New Electrical Service

DoRight | Posted in General Discussion on September 8, 2012 02:20am

Ok, new electric service going in.  Electric company requires the owner to install meter base (freestanding, not on buildign).  The base is to be five or so feet from the transformer.

I do not know what this entails.   If this is a DIY project I will do the research, perhaps with help from you, to find out what is entailed.  IS this a DIY project? 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. calvin | Sep 08, 2012 04:05pm | #1

    Is this for your temp. power?

    if so, your electrician should have some temp boxes available.

    1. DoRight | Sep 08, 2012 04:16pm | #2

      Meter

      Temp service?  Yes and No.

      The meter will permanently be set on a post at teh transform and not on the house.  It sounds like you can have an outlet or two at this meter and it makes sense that this can be your temporary power for the buiding project.

      As for my electrician?  That is my question do I need one for this project?  I feel confident in doing much of the actual house wiring and maybe the panel wiring, but not the final hook-up.  The meter install sort seems like teh project falls closer to the same type of project of the final panel hook-up so I am not sure it is a project for me.  However, then again, it is just the meter and the transformer would not be live at that point.  SO is it DIY project or not?

  2. oops | Sep 08, 2012 04:29pm | #3

    Elect. Service

    Around here, a temp. service or as you describe here would require it to be permited and inspected by  AHJ.  Therefore you would need a licensed  electrician.

    1. DoRight | Sep 08, 2012 07:39pm | #4

      where is around here?

      Where is here?

      Here you need a permit, question is do you need a licensed Electrian?

      1. oops | Sep 08, 2012 10:46pm | #5

        Elect. Service

        Here is DAllas/Ft. Worth.  You can't get an electrical pemit unless you are licenced. Maybe out in the boonies. I don't know.

        Also I wonder what effect it might have on ones liability or insurance  for a DIY installation.

        I suppose I should mention that I am a GC and not an electrician.  That is why I always call my friendly sparky.

  3. gfretwell | Sep 09, 2012 02:40am | #6

    I will bet you need a permit but if you are building a house you probably already have one. Just amend the permit for this meter base and I am guessing a service disconnect.

    If they are OK with you doing the rest of the electric, they will probably be OK for this. It all depends on how your local building people feel about "owner/builder".

    There are plebty of issues in doing this to code and if you are not sure you know them all, you probably should get an electrician.

  4. SpeedyPetey | Sep 09, 2012 09:03am | #7

    IMO this is absoluely NOT a DIY project.

    1. DoRight | Sep 09, 2012 01:23pm | #8

      No plan to argue

      Why is this not a DIY project?  The power company hooks up the power from teh transformer to the base.  Are splinters from teh post that much of a hazard in your opinion?  Just joking.  It seems like the project is sinking a post and attaching a meter base?  Am I wrong?  The other question is what meter unit do I want or need, and for that it might be easier to pay a guy fro his advice.

      Thanks again.

      1. DanH | Sep 09, 2012 02:01pm | #9

        I don't think you need to continue demonstrating your ignorance -- you've done the job just fine.

        1. DoRight | Nov 14, 2012 02:00pm | #20

          Cake walk

          I think since this project was a ridiculous cake walk someone else on this board is demonstrating ignorance and lack of skills and or confidence.

      2. DoRight | Sep 09, 2012 02:47pm | #10

        IT is always possible to get an education, but sometimes it is just not worth spending the time.  Of course there are always teh sub 60 IQ types like Dan you can not comprehend learning anything new or just not capable.  Of course we just pray for the handcaped sub 60 iq types, at least I do.  SO very sad.

      3. SpeedyPetey | Sep 09, 2012 03:00pm | #11

        reply

        DoRight wrote:

        Why is this not a DIY project? You asked a question and I answered it.

         DoRight wrote: The power company hooks up the power from teh transformer to the base. Not usually. 

        For underground most places require the contractor to bring hte service lateral to the transformer pad. IMO this is NOT a DIY job.

        DoRight wrote: It seems like the project is sinking a post and attaching a meter base?  Am I wrong? Well, if you want to oversimplify it to the highest level, yeah. Thing is you have to wire it and provide grounding/grouding electrodes.

         DoRight wrote: The other question is what meter unit do I want or need,This is something your POCO can tell you.

        We don't even know what state you are in, HOW can we tell you what meter pan you need???

        1. DoRight | Sep 10, 2012 01:11pm | #13

          Thank you for your respectful answer

          Thank you.

