installation?

    1. Rolcor | Feb 14, 2016 10:27pm | #3

      Thanks for the reply, I initially thought it was a leak from the exterior too. I'm 100% confident with the window install. Tyvex and redseal all lapped correctly.  Roofer was good and I think flashed everything correctly, I can't see any issues, sealed all flashing pentration, etc.

      Everything holds up well in the rain / snow, I only have issues in freeze - thaw conditions. My only other thought is that I'm some how wicking water back up under shingles when there is snow on the roof and it's warm outside. Only a 2/12 slope but it does have full ice barrier under lay.

      I'm reasonably sure that its condenstation though but then again........

      Thanks, Ro

  2. DanH | Feb 14, 2016 08:49pm | #2

    Nothing is "attached".

    Nothing is "attached".

    1. Rolcor | Feb 15, 2016 12:34am | #4

      Hmmm, I'm trying . When I click the boxes at the bottom of my original post the picture coems up fo rme. (I gather not for you?) but I can't seem to imbed the photo's in the post. I tried seaching for help on uploading photos but got side tracked on searching on how to search......? I must be missing something here. 

      Edit: Wait, I think I got it. Sketches are sideways but I'm geeting closer 

  3. User avater
    deadnuts | Feb 15, 2016 08:37am | #5

    2 problems:

    1. Dimensional shingles not recommended for 2/12 pitch roof. Probably not warranteed either.

    2. Double vapor barrier detailed in your roof assembly notes. I'd like to see a full roof assembly section that shows no chance of air leakage and thus, potential for trapped moisture or condensation.

    I'd resolve both before considering resolution of venting detail. Personally I'd advocate with your local inspector for a properly executed unvented roof assembly. I believe Green Building Advisor website has details for this in your climate zone.

    1. Rolcor | Feb 15, 2016 01:39pm | #6

      Thanks for the input. Shingling the 2/12 roof was debated at length prior to install. Roofer was / is confident of his install solution. He has been back to have a look. I'm only shying away from this as a possible casue as I have issues at 4 windows, different joist lines. So i would need to be an issue across the entire roof. (not saying thats not possible).

      I've attached a detail of the roof to wall for reference. 

      1. User avater
        deadnuts | Feb 15, 2016 07:42pm | #7

        few more questions...

        1.nominal 6" of open or closed cell spray foam?

        2. what constitutes your vapor barrier? Is it continuous with little to no penetration or leak points around outlets or fixtures?; even at ceiling-to-interior wall junctures?

        3.what climate zone are you in?

        1. Rolcor | Feb 15, 2016 10:53pm | #8

          1. "6 closed cell. 2. 6 mil

          1. "6 closed cell.

          2. 6 mil poly that meets Canadian air / vapour barrier standards. Little to no penetrations. There are no potlights in this ceiling and only 5 octangon boxes. All boxes have air barrier wraps around them and tie back into the air barrier with tuck tape or acousta seal and tuck tape. 

          3. Not sure of the correct answer to this, Semi arid, Energy star Zone B. Calgary, AB Canada.

          I removed a top window trim today and a small section of drywall wall and ceiling. There is no evidence, at that location, that water is traveling down between the closed cell insulation and the top of the air barrier. I think I have the water path figured out as coming down the ceiling joist hangers at the perimeter beam. Still don't have the source figured out though.

          I'd  like to try and get a camera/light in the void space some how. Maybe a drain camera? Also think that some thermal imaging may help out. 

          Also, I'm considering trying to seal the soffit vent to see if the problem presist. I not sure why it hadn't dawned that I can still be getting air changes in the void with just the bottom vent. Of coarse I'm the guy that didn't put in the top vent so....I don't really need to finish that thought....

          I very much appreciate the help and consideration you are giving this.

          Ro

      2. mark122 | Feb 16, 2016 07:18pm | #9

        Just about EVERY shingle manufacturer warrants shingles on a 2/12 (the low spectrum of low slope). Diamond deck, winter guard and shorter shingle exposure. (certainteeds guidlines in case some clown wants to dispute it)

        did you confirm with your local office about the air gap? Your air gap is killing you. Even if you can succesfully retrofit a vent on the top side it may not be enough to keep the condesantion from forming and freezing. 

        what is the size of that shed roof? 

        with a vented roof, to little ventilation causes these kinds of issues (and others) that will slowly decay your deck, rafters and eventually attached framing members.

        i would be inclined to speak with your code official, explain your situation and explain your proopsed system (hot roof) for the shed only. 

