Proper flue/masonry chimney connection?

RustyNail | Posted in Energy, Heating & Insulation on July 4, 2008 07:30am

Hi all!  What is the proper means to connect a metal flue pipe (coming off a hot water heater) to a masonry chimney?  The flue is standard single wall pipe (exposed in the basement), passing into the chimney.

Do I just install a standard piece of flue pipe, similar to the metal flue leading to the chimney from the water heater?  I ask since the previous installer did as I just mentioned… and it has since rotted out inside the concrete block (block surrounding the terra cotta masonry flue.   

Thanks in advance!

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. MikeSmith | Jul 04, 2008 09:53pm | #1

    i'm confused  .... if it's a masonry chimney... does it have a metal flue liner  or a clay flue liner ?.. i think it has a clay flue liner from your description

     

    ok... does it have a thimble let into the clay flue liner

    sound a little jury rigged ....

    other than the previous one rusting/ corroding.. you could simply do the same thing.... maybe a heavier guage

    if there is a heat issue .. with the flue pipe being too close to combustibles... you may want a heat shield

    Mike Smith Rhode Island : Design / Build / Repair / Restore
    1. RustyNail | Jul 04, 2008 11:11pm | #2

      It's a masonry chimney (block/brick) outer with clay flue liner. 

       <!----><!----><!---->

      Nope, no thimble let into the clay flue liner for the hot water heater.  Just the single wall metal flue stuffed into a hole knocked though the outer block and inner clay flue of the chimney (with mortar slathered around the metal flue). 

       <!----><!---->

      Looks kinda jury-rigged, but an HVAC guy I just had in for some other work said that that's standard installation.  I asked "no requirement for stainless steel/clay thimble of sorts?".  "Nope". 

       <!----><!---->

      To me, it's something that just looked so crappy, I had to ask whether this is really the way it should be done...

      Otherwise... no heat issues (i.e. no fear of nearby combustibles becoming kindling)...

      1. MikeSmith | Jul 04, 2008 11:16pm | #3

        take a look at your clay flue liner.... if it's in good shape... then the heavy guage metal thimble / lead-in will be just fine

         

        worked ok for the previous, right ?Mike Smith Rhode Island : Design / Build / Repair / Restore

      2. Piffin | Jul 05, 2008 07:59am | #4

        From what I am reading, it sounds like this was added to a flue designed for something else. Is that true? Other than that - going back to the original question - the firs thing to do is to inspect the chimney to see if it is safe, and then to be sure it is the right size.Most times, the right thing to do when adding an appliance to a flue already in place is to line that flue with SS to downsize it to the right size for that appliance. Modern fuel burning appliances are more efficient so they tend to produce more condensation. They don't run long enough or waste enough heat energy to keep the flue warm, so the water vapour by product of combustion will condense in the cold flue. That water is probably the reason for your rust.
        Stainless steel or heavier gauge will deal with that, but there could still be more necessary. A common mistake is to say - hook up a burner needing a 6" round exhaust to an 8" square flue. That will cause a slow draft and even more condensation. That is why a liner to re-size the flue can be needed. 

         

        Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

        1. RustyNail | Jul 05, 2008 05:42pm | #5

          It appears that the chimney flue was used for both the hot water heater and furnace years ago.  The chimney actually has three thimbles:  one for the old furnace (no longer in use, due to a high-efficiency furnace now being in place), one for the hot water heater (in use, and the source of this question), and one for possibly a previous hot water heater (it is a clay thimble, but is too low and has been mortared up). 

           <!----><!----><!---->

          I'm thinking you're also correct about the flue actually now being too big for just the hot water heater.  I believe the clay chimney flue is 8x12...

           <!----><!---->I'd put in a liner, but since this house will be going up for sale soon, I'm looking to spend as little $ as needed...

