repurposing a 50amp oven circuit
i have a 50 amp oven receptacle that will no longer be used for an oven. i would like to “repurpose” the circuit to power a refrigerator, a microwave and under cabinet lighting. What concerns does this cause?
thanks
Replies
repurposing a 50amp oven circuit
Let me first begin with the fact that I am NOT an electrician.
That being said, I think the smart thing to do would be to install a 50-amp circuit breaker in the main panel, then install a sub-panel where the oven receptacle is located.Then, you can run your 15 and 20 amp circuits from the subpanel.
An electrician can do this pretty simply for you since all the wire is in place. Otherwise, you could easily do it yourself, as there are many books and websites that tell you how to install a subpanel.
I can't think how this would raise any kind of concerns beyond the possible requirement to get a permit/get it inspected by your AHJ.
Is it a 4 wire circuit (2 hots, neutral, ground)? It could be done, I don't know about it being code compliant. Three wire circuit, don't bother with it, even though it could be kludged to work.
He said 6/2 in the other thread, That was never legal for a 120/240 circuit, even for dryers and ranges. The third wire has to be insulated to be used as a neutral.
A lot of cooktops and a few ovens were 240 only (no light or timer) and they would be legal.
Good Catch!
Good catch, Greg ..... I forgot all about that little detail.
If the OP only has three wires, then he can't do much. He has no choice but to run new wires.