        I wonder if your insulation guy was confused by this:

         R806.3 Vent and insulation clearance. 

        Where eave or cornice vents are installed, insulation shall not block the free flow of air. A minimum of a 1-inch (25 mm) space shall be provided between the insulation and the roof sheathing and at the location of the vent. 

        which does not mean you have to have a 1" air gap across your entire roof deck.

        1. Rolcor | Feb 16, 2016 10:02pm | #11

          Codes officer and city of calgary are very confused on this point. I did a lot of research on unvented roofs prior to decided on a non-vented system. After discussing at lenght with the city I decided to back down and install the 1" air space. Strangely enough the city has no code for venting tthe space. Which is just slightly more ridiculous. Long story / process short we tore off all the non-vented fascia, used ridgid foam to generated the 1" gap and Coravent at the soffit and ridges.

          I should point out that this is city code, not provincial or federal. "Yeah I feel your pain, next town over sprays tight to the deck all the time, just not Calgary" Quote from the spray foam crew.... 

          Shed roof is approxiamtely 30 x15. However, the entire house (2700 sf bungalow) is built the same way. About 700 sf of roof is 2/12 rest is 5/12. I have no known issues on the low slope front roof or 5/12 roofs which are vented top and bottom. 

          Thanks, Ro

        2. User avater
          deadnuts | Feb 17, 2016 07:12am | #16

          explanation?

          mark122 wrote:

          Your air gap is killing you. Even if you can succesfully retrofit a vent on the top side it may not be enough to keep the condesantion from forming and freezing. 

          If you believe this is the case, then please explain why.

          1. mark122 | Feb 17, 2016 09:29pm | #17

            Ill talk to you like i do to my 5 year old, although im pretty sure he is smarter than you are.

            The OP is all but certain there is no roof leak. What does this mean Dumbnuts? no water infiltration.

            If there is no water infiltration, and there is moisture, this most likely means there is some degree of air leaking from the conditioned space. Because Calgary has an absurd code requiring a 1" gap, this gives that hot air a cavity to wreak havoc in that little space. causing condensation probablly mold and eventually rot.

            This 1" gap is not vented properly so this space is not moving air as it should. When the vented space does not move the required air thtough it to properly it can not preform as a vented roof should.

            Even if the OP can get some sort of vent at the low end of the roof, if he can not get the appropriate amount of ventilation it will be a futile attempt.

            I get it, you read an article and speak on the issue as if you pattented the product, but, seriously...stick to houzz house wives man, im sure they are easily impressed.

          2. User avater
            deadnuts | Feb 17, 2016 10:12pm | #18

            The only "air gap" wreaking

            The only "air gap" wreaking havoc is the one between your ears.

            Look at the section. Perhaps you are unable to read drawings and notes, but the O.P. has indicated 6" of closed cell spray foam directly on the underside of his roof sheathing. This is no different from a typical "hot roof" insulation detail that is unvented. The "gap" is above the sheathing and is exposed to outdoor temperatures. There is no "hot air" pocket here as that zone is outside of the thermal envelope (and appears to be code), thus likely avoiding dew point temperatures. He has also indicated a complete 6 mil taped vapor barrier (thus air barrier as well) on the inside of his building thermal envelope. What is this tremendous amount of hot air and water vapor traveling through? Oh yeah, according to your "gap"  it's traveling through the 6 mil poly AND the 6" closed cell foam-- which is also a vapor barrier. Right.

            If you want to argue that the vapor barrier is compromised, then you'd have to accept the argument that the bulk water plane could also be compromised. However, I see that your engine has no spark; that may be impossible.

          3. mark122 | Feb 18, 2016 07:19am | #19

            REALLY

            Gap above the sheathing? WHAT are you talking about.

            Ill leave you with your own thoughts...