          I know for a fact that the power company hooks up the transformer.  As for oversimplificaion, yes I did.  Yes there are ground rod(s) and conduit.  Today I received a drawing from the power company as to what is required.  It looks pretty straight forward.  I may do a bit more homework if I have time or I might just sub it out as that is probably the easiest way to get advice as to what box is best, do I want an outletor outlets at the location, should I plan to run a well directly from this location, etc.

          Thanks again.

    2. DoRight | Nov 04, 2012 07:44pm | #14

      Meter Base in

      Update for all who care.

      I put the meter base in, main breakers, ground rods, and outlet circuit for construction, no thanks to teh naysays who typically don't think anyone who does not call themselves a "professional" is capable of operating a screwdriver, and thanks to all who attempted to help.  This was a no brainer, with a little homework, primarily the code details.

      Got permit on-line, very easy.

      The inspector was awesome, nice and helpful.

      The biggest problem was deciding on 200 amp or 200 amp.  About half electricians said an all electric house "should" be ok with 200 the other said go 400 amp.  Electric furnace people said 400 amp, but then again they really don't know about that kind of stuff.  The inspector said I made a safe bet with 400 amps.  I still "guess" I went for overkill ... but then I am not sure ....

      So for anyone considering this project go for it.  Piece of cake.

      1. User avater
        xxPaulCPxx | Nov 05, 2012 03:07pm | #15

        The biggest problem was deciding on 200 amp or 200 amp. 

        Really, that doesn't sound like much of a decision!  :)

        1. tsenator | Nov 05, 2012 11:59pm | #16

          xxPaulCPxx wrote:

          The biggest problem was deciding on 200 amp or 200 amp. 

          Really, that doesn't sound like much of a decision!  :)

          I'm Glad he went with the 200Amp -- I think that was the right choice ;-)

          1. DoRight | Nov 12, 2012 01:52pm | #17

            Did I really type that?  "200 vs 200".  Ok, LOL.

            I was amazed how difficult it was to get definitive advice on 200 vs 400 amp service.  I talked to several electricians.  Some said 200 was plenty for an ALL ELECTRIC house.  Then I said "even with a 120 or 130 amp furnace, and the said ... "well that is a big furnace" as if they had never heard of such a thing.  And the furnace "people" said they would size a furnace at 130 amps ... so.  Some electricans said they would go with 400 amps, but did not really go into any detail.  One guy at the power company said 200 was fine and another guy said you "might" go with 400. 

            Load calculations information on the web was all over the map as well.  Some suggested taking heating, cooling, hot water, and cooking appliances and adding out the total load and others more or less said take 40 percent of it.  It seemed to me that it would not be that unlikely a situation for to have a cold Christmas day with teh 130 amp furnace running, a goose in the 50 amp electric furnace, guest taking showers (40 amps) using hot water, and then the well pump kicks on, while others are watching teh Christmas day parade on the big screen.  And yet no one could tell me why that senerio did not warrant 200 PLUS amps.

            Pretty strange.

            So 400 amps it is.  Not a big big cost difference when doing the work yourself.

          2. gfretwell | Nov 12, 2012 05:27pm | #18

            As often as not 400 ends up being 320 and that is not unreasonable with 130a of fixed electrical heating load.

            The only real way to know is to do a load calculation. I think there are Excel templates out there to make it easy.

            This is an old one I have but I have not played with it much

            http://gfretwell.com/electrical/2005loadcalculator.xls

          3. User avater
            xxPaulCPxx | Nov 14, 2012 03:38pm | #22

            When I upgraded my service panel (from 100 to 200), I did it gradually, cutting circuits over from one panel to the other when they were ready.  The first one I did was the largest ciruit I had, the 40 amp line to my electric oven.

            I disconnected the 40a wire in the old panel

            I cut the flex conduit and added the length I needed to jump from the old panel to the new panel

            I ran new wire from the 40amp breaker in the old panel to a 40 amp breaker in the new panel... and labled it TEMP POWER CUTOFF

            I installed a new 40 amp breaker and ran it to my oven.

            I then gradually cut over all the other circuits in my house

            Eventually, my entire house was running through that single 40amp circuit for about a month.  Never any fade or browns, and I run alot of computers and have a heavy laser printer.

          4. DoRight | Nov 14, 2012 09:15pm | #23

            Did you have ...

            Did you have a 130 amp furnace running on that 40 amp breaker?  a 130 amp furnacne and a 40 amp hot water heater. perhaps?

