GaryGary | Posted in Energy, Heating & Insulation on November 16, 2006 02:39am

Hi,
I am putting in a radiant floor.

Over the existing 3/4 wood subfloor, I am installing half inch PEX lines at 9 inch spacing with 3/4 inch spacers or sleepers between the PEX lines. Then the thin foam sheet underlayment and then laminate flooring.

I am going to use the type of aluminum sheet heat spreaders that have a groove for the PEX tubing to sit in.
The spreaders can be installed in two ways:
1) with the groove facing up and the alum sheet extending over the top of the 3/4 spacers just under the finish floor.

2) with the groove facing down, and the alum sheet extending under the 3/4 spacers (between the spacers and the 3/4 subfloor).

I was told that the performance would be about the same with either scheme, but I did a little test, and scheme 1 seems to do a lot better getting floor surface temperatures that are higher. Since the heat is supplied by solar collectors, the lower the water temperature I can use, the more efficient the system.

So, I am inclined to use scheme 1 (with alum spreaders right under the finished floor). My question is: Are there any disadvantages to this scheme, or any reason I should use scheme 2 instead??

—-
I am using PEX-AL-PEX for the tubing, so the expansion rates for the PEX and the spreader plates will be similar.

The alum sheet I am using for the spreaders is 0.019 thick.

Details on the spreader plate test:
http://www.builditsolar.com/Experimental/RadFloor/HeatSpreaders.htm
Water temp 92F,
Scheme 1: floor surface temp 82F
Scheme 2: floor surface temp 72F

Gary

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. rocknreno | Nov 16, 2006 05:22am | #1

    I used method one under my bamboo floor and am very happy with the result. Less insulation above the plates made the most sense to me.

  2. Grott | Nov 17, 2006 05:06am | #2

    One.

  3. McPlumb | Nov 17, 2006 05:21am | #3

    The aluminum plates reflect heat, if it's under the tube heat is reflected into the living space. With the plates over the tube heat is reflected away from the living space, as your test show.

    1. User avater
      BillHartmann | Nov 18, 2006 12:30am | #7

      "The aluminum plates reflect heat, if it's under the tube heat is reflected into the living space. "Actually in this case it would be a radiator and not a reflector.But for it to radiate the AL needs to have 1" free air space, which it does not have in this application.Also it is a good conductor and in free the whole plate would be at the same tempature and it would radiaton almost as well in both direction. The slight difference would be the space that the tube takes up.The differnence is his experiement has nothing to do with the abilitly of the AL to radiate or not.The difference is the thermo resistance of the 3/4" ply spacers.

      1. User avater
        BillHartmann | Nov 18, 2006 03:34am | #8

        From email."Radiant is the key word here. It can be and is reflected in this case. Put a sheet of Aluminum out in the sun, the temperature of the aluminum will change some  but the amount of radiant
        energy it reflects will cook your dinner. Wirsbo publishes a complete design manual it explains the principles of radiant floor, radiant ceiling, ice melt installations. Wirsbo wholesaler supply
        houses have them they are an excellent resourse . I keep one on the truck."Yes. Radiant is the key word.Place the aluminum between plywood and flooring like it is in this application the and then see if it will cook your dinner.The aluminum is only used as a conductor in this application to help transfer and spread the heat from the tubing to the floor.Any radiating is done what is done from the flooring.

        1. McPlumb | Nov 18, 2006 04:07am | #9

           

          Me thinks thou dos't protest to much! Simple physics only works one way!

          1. User avater
            BillHartmann | Nov 18, 2006 04:10am | #10

            "Me thinks thou dos't protest to much! Simple physics only works one way!"Exactly.What is the physics of radiant energy heat transfer and the physics of conduction heat transfer?

      2. User avater
        RBean | Nov 18, 2006 04:12am | #11

        The reflective or radiative properties of materials are determined by its emissivity.

        <!----><!----> <!---->

        1.0 being the perfect radiator and 0.0 being the perfect reflector. <!----><!---->

        <!----><!----> <!---->

        Bare aluminum, even oxidized, has only a nominal emissivity between 0.20-0.31 and thus would make at best a poor radiator.

        <!----> <!---->

        In order for the plate itself to reflect or radiate it would need to be decoupled from the mass of the floor.  It is however an excellent conductor in the application – coupled to a wood surface having a plus 0.9 emissivity. <!----><!---->

        ___________________________________________________________<!----><!---->

         <!----><!---->

        This link and images come from our resource library and will “shed some light” on the topic of plates and orientation.<!----><!---->

        http://www.ngml.ksu.edu/research/project_archive/project_archive_publications/ashrae/1036_final_report.pdf

        View ImageRBean

        web: http://www.healthyheating.com blog: Journal of Indoor Environmental Quality

         

        1. McPlumb | Nov 18, 2006 06:28am | #12

          In the fourth photo they show plates. For obvious reasons they didn't bother to test and show pictures of a test with plates installed on top of the tube, witch a certain individual suggested wouldn't make any difference. It also is appearent that the heat is radiating more at the tubing than the edges of the plate. This leads me to conclude the whole plate is not the same tempureture as a certain individual suggested it would be. The 100,000 BTU radiant tube, gas fired heater I installed today  required 18 inches of clearance to combustibile on the back side of its inefficent aluminum reflecter and 74 inches to combustibiles in the front. Or maybe they put aluminum on there for an insulater!