            "If you're absolutely sure you don't have bulk water intrusion issue from above, then I'd agree that your only avenue for moisture damage is condensation. Since heat energy moves from hot to cold and moisture moves from areas of high density to low density, warm, moist indoor air is naturally wanting to move outdoors where its generally colder and drier this time of year. Possible air leakage points and areas of inadequate thermal envelope would be prime suspects for your problem.

  4. User avater
    deadnuts | Feb 16, 2016 09:19pm | #10

    While some shingles may

    While some shingle manuf. may warrant their shingles on a 2/12 pitch, what their warranty is based on is the use of their underlayment membrane. This is expensive and you're putting 4 holes in it per every three tab shingle. Sure, you can argue that each faster is "self sealed" by the membrane; but not an argument I would bet on long term for this shallow of a roof.

    Anyhow, just because you may be able to monkey dance toward a warranty, doesn't mean it is good practice. In fact, Paul Fisette, editor at JLC writes in a Q&A section in  April of 2001: "I would never install shingles on a 2/12 roof, especially in an area where snow falls. In fact, I have had numerous problems in northern climates with asphalt shingles on 3/12 roofs. As a result of this experience, I would limit the application of asphalt roof shingles to roofs that are 4/12 and steeper. The National Roofing Contractors Association recommends that asphalt shingles be installed only on roofs with slopes that are 3/12 and greater."

    I believe that bit of good advice that is as relevant today as it was then.

    BTW, you don't show how your roof 3/8" sheathing is supported in your section.  I'm wondering if this could be a avenue for heat and vapor drive leakage. If you're absolutely sure you don't have bulk water intrusion issue from above, then I'd agree that your only avenue for moisture damage is condensation. Since heat energy moves from hot to cold and moisture moves from areas of high density to low density, warm, moist indoor air is naturally wanting to move outdoors where its generally colder and drier this time of year. Possible air leakage points and areas of inadequate thermal envelope would be prime suspects for your problem.

                

    1. Rolcor | Feb 16, 2016 10:38pm | #12

      Ahh, I see what you mean, I missed line on my detail, the 2x10 ceiling joist rides higher than the 2 ply 2x8 beam. 3/8" sheathing is nailed directly to the top side of the 2x10. I do appreciate the low slope shingle comments but i just can't see any signs of daming, damage, improper install that would trigger water in that many joist spaces. 

      You have me thinking about every possible area that I could be driving humid area up there and I'm coming up blank. Since my spray foam is over 5" it techically is an air barrier. Reading Green Building is what triggered us to add the poly air barrier. Just as cheap insurance more than anything else and due to the limited depth 2x10 (2x8 in the 5/12) I killed all potlights in house to prevent this. 

      Should also mention that the 2x4 walls are closed cell sprayed foam and air barriered. All windows are spray foam sealed.

      At this point I think I should try venting it. I'm working on a slightly simplier top vent detail but need to check some calculations. My vent at the top will be continuous so I think my calculation should be based on a bunch 14 1/2" by 15' roofs. Does that make sense? but, I have a feeling that I can't just apply venting calculations in a linear method.

      Again, any help is appreciated.

      Thanks, Ro

      1. DanH | Feb 16, 2016 11:02pm | #13

        It might be worthwhile wondering what your inside humidity is.  With the envelope so tightly sealed you could easily be hitting 60-70% humidity inside if nothing is being done to ventillate the structure.

        1. Rolcor | Feb 17, 2016 12:25am | #15

          I don't think that's my issue, most of time I'm down under 35 humidity wise. I have two, large hrv's that cycle with the furnaces plus they are interlocked to kitchen and main bath exhausts. So, I have a good amount of relatively dry, fresh air coming in. You made me run down and double check my humidifiers to see if anything went sidewise though!  Thanks for the input. Ro

  5. User avater
    deadnuts | Feb 17, 2016 12:00am | #14

    some additional thoughts looking at your roof wall section:

    1. You don't really have a continuous thermal break at your double x8 header. The lower part of beam seems uninsulated. Maybe your spray foam comes all the way down in actuallity, but it's not shown here. Anyhow, designing a sandwich layer of 2" rigid insulation between structural wood members may have been a good "belt and suspenders" approach here.  2- LVL's with structural screws cinching rigid insulation may have been worth looking into with your engineer in order to accomplish structural as well as thermal break integrity.