          1. Piffin | Jul 05, 2008 05:56pm | #6

            Well, I think you now know what the problem is.
            8x12 is far too large for a water heater.One more problem with that - the oversized flue can make it so hard for a good draft to get going, that the fumes can gutter and spill inot the house.So get a couple good CO meters to warn you that you are poisoning the family 

             

            Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

          2. brucet9 | Jul 05, 2008 07:21pm | #7

            "I'd put in a liner, but since this house will be going up for sale soon, I'm looking to spend as little $ as needed..."LIABILITY ALERT!If the buyer should suffer injury resulting from gases spilling into habitable spaces due to that over-size flue - the previously mentioned guttering or a corrosion failure of the water heater flue or whatever - you could have an expensive lawsuit filed against you that would make the cost of a liner look very cheap.
            BruceT

          3. RustyNail | Jul 05, 2008 09:09pm | #8

            I know, I know... another one of those, you touched it in some manner, now you're liable.  Neglect the fact the venting has been like this for an unknown number of years (13+)...

          4. Piffin | Jul 05, 2008 09:48pm | #9

            what RE law says is that if you KNOW about a defect and fail to disclose it, you have a liability and penalties can apply on top of the liability. Not that you touched it, it is that you knew it needed some correction. 

             

            Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

          5. RustyNail | Jul 06, 2008 07:08am | #10

            In the effort of trying to learn something new... how do I know that I need a liner, and what size?  In the IRC, for draft-hood appliances in masonry chimneys, all I see is the max allowed appliance input rating.  No minimum (as the min/max applies to fan-assisted combustion systems).  I know I have to be missing something, just not seeing it.  <!----><!----><!---->

            The water heater setup is as follows:  32K BTU water heater equipped w/ draft hood (not high efficiency heater).  The connector (draft hood to chimney) is 3" single wall, 8' long (1' rise), connecting into masonry chimney flue, 8" x 12",  approximately 30' long.  Again, this is now the only appliance using the chimney.  <!----><!---->

            From looking at the code book, it appears there's also code compliance issues with the connector, in that it needs to be 4" pipe.  <!----><!---->

            Oh, and please don't refer me to an HVAC guy!!  Been there, done that, and he saw nothing wrong with the setup.  :-D  Really...  Just this past Wednesday.  And he was by far the better of the two HVAC guys that I've used in the recent past...<!----><!---->

          6. Piffin | Jul 06, 2008 06:22pm | #11

            "how do I know that I need a liner,"'cause a bunch of yahoos on the internet just told you so
            ;)"and what size?"There is an install manual that came with the unit. If you don't have it, you can find it on the web in *.pdf format at the manufacturers site, or you can call their tech help line.Going generically, since you have a 3" flue feed and that is typical for that type heater, the manual probably calls for a 3" flue, so you should have nothing larger than a 4" the rest of the way out, or have a mechanical assist ( in line fan linked to run when things fire up and for a period after the flame goes off)
            But if code suggests 4", that may be the main flue requirement - I am not reading it myself. Sometimes manufactures specs dominate, and sometimes codes do. for now, my interpretation would be that the manufacturers on yours says 3" and the main stack should be 4"
            What size is the actual exhaust on the unit?BTW, an 8' nearly horizontal line is also contributing to your problem with draft. 

             

            Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

          7. RustyNail | Jul 06, 2008 08:05pm | #14

            No, no... I'm not going to imply anyone here is a yahoo!  :-D  I appreciate the input... I learn, but know enough to go back and check things stated online...

            The install manual... kinda useless.  It discusses only the connector size, nothing about the vent, and not venting tables. It just refers you to the National Fuel Gas Code.  This heater will probably end up getting replaced, as it's past it's expected life (installed in 1995).  <!----><!----><!---->

            I think I found what I was looking for after I posted last night, telling me how I know the vent's too big.  It wasn't in a table, but in the following text, as it applies to masonry chimneys venting a listed appliance with draft hood/category 1 appliance (IRC 2427.5.4):  "For sizing an individual chimney venting system for a single appliance with a draft hood, the effective areas of the vent connector and chimney flue shall be not less than the area of the appliance flue collar or draft hood outlet, nor greater than seven times the draft hood outlet area. <!----><!---->