          1. User avater
            RBean | Nov 20, 2006 07:29pm | #13

            Unfortunately, there is a shortage of researchers with dollars but infinite ways to assemble radiant systems (thus, the limited number of assemblies tested).  <!----><!----><!---->

            <!----> <!---->

            There are however, mathematical means and the FEA software to play “what if”.  The plate manufacturers would be able to provide the FEA models for most assemblies – I would venture to guess they already have this stuff on file. <!----><!---->

            <!----> <!---->

            So long as there is a temperature difference between the fluid in the pipes (or temperature of an electric element) and its surrounding mass there will be a difference in temperature in the "chain" so yes the whole plate is not the same temperature when it heating or cooling.

            <!----> <!---->

            The temperature profile at the surface (infrared footprint) will vary depending on the spacing and depth of the tubes and the conductivity of the assembly.  

            <!----> <!---->

            We recommend locating and reading these three resources:<!----><!---->

            <!----> <!---->

            Depth Perception, by John Siegenthaler, P.E. <!----><!---->May 18, 2000<!----> The depth of<!----><!---->

            hydronic tubing can affect the performance of a heated concrete slab. <!----><!---->

            <!----> <!---->

            Is 2 Foot Too Far? By John Siegenthaler P.E. , <!---->January 31, 2001<!---->, Some<!----><!---->

            radiant installation can afford to push the envelope.<!----><!---->

            <!----> <!---->

            Impact of Surface Characteristics on Radiant Panel Output, University of Illinois at Urbana-Champaign, Department of Mechanical and Industrial Engineering, ASHRAE 876 TRP<!----><!---->

            <!----> <!---->

            Not sure what you mean by “inefficient aluminum reflector” or “aluminum on there for an insulater”. 

             

  4. User avater
    johnnyd | Nov 17, 2006 03:33pm | #4

    That's a valid test, GaryGary.  Your method #1 is exactly the right way to do this IMHO, especially the PEX-AL-PEX.  You might even want to look into pre-made heavier extruded plates to see if they might fit in your budget.  They will be even more efficient at emitting heat into your room.  Especially with such low water temperatures.

    Have you done a room-by-room heat loss analysis?  What is your design day temp? How many heating degree days (HDD) in your climate? Do you have climate data indicating % of clear days?  Ah, looking back now I see you are in Bozemen..should be just about the perfect climate for a solar system.

    These are all things that are nice to know as you design your system.

    What provisions, if any, have you made for back-up heat for extended periods of cloudy weather?  Do you have a large storage tank that will store fluid at a higher temperature and then mix it down for your floor?  Are you going to drain back the fluid from the collectors when the circulators are off to avoid freezing or flash-to-steam problems?

    These are all things I've thought of when pondering whether or not to add solar to my current electric resistance/propane sourced system.

    One thing for sure, don't try to economize on the plate coverage.  Put them just as close together as you can without touching.

     



    Edited 11/17/2006 7:35 am ET by johnnyd

    1. GaryGary | Nov 17, 2006 07:28pm | #5

      Thanks all -- appreciate the help!Looks like method 1."Have you done a room-by-room heat loss analysis? What is your design day temp? How many heating degree days (HDD) in your climate? Do you have climate data indicating % of clear days? Ah, looking back now I see you are in Bozemen..should be just about the perfect climate for a solar system."I used the Ipex software to do the heat loss and loop sizing. For the time being, our existing forced air system will be the backup heat. At some time in the future, I plan to add a condensing boiler, and get rid of the forced air altogether. I sized the loops to be good for our full design temperature. Bozeman is pretty good on sun, but our house is about as bad a passive solar design as one could imagine -- my simulation says the collectors will be able to provide nearly half the heat."What provisions, if any, have you made for back-up heat for extended periods of cloudy weather? Do you have a large storage tank that will store fluid at a higher temperature and then mix it down for your floor? Are you going to drain back the fluid from the collectors when the circulators are off to avoid freezing or flash-to-steam problems?"The solar heating system I have put in has 240 sqft of collector and a 500 gallon hot water storage tank. Its a drainback system. Its described in way too much detail here:
      http://www.builditsolar.com/Projects/SpaceHeating/SolarShed/solarshed.htm
      (any comments on it would be appreciated)Thanks,Gary

      1. User avater
        johnnyd | Nov 17, 2006 07:49pm | #6

        Wow, sounds like you've really done your homework well.  Good luck on the project, and let us know how it works out.  We love pictures!

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data