            It is interesting how one can get anacodotal (spelling?) stories about what can be done, but no one can explain how it can be ok to run a 130 amp furnace, a 40 amp hot water heater, a 40 amp oven, and xx amp well pump, and x number of lights and TVs simultaneously on a 200 amp service.  This does not seem like a difficult question for anyone claiming (understanding you did not make that claim) to be an electrian, but it is!  Bizzare.

            It is easy to understand how you can have x number of breakers in your box totally well over the amperage of teh service.  Obviously many many items are not running simulataneously.  You may have several lighiting circuits and small appliance circuits which total your service enterance amperage, but you do not have every light and every outlet running at the same time.  However, it is more than possible to be running furnance, heating water and cooking a turkey all at the same time. ?????????

          5. User avater
            xxPaulCPxx | Nov 15, 2012 03:46pm | #27

            I think the real curve ball for you is actually efficiency.  In my case, I doubt I ever ran all 4 electric burners on HI and had the oven up at 475 and then did a bunch of other things simutaniously.  The line I ran had to accomodate that, but barring that particular event there was still plenty of room on the line, apparently.  Much to my surprise I might add - I fully expected to be resetiing the breakers fairly frequently.

            I'll bet that 130 amp furnace is variable speed, and variable temp too.  While it may use the full 130 for a second while it is warming up the coils on max AND starting the blower moter on max... it probably settles back to a much reduced run.

          6. DoRight | Nov 15, 2012 07:07pm | #28

            I bet you are right about the furnace draw.  I beleive I even attempted to have a thread here asking if a 130 amp furnace actually drew 130 amps and or when.  No good information was collected, which was par for that question ask of various sources.  This is what I mean by hard to ferit out.

  5. Scott | Sep 09, 2012 03:38pm | #12

    I did my own meter base and wired the house under a homeowner permit. I had an inspector that absolutely hated homeowners and did everything he could do to discourage and frustrate me. So I had to read lots, study hard and make sure everything was absolutely perfect. I had pulled 15 to 20 permits before that so I had some background experience.

    You could pay a pro to do the service, meter base and install the main panel. Then you could so some or all of the branch circuit work. You'd still save lots of money because the branch circuits are were all the work is, and you'd gain valuable experience for the next job. And you'd get to watch and learn from the work the pro does.

  6. junkhound | Nov 12, 2012 05:45pm | #19

    Easily DIY in localities that let HO pull the permit and do the work.

    Most poco have detailed guidelines on what they require (e.g. 3" sch 80 pvc for 400 A service, with 24" wide trench and dirt 24" away, etc. etc. )  Puget Sound energy here in PNW has very specific homeowner guidelines.

    WA state constitution has been interpreted that HO are allowed to do own work on home they are living in, your state or locality may be different.

    An electrical service is NOT rocket science.  There are also many guidelines on the most common DIY 'mistakes' that inspectors flag, you can find them on the internet.

    First hit on search for "common homeowner electrical mistakes" on bing:

     http://electrical.about.com/od/electricalbasics/tp/commonelectricalmistakes.htm

    Have at it!

    1. DoRight | Nov 14, 2012 02:10pm | #21

      thanks

      Thanks, I will check out the link.  That type of information is the exact kind of stuff I think about;  do inspectors care about what type of accorns you use, or the type of outdoor outlet covers, or how many staples you use on the ground wire, etc.  All the little stuff.  The devil is in the details.  As it turned out with this project,  I did enough homework to keep me out of trouble, ... 3 inch conduit vs 2 1/2 etc.  All this stuff the pros know or have been caught by an inspector before and don't make the error again.  For the DIY you have to get alot of detailed information.  Lucky I enjoy it.

      I enjoyed the experience of figuring it out including, for the most part, getting ideas and questions form members of this board.  It also gave me a great deal of comfort with the potential of working with my particular inspector again.  I think he was a very helpful guy and will be available for code questions as I move forward.

  7. IdahoDon | Nov 15, 2012 09:35am | #24

    I call bs on this post - talking about electrical service like an easy diy project is not only  misleading, in many (most?) areas and all areas I've worked in power companies won't even consider allowing a homeowner to setup what you've allowed - not because it's rocket science, but because it's critical that everything is correct and since most diy types can't even figure out how to properly clean a paintbrush, this is more often than not screwed up.

    No this isn't a DIY project.  Yes anyone who is detail oriented and makes good decisions can figure out how to do it. 

    This reminds me of a discussions of DIY house jacking to replace a foundation.  No it isn't rocket science, but it's well beyond DIY abilities and sensibilities.

    As a contractor if a client wanted to take on this portion of the job I'd have to see something from them this is well above 95% of all homeowners before I'd consider it even if the local code would allow it. 

