NM in Conduit

Ms_Chips | Posted in General Discussion on February 6, 2009 08:51am

I may be mistaken but I think I have read that using NM wire (A.K.A. Romex) in conduits is forbidden by code. The reason I read was that in a conduit, it would not be able to dissipate the heat from the resistance inherent in all wiring.

Aside from the problem of pulling it through the conduit with bends, how is the heat buildup in a conduit anymore severe than running it in a wall completely surrounded by insulation? If anything, if the conduit were surface mounted, I’d think it would be better than buried in insulation.

Inquiring minds want to know 🙂

Teri

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    BillHartmann | Feb 06, 2009 09:09am | #1

    There is no restriction, I repeat NO RESTRICTION in using NM in conduit.

    And there are not adjustments for heat build up.

    For pulling NM through conduit it has to be figured as one big wire with the diameter the width of the NM. So that makes for fairly large conduit.

    But that it does not have to be that big when it is only used to sleeve for protection. Such as a drop down a basement wall.

    .
    William the Geezer, the sequel to Billy the Kid - Shoe
  2. renosteinke | Feb 06, 2009 06:59pm | #2

    Bill can repeat himself all he likes .... but this is a topic of considerable debate in the trade. This suggests that the answer isn't that clear.

    Not that it really matters; "designing to code" is itself a violation of of the NEC; Article 90 specifically states the NEC is niether a design manual nor a DIY guide.

    I'm pretty sure there's no law specifically prohibiting one from playing on the freeway while wearing a blindfold; yet that doesn't mean you should do it.

    Cutting to the chase, Romex is it's own complete wiring method. If you want to change to another method - such as pipe - why not use materials intended for use with that method?

    Also, contrary to Bill's assertion, running Romex in pipe can create situations that the NEC prohibits - such as running Romex in a wet location. Examine your reasons for wanting the pipe in the first place; chances are, this is a situation where you're not supposed to use Romex at all.

    1. User avater
      BillHartmann | Feb 06, 2009 07:34pm | #3

      "Also, contrary to Bill's assertion, running Romex in pipe can create situations that the NEC prohibits - such as running Romex in a wet location."No, the problem is not caused by having Romex in conduit. The problem is caused by using Romex in none approved locations. But you would have the same problems using other wires not rated for use in wet locations.The problem is not the conduit, but the wire..
      William the Geezer, the sequel to Billy the Kid - Shoe

      1. BillBrennen | Feb 06, 2009 09:04pm | #4

        Bill,I ran into what you spoke about in 2003 when I was wiring my Rastra ICF shop/apartment. The NM was run in the wooden floor system and then sleeved in EMT where it ran a short additional distance in a channel cut into the Rastra to reach the boxes. My inspector had a problem with the sleeving of the NM for heating concerns, and he wanted me to transition to individual conductors in the EMT. This would have peppered the ceiling with j-boxes and taken a longer time to do. However, he was okay with it when I explained that the EMT was only for very short runs at the boxes, purely for mechanical protection.When dealing with the AHJ, it sometimes matters a lot the way you describe what you plan to do.Bill

  3. ChrisComGC | Feb 06, 2009 11:56pm | #5

    The International Electrical Code doesn't say NM cable in not permitted to be installed in conduit.  It tells you what type of wire IS permitted to be installed in conduit and NM cable is not one of them.  The UL (Underwriters Laboratory) has not approved NM to be installed in a "raceway" therefore the folks that write the codes, the International Code Council say "NO".  It's all about keeping the wire within the temp. range of it's intended operating range by allowing air space around the wire.

    You can either use to correct wire (THWN or THHN) or you can strip the outer jacked off the NM cable. The wires inside the "Romex" are THWN.

     

    1. User avater
      BillHartmann | Feb 07, 2009 12:25am | #6

      "International Electrical Code "Where is the International Electrical Code used? I have never heard of it..
      William the Geezer, the sequel to Billy the Kid - Shoe

      1. timothale | Feb 07, 2009 02:05am | #7

        the last inspector I asked said if the run was 24 in or less he was ok with it... Longer he wanted a bushing on the end of the conduit to prevent mechanical damage and to strip off the sheathing.

