| Posted in General Discussion on October 28, 1999 11:27am

*
I can’t decide whether to use rigid foam sheets or plywood (or both) as exterior sheathing. I live in an area of very high winds year-round, so plywood sheathing seems like a good idea. Plywood sheathing also would provide a good nailing surface for the brick ties, since the exterior will be brick.
On the other hand, rigid foam insulation apparently prevents thermal bridging and adds extra R-value. The structure of my house will be 2×6, with fiberglass blown-in insulation. I live in the southwest, so my concern is not heating, but reducing the air conditioning load.

Or would I be foolish to use both materials?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Guest_ | Oct 04, 1999 09:27am | #1

    *
    Bonnie I would go with plywood. The r value of the foam on 6" walls versus the strength of the plywood, to me it's no contest. And since You didn't ask I'm no big fan of blown insulation.For what it's worth. Skip

    1. Guest_ | Oct 04, 1999 04:51pm | #2

      *Go with the plywood,or osb,and if the budget allows add the foam.As for your insulation, would blown in cellulose be better?Floating fiberglass particles scare me.

      1. Guest_ | Oct 04, 1999 05:28pm | #3

        *Cellulose is safer, has a higher R value, and blocks radiant heat far better than fiberglass.

        1. Guest_ | Oct 05, 1999 12:24am | #4

          *Bonnie, et al. The 1977 Legre house, arguably the first double wall super insulated house in America, was sheathed with i-inch of Dow Styrofoam. The only bracing was let-in corner bracing which, a few years later, we learned does not work. After twenty years the house still stands, free of moisture or rotting problems. It has been subjected to dangerous high winds. By the bye. I'm not necessarily arguing for non structural RFBI sheathing. Just wanted to let you know how one house in Massachusetts sheathed with RFBI only, fared over twenty-two years in Massachusetts.If one opts for this method, use two full sized sheets of plywood or OSB vertically in each corner. The UBC--West coast code-requires that additional bracing be installed every 25 feet. Keep in mind that the interior gypsum wall board (GWB) provides some racking resistnace. The UBC code acknowledges this. Neither the BOCS or UBC says anything about metal bracing. GeneL.

  2. jerry_parker | Oct 05, 1999 01:13am | #5

    *
    Bonnie,

    I posted a message with a concern I have using rigid insulation with no wood product sheathing.

    Along with the structural integrity issue, I am concerned about security. With no "hard surface" sheathing, intruders could cut through vinyl siding, rigid foam, and drywall.....never having to break a window!!

    The national builder Ryan Homes seems to be big on this type of construction, i.e. rigid foam over studs (no OSB).

    I am trying to find out results form long term tests of this method.

    To your question, I am a traditionalist and OSB sheathing with fiberglass batts (esp with 2x6 walls) have shown to be a very effective insulation solution as well as structural.

    Jerry

  3. Guest_ | Oct 05, 1999 04:29am | #6

    *
    Bonnie:

    The brick ties should be nailed into the studs, not just the sheathing.

    Jerry:

    20 years ago I worked as a subcontractor on Ryan homes. Not sure what has changed since then, but from what you say, it sounds like things are about the same. What I am getting at is, at least back then, Ryan delivered very inexpensive square footage.

    1. Guest_ | Oct 05, 1999 08:50am | #7

      *Gene, if you say the let in corner bracing doesn't work, why is the house still standing?It sounds contradictory.And we have been using that sysytem here in MI for the last twenty years. And there aren't any leaning towers of pizzas here!Please elaborate.blue

  4. Bonnie_B. | Oct 05, 1999 10:29am | #8

    *
    Skip: Why don't you like blown-in insulation? Fiberglass batts do not seem to be particularly effective at stopping air insulation because they never completely fill the wall cavity. Bonnie B.

  5. Guest_ | Oct 05, 1999 11:00am | #9

    *
    Bonnie;

    I am a believer in Radiant Barrier insultation for reducing AC loads. Results are dramatic. You may want to look into this.

    1. Guest_ | Oct 05, 1999 03:03pm | #10

      *Bonnie,I do not know where you are but I would go with Plywood or osb sheeting. FEMA requries this now because of experiences of wind loading during hurricanes in my area. If you use osb it does not have the nail holding power of plywood. Make sure siding is nailed into studs. If using vinyl siding staple it.Use batts to minimize shrinkage and setteling in your insulation. You dont want 6 inches of uninsulated space at the top of your walls 20 years from now.Do not use osb on your roof. Use 5/8 plywood. If you are in a humid area ventilate the hell out of your house.Good luckRick Tuk

      1. Guest_ | Oct 05, 1999 07:32pm | #11

        *Maybe dumb Q: Why isn't (or is it?) T&G OSB or ply used on roofs? I know some people use those Simpson clips, most seems to just stick a 16d nail in for spacing. Doesn't this cause problems when the completed roof is walked on, esp. at low pitches?

  6. Bonnie_B. | Oct 05, 1999 10:23pm | #12

    *
    Reinhard: Thanks for your tip. I just checked into the availability of blown-in cellulose. It is available, but not common here. Do you think the fiberglass fibers would still be a threat once the drywall is installed? Bonnie B.