    2. You have metal hangers that are great thermal conductors at this beam area with ends having virtually direct exterior exposure . Could these conduits be sweating on the other side of your 6 mil poly and running out behind your interior trim?? I realize it's not a tremendous amount  of material exposure, but couple that with partial cold wood surface (beam) and warm, moist air migrating to that area and it could be enough to drip when it's super cold outside.

    Also, when its warms up outside (and has been relatively dry), you might want to hose test the roof to verify it's not a bulk water penetrating  issue. Can't hurt mimicking rainfall and I'm still not convinced it's not the problem with low pitch shingled roof.  Keep in mind that the only thing you won't be able to mimick with a hose is ice daming. If your underlayment membrane is at all compromised and warm air is leaking causing ice daming, those shingles aren't going to do a damn thing to keep bulk water out.

    1. Rolcor | Feb 18, 2016 11:50am | #20

      1. I agree with the thermal break comment. The house was built back in 1972, its was an extensive renovation but we did not get into large structural changes. Sprayfoam at the perimeter does actually roll down to the top sill plate of the wall.

      2. Also agree with the metal hanger, it's not ideal but I tend to think I get some sweating at best in the location. Plus, it just hasn't been that cold here this year. I do think the inherent space between the 2 ply 2x8 and the 2x10 ceiling joist is providing the pathway for the water.

      I purchased a borescope and hope to feed it into the void. As luck would have it they are calling of a full range of weather in the next few days. Warm and rain today and tonight, then sunny and cooling. Getting down to 6C below on Saturday night. Hopefully something will show up.

      If it works out I will post some pics. Thanks again.

  6. Rolcor | Mar 02, 2016 12:56pm | #21

    Deadnuts, thanks for not letting me overlook the bulk water possiblities....

    The other day it had not frozen over night and it started to rain about mid day. A small but steady drip formed at my exterior wall. So back up on the roof I go to investigate. Everything looks to be fine, I still had a band of snow and ice about mid way down the roof. My feeling now is that band is creating enough daming to drive some water up under the shingles, down though any penatations (roofing nails), ultimately traveling down the air void to the celing joist hanger where it has a path to the inside of the exterior wall.

    I guess I need to figure out / install a roof finish solution. While I'm at that I will install the venting as well.

    Any thoughts on a  "shingle looking" metal roof on a 2/12 slope?

    1. User avater
      deadnuts | Mar 02, 2016 06:12pm | #22

      I'm not familiar with the material to which you refer. Send a link.

    2. DanH | Mar 02, 2016 06:42pm | #23

      Be aware that any metal roof without standing seams will have the potential for backflow due to damming on low slopes.  Its simple geometry.  Either prevent the dams or use a continuous membrane.

      1. User avater
        deadnuts | Mar 04, 2016 10:00am | #24

        be aware of bs

        DanH wrote:

        Be aware that any metal roof without standing seams will have the potential for backflow due to damming on low slopes.

        Yet another bit of false information from someone who usually has no idea what he's talking about. There are plenty of metal systems installed on low slope (less than 3/12) roofs that are not standing seam. Most will have an interlock detail that is also joint sealed. The sealing material can be any one of 7 types of liquid sealants; which may include a semi-solid form offered in "tape".

        In my opinion, any roof with a pitch of 2/12 or less deserves special detailing and installation; and it definitely would not involve dimensional asphalt shingles. This is evidenced in the problems you're having here.  Most code officials will accept manufacturer installation speciifcations and ICC reports during plan review or inspection for whatever material you're using. Most manufactureres for low slope roofing materials will also indicate a solid warranty for their product. If it doesn't have one that you or your customer are comfortable with, then don't use it; even if your roofer claims it's the best thing since sliced bread. Chances are he's only going to stand behind his installation, not the material.

        BTW, why doesn't your roofer stand behind his (apparently) recently installed and leaking roof? If he installed your roof according to low slope installation guidelines which support any warranty (if their is one), then he should have no problem making a warranty claim on the material he used.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels

Listeners write in about fireplaces and ask questions about sharpening hand tools, easier wiring upgrades, and fixing cedar siding.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels
  • FHB Podcast Segment: Hand Tool Sharpening Tips
  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data