        1. User avater
          BillHartmann | Feb 07, 2009 05:04am | #9

          I have the 2005 NEC in PDF form and searched for "24 in".And this here are the only 2 places that use 24 that might have any bearing on this.310.15 (B)(2)(2) Adjustment Factors
          (a) More Than Three Current-Carrying Conductors in a Raceway or Cable.Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(2)(a). Each current-carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.But that says that if you have more than 3 current carrying conductors in a cable or more than 3 current carrying conductors in a conduit or more than 3 conductors or cables are bundled together then you need to derate.But, in most case we are talking about only 2 or 3 conductors so whether they are in a conduit or outside a conduit and bundled they aren't derated.The other place is in calculating conduit fill."(4) Where conduit or tubing nipples having a maximum length not to exceed 600 mm (24 in.) are installed between boxes, cabinets, and similar enclosures, the nipples shall be permitted to be filled to 60 percent of their total cross-sectional area, and 310.15(B)(2)(a) adjustment factors need not apply to this condition." That says for for 24" or less you can go to a higher percentage of conduit fill.Again that is the same regardless of if it is a wire or cable.Now the NEC very clearly states that CABLE can be used in conduit. But there are many different types of cable. But the NEC never references any specific types.Now this is the section on calculating conduit sizes based on fill."(2) Table 1 applies only to complete conduit or tubing systems and is not intended to apply to sections of conduit or tubing used to protect exposed wiring from physical damage.Now this is from the handbook. It is not code, but explanatory information. "The maximum fill requirements do not apply to short sections of conduit or tubing
          used for the physical protection of conductors and cables. Cables are commonly
          protected from physical damage by conduit or tubing sleeves sized to enable the cable
          to be passed through with relative ease without injuring or abrading the protective
          jacket of the cable. The requirement of 300.5(D)(1) regarding physical protection of
          direct buried cables and conductors as they emerge from below grade is an example of
          conduit or tubing being used as a protective sleeve and not as a continuous raceway
          system per 300.12. However, a fitting is required on the end(s) of the conduit or tubing
          to protect the conductors or cables from abrasion. [See 300.15(C)."This would be what is typically used to sleeve a run down a basement wall. And this is how you treat a CABLE when calculating conduit fill.If you could not put cables in conduit then this would not be their."(9) A multiconductor cable of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter."Now here it specifically allows for NM to be run in conduit for protection.300.15 Boxes, Conduit Bodies, or Fittings — Where Required...
          Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable (NM), or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).
          ...
          (C) Protection A box or conduit body shall not be required where cables (of which NM is one type specified) enter or exit from conduit or tubing that is used to provide cable support or protection against physical damage. A fitting shall be provided on the end(s) of the conduit or tubing to protect the cable from abrasion.And from the handbook."Section 300.15(C) permits conduit or tubing to be used as support and protection
          against physical damage without terminating in a box. It also permits conduit or tubing
          to be used as physical protection for underground cables that exit from buildings or
          that are located outdoors on poles, without a box being required on the end of the
          conduit. A fitting to protect the wires or cables against physical damage is required on
          the ends of the conduit or tubing.".
          William the Geezer, the sequel to Billy the Kid - Shoe

      2. Scott | Feb 07, 2009 07:43am | #11

        >>>Where is the International Electrical Code used?Indeed. What is IEC?I've used NM inside conduit in many situations, mostly to protect conductors from mechanical damage. It would have been really messy and unsightly to transition to THHN.None of my inspectors had a problem with this.Scott.

  4. arcflash | Feb 07, 2009 03:37am | #8

    I personally have never read that you are not allowed Romex in conduit. Then again I have never looked because it is something that we NEVER do out in the field, probably for the same reasons others have mentioned. We ALWAYS transition to individual conductors by stripping the jacket and using the appropriate change-overs.

    If anyone can share the section of the Codebook that references this, please share with the rest of the class. This thread has ratcheted up my curiousity.

    1. User avater
      BillHartmann | Feb 07, 2009 05:09am | #10

      "We ALWAYS transition to individual conductors by stripping the jacket and using the appropriate change-overs.""310.11 Marking
      (A) Required Information
      ...
      (B) Method of Marking
      (1) Surface Marking The following conductors and cables shall be durably marked on the surface. The AWG size or circular mil area shall be repeated at intervals not exceeding 610 mm (24 in.). All other markings shall be repeated at intervals not exceeding 1.0 m (40 in.).(1) Single-conductor and multiconductor rubber- and thermoplastic-insulated wire and cable(2) Nonmetallic-sheathed cable
      ...If you strip the sheathing then you remove the markings.Although it is only for a section that you can see anyway. But a inspector that want to hang you, but can't find an "real" problem could call that out..
      William the Geezer, the sequel to Billy the Kid - Shoe

  5. Ms_Chips | Feb 10, 2009 03:57am | #12

    Thank you gentlemen,

    Even if some of you don't think some of the other respondents are gentlemen :-)

    I only asked the question as I got to thinking about the alleged problem with heat buildup.

    If I may ask, if the wire (circuit) is so loaded as to have significant heating from the current for the wire size, then NM (aka Romex) buried in insulation can't be good either? But I suppose there is some code de-rating for that situation.

    I wasn't planning to actually put NM in conduit except for a sleeve in areas where there is potential mechanical abuse. Several answered that question, so thank you.

    -- Teri

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Vintage Sash Windows Get an Energy-Efficient Upgrade

Low-e storm panels improve the energy efficiency of these old sash windows without changing their classic look.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • From Victorian to Mid-Century Modern: How Unico Fits Any Older Home
  • Designing the Perfect Garden Gate
  • Vintage Sash Windows Get an Energy-Efficient Upgrade
  • Design and Build a Pergola

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data