    1. gfretwell | Nov 15, 2012 12:40pm | #25

      It depends on where you live. In Florida you can do a service as a home owner as long as you get a permit and have it inspected. FPL just wants to see the permit and the inspector sign off. That is online now so they can do it before they even send out a crew.

    2. DoRight | Nov 15, 2012 01:50pm | #26

      Cake Walk Yes

      Call BS if you like.  However, this project was a joke.  That is just a fact.  If you must run around and scare everyone be my guest.  And perhaps in some areas, or in the case of some power companies, things might be different, but perhaps rather than scream the sky is falling people should ask questions to clarify the scope of the project.  Just telling please they can not operate (LOL) a screwdriver is not helpful except perhaps in inflating the ego of the naysayer.

      I went into this project with a healthy dose of respect of the potential problems and understanding of the areas in which I needed to gain knowledge, which turned out to be a LOT LESS then I first thought.

      I came and come to this board to hear from helpful people and also expect to hear from those who think special training is required to use a screwdriver.  Comes with the territory.

      Installing my meter base was a piece of cake.  The fact of the matter is the meter was required to be installed prior to the power company even plowing the power line in!  Totally a dead project!  I made this clear in my postings here.  Of course there are those who like to spout off and not actually read the posts and threads before commenting, perhaps an ego thing.

      My project entailed:

      Set posts.

      Hang meter / breaker box on posts

      Attach conduit from box to 24 inches below grade.

      Drill hole in box for ground wire

      Drive two ground wires in ground.

      Run and staple ground wire from box to groound rods.

      DONE!  (as it was I also installed a 20 amp breaker and outlet in the box and on the post)

      These are the facts.  If you would be frightened of this as a project for yourself what can I say.  I do not know your skill level with a screwdriver and sledge hammer.

      If people thought this project entailed hooking-up the transformer to the meter, and said that is not a DIY project, I could understand that.  However, one poster said my project was not a DIY project, when I asked why the question was ignored.  Sure glad I ignored him.

      This was a joke of a project and saved me 400 to 500 bucks.  And that is not BS.

      1. michaelinga | Nov 16, 2012 06:23pm | #32

        I'm with ya on this one. I built and remodeled houses for 15 years and became a pretty fair all-around builder. The main reason I got out is the frustration of every task becoming a weiner measuring contest if there was more than one guy involved. 

  8. DoRight | Nov 16, 2012 02:38pm | #29

    If you say so.

    All I can say is that was the case. You just don't have a clue as to what you are talking about IN MY PARTICULAR CASE.  I did the homework, and I did the work, I had it inspected, I had the pwoer company hook it up and they said my install was better than have of the professional jobs they energize.  You just don't have clue.  I know what I am talking about BECAUSE I ACTUALLY DID IT.  DONE!  Just a fact.  A no  brainer.  You can not know crapp about it since you were not there and know NOTHING about this jurisdiction.  Just a fact.

    Of course the power company had specs on the post, 6 x 6, PT, 3 feet min in ground, 4 to 6 feet above ground.  Now if you are not capable of reading then, in your case, you might have a bit more trouble.  Or if your IQ is sub 60 you could have a problem.

    The take away here is that anyone who wishes to do this job should do their homework and ignore the naysayers on this board.

    1. IdahoDon | Nov 16, 2012 10:30pm | #34

      I have no doubt you did just fine in your simple install - my beef isn't with that, it's that you are trying to tell everyone that a service hookup is easy.  It's complicated in situations where there are multiple choices that have significant impacts on the project as it moves further to completion, not to mention the impact meter site selection has in situations with multiple buildings fed from the location chosen and the gray area surrounding what is and isn't a "building" for this purpose (or what needs to be done to bring an existing outbuilding up to specs - complicated by historic district rules that govern what we can and can't do and the work arounds for situations we want to fall in our favor).   I take pride in working with a top electrican and architects to work all this out so the client gets the best solution.  The electrican by himself doesn't see the big picture, the architect doesn't understand electrical codes and how they are inforced locally to know how far things can be bent to what he wants aesthecially, and I'm the only one who works continously with the clients and the site to see things the others might not and make sure we're all working together.  I'm also the one who gets to be the bad guy and take the heat away from my subs when we don't get our way and have to call in favors at city hall or file formal complaints - find instructions for that in a code book!  lol

      1. DoRight | Nov 17, 2012 01:11pm | #35

        DIfferent in different locations

        No, I am not "telling everyone hook-up is easy".   I said my hook-up was easy, don't be afraid to look into your own situation.  And I repeatedly stated that it very well might be different in different locations.