            And no, the text wasn't underlined for me in the book, so I'm not that blind!  ;-D<!----><!---->

            To answer your question, the exhaust on draft hood is 3".  So, area of 3" pipe is 7.1 sq in.  Area of the existing flue is 96 sq in, well over the 49 sq in max (per the above citation).  <!----><!---->

            The 8' line, with 3" appears to be a problem.  From what I read, two different problems with it (based on IRC G2428.3.2 and 3.3):<!----><!---->

            1.  If I read the table correctly, with a 1' rise in the connector, with a chimney vent 30' high, the highest appliance input rating is 24K BTUs, 10K under the 34K rating of the water heater.    <!----><!---->

            2.  The 8' connector (using 3") is in violation of the maximum vent connector length, except if the capacity is reduced.  If I read it correctly, I'd have to reduce the max input rating by 10% (reducing 24K BTU to 21.6K). 

          8. Piffin | Jul 06, 2008 08:19pm | #16

            OK, you have some hard info to work from now.My experience is in solid wood appliances mostly, where a lot of other influences and variables are learned.What is not specificly covered in addition to why you have recounted here is the combination of the flue size problem and the horizontal run problem. my instinct is that a specific analysis of your installation by an expert yahoo would indicate that you'd definitely need less than a 49" flue cross section or a shorter feed line or a greater up angle or a combination of all the above.Simplest of course is to just use the 4" all the way. 

             

            Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

  2. User avater
    rjw | Jul 06, 2008 06:32pm | #12

    On Edit-Note: I wrote this before reading the whole thread: So consider this confirmation.

    FWIW, the better heating contractors in my area automatically install a flue liner for the water heater when changing out to a 90+

    Consider finding a qualified HVAC contractor in your area using the contrator locater at http://www.nationalcomfortinstitute.com

    >>it has since rotted out inside the concrete block (block surrounding the terra cotta masonry flue.

    OK. You've been getting condensation at that point - showing, or at least suggesting, that the block/liner is relatively coldand thus the flue gases are cooling too much causing the condensation.

    I'm guessing the chimney/flue originally served both a furnace and the water heater, and now the original furnace has been replaced with a side vented 90+ furnace, leaving the chimney much cooler than before.

    If so, a flue liner should be added to the water heater flue as it passes up through the chimney.

    In NW Ohio, for a 2 story house, you'd be looking at $300+/- installed price.

    Or you can DIY.

    If the furnace hasn't been replaced, check for too much air getting into the flue (either at a flue connection or through a cleanout reducing the effective draft in the water heater (and furnace flue)


    Remember Mary Dyer, a Christian Martyr (Thank you, Puritans)
    http://en.wikipedia.org/wiki/Mary_Dyer


    May your whole life become a response to the truth that you've always been loved, you are loved and you always will be loved" Rob Bell, Nooma, "Bullhorn"



    Edited 7/6/2008 11:36 am ET by rjw

    1. User avater
      rjw | Jul 06, 2008 06:37pm | #13

      Oh yeah, if your house is 70-80+ years old, that third flue opening may well have been for an incinerator.

      Remember Mary Dyer, a Christian Martyr (Thank you, Puritans) http://en.wikipedia.org/wiki/Mary_DyerMay your whole life become a response to the truth that you've always been loved, you are loved and you always will be loved" Rob Bell, Nooma, "Bullhorn"

    2. RustyNail | Jul 06, 2008 08:11pm | #15

      You guessed right, both the furnace and hot water heater used to use the same chimney.  The furnace installer (years ago) put in a 92 AFUE furnace and didn't bother to address the now oversized flue for just the hot water heater.  <!----><!----><!---->

      Yes, thinking that both a flue liner and new water heater may be in the future... 

      Hmm, you have me wondering about the incinerator.  House was built around 1940.<!----><!---->

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Simple and Discreet Countertop Power

A new code-compliant, spill-safe outlet from Legrand offers a sleek solution for a kitchen island plug.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data