        One of my beefs is that people repeatedly scream blooding murder "how this and that is not humanly possible for mer mortals".

        Second, beef might be that people don't read posts and make ASS-out of-U-and-ME about many inpertient things.  Many other people try very hard to ask clarifying questions, are very patient, encouraging, and helpful.

        I am sure in some locations permiting is nearly impossible for a homeowner.  But no one can assume this to be true, the HO needs to find out.  I knew without question that HO permiting was not a problem (said so repeatedly in my posts) and the power company did not bat an eye(and said so repeatedly) when they knew I was interested in doing the work myself.  As a side note, in my locale there is NO BUILDING DEPARTMENT; however, the state requires Electrical, Plumbing, and HVAC inspections.  HO permits are easily obtainable for all.  How gentle or helpful the inspectors are to HO is hard to say.  The Electrical guy was great!  And everyone's point here that if you are going to do some of these jobs yourself you need to get the facts, which is why I came and come to boards like this (not to mention I love to learn stuff which I do from you and many others on this board weekly)

        You make great points about the value of professional advice.  For example the location of the service enterance and future outbuildings etc.  This was a major consideration for me as well.  That is why the decsion about 200 vs 400 amp service was so hard.  I knew about load calculations, but could not find a consitent method, and PROFESSIONALs were strangely all over the map on the subject .  The professonals at power company suggested one thing and the professional inspector (who was a praticing electrician for 20 years) suggested the opposite. 

        So advice is great; however, in my experience most professionals just want to get the job done.  Not a reflection on you or anyone on the board, just my experience.  This could be for various reasons, one of which is that some customers "know best" and probably suggest to the contractor that they should mind there own business so contractors are taught to stay out of it.. Or doing it right costs more and they learn that is a losser for them.  I GET IT.   Then again I have gotten alot of advice from professionals which just plain turned out wrong.  Ask yourself how many times you dug into a remodel and cursed the remodeler before you.  How many times was that remodeler another "professional".

        A friend of mine asked me to replace her vinyl (spelling?) floor.  I looked at it and could see that in order for the entry door to clear the flooring without scraping I would have to take out the old flooring if not the underlayment, so I passed.  She hired a professional.  You guessed it!  He took the easy path and laid the new floor on top of the old, collected his insane pay, and moved on.  My friend then called me and said her door dragged horribly on the floor.  I then ripe her door out and raised it, redid the trim and siding, etc.

        Just sayin

        1. IdahoDon | Nov 17, 2012 08:31pm | #36

          I shouldn't have been so hard on you and I should have been more positive about it all - it was a stressful week, not that that's an excuse, but I'm not really as big an ass as I sounded.  I was reminded today to not sweat the small stuff.....and it's all small stuff.

          You are right about "professionals"  and I don't like the bottom 90 percent of them from all trades.  There is a brain drain in construction right now so it's a hard time for the industry and especially clients.   

          1. DoRight | Nov 18, 2012 05:13pm | #37

            That is big of you!  A rare post.  Thank you.

            I too should not rise to every ocassion offered.

            Thanks for your input. 

            I still really love your post about the two tone painting trick (That was you, right?)

  9. DoRight | Nov 16, 2012 02:42pm | #30

    You have no clue

    You are clueless.  I did what I said I did, had it inspected, and energized.  Just a fact.

    I don't doubt it is different in different areas, but for you to insist that my jurisdication is governed as is yours is to make you look dumb.

  10. gfretwell | Nov 16, 2012 03:38pm | #31

    I would be interested in any citations from the NEC to support all of those concerns about these posts.

    You are certainly trying to complicate a simple task with a lot of  bull spit

    1. DoRight | Nov 16, 2012 08:11pm | #33

      Thanks gfret

      Yes, the electricial inspector had me plumb my posts to within 3 nanometers.  That really was the hardest part of the job.  LOL.

  11. harryv | Nov 21, 2012 11:37pm | #38

    RE: Service panel size.

    I'm. surprised the utility company did not want load calculations in order to size the transformer.

    We have to supply this information to apply for electrical service.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Outdoor Lighting

Lighting up an exterior isn't just about ambiance— it's also about code compliance. Here is what the code says about safety and efficiency when it comes to outdoor lighting.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • A Postwar Comeback
  • With Swedish Arts & Crafts Precedent
  • Natural Simplicity
  • A Grand Rescue on the Coast

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • With Swedish Arts & Crafts Precedent
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data