  7. Guest_ | Oct 06, 1999 12:42am | #13

    *
    Blue. No it is not contradictory. I've written and posted on Breaktime several in depth articles on wood corner let-in bracing. I wrote an article on it called To Brace or not to Brace for the May 1999 issue of Building & Remodeling News.

    Codes require let-in corner wood bracing to with stand 5200 pounds of racking force. A considerbale amount of actual testing of braced walls shows that the let-in brace will break when less than 2/3 of the 5200 pounds of force is appliesed to the wall.

    So why doesn't the wall collapse? Because the ultimate strength of the wall is dependent on the studs. The worse that happens is dyrwall and plaster crack, doors and windows stick and become hard to open and close. This is also true of metal bracing such as manufactured by Strong Tie. They do not recommend the use of their bracing only, and say it is to be used only as a temporary brace until the wall is structurally sheathed. GeneL.

    1. Guest_ | Oct 06, 1999 04:14am | #14

      *Andrew yes t&g ply can be used on a roof deck. The sheets still get spaced like any other sheet goods. The reason why it's not more common? $$$$$$$$$$$

  8. Cesil | Oct 06, 1999 05:32am | #15

    *
    Speaking of tongue and groove. Floor decking panels say to space them. We always butt them tight with a sledge. Which is correct? How to you space them. Same question for wall sheathing...

  9. Guest_ | Oct 06, 1999 05:50am | #16

    *
    Not so much that it is a "threat" as it is inferior to cellulose, as Ron notes. If someone were to market cellulose aggressively -- for example, a pink version -- it would be more common. Note how much direct consumer marketing Owens-Corning does.

  10. Keith_Taylors | Oct 06, 1999 06:17am | #17

    *
    I've seen a lot of guys skip the spacing on OSB roof sheathing and in the fall when frost forms on the roof you can see every seam in the whole damn roof. Somone else asked about the layout problem when spacing OSb sheathing, I've always just cut a sheet back to the next layout and kept on going. I think that this issue was gone over not too long ago in another posting which delt with 2x4 vs. 2x6 wall thickness, you may want to check the archives for that posting.

  11. Guest_ | Oct 06, 1999 06:46am | #18

    *
    Andrew:

    The plywood clips are used (and required here) with 24" OC rafter (truss) spacing. If they are left out, local inspectors will make you block every plywood or OSB joint on the roof!

    1. Guest_ | Oct 06, 1999 07:31am | #19

      *Most wood or wood composite sheet goods,(decking,sheathing),are sized for spacing.The allowances are made so panels still hit 16" centers and have the spacing for expansion and contraction. In the real world does anybody do this? On a roof sometimes ,on a deck rarely.How do I space them?By not bangin em' tight with a sledge hammer!

      1. Guest_ | Oct 06, 1999 07:47am | #20

        *Although I know OSB isn't popular with a lot of people here, we use it for sheathing , subfloor and roof decking.I prefer 3/4" OSB to plywood for subfloor, as long as it doesn't get wet repeatedly. As far as roofs, around here the H-clips Andrew asked about are mandatory even for 16" centers. They do help and also space the sheets automatically. OSB might not be perfect, but we haven't had any problems with it so far. Pricewise it's not nearly as cheap as it used to be. I might be nervous if I was putting three-tabs over OSB, but I worry more about uneven rafters than joints in the OSB. Around here in the morning, when the sun is at a low angle, you can see every rafter on the cheap tract houses.

        1. Guest_ | Oct 07, 1999 11:19am | #21

          *Bonnie, The blown in insulation settles like the crackers that come packed by weight not volume. Some serious caulking and expandable foam should help the infiltration. The batts can be fitted pretty tight. I'm not hip to the cellulose versus fiberglass r value competition.The detailing around wall penetrations makes a sizable difference.Good Luck! Skip

          1. Guest_ | Oct 07, 1999 03:18pm | #22

            *Nick,I also prefer 3/4 T&G on floors. And 1/2 on walls. But we have learned manylessons from storms. I saw a lot of shingles and metal roofs With nails and staples pulled out of the osb. It was easier to patch because there were no nails to get in your way. On plywood and plank roofs the shingles may have been ripped off but the nails were still in the wood.Rick Tuk

          2. Guest_ | Oct 07, 1999 05:07pm | #23

            *Blue,The drywall contributes to the bracing more than most people realize. By the way it is easier to break a window than to cut thru vinyl siding.Ron

          3. Guest_ | Oct 07, 1999 06:06pm | #24

            *The storms, particularly hurricanes, sure do the most relevant research work! "My" hurricane demonstrated the need to properly nail off sheathing, for example. I would not be eager to live in a foam home. OSB seems to be fine for wall sheathing, and really not overbuilding.The most common reason given here for switching from ply to OSB on roofs has been a the builder's bitter delamination experience from rain during the exposed phase of construction.On floors, I was surprised a few months ago that the overwhelming response here was for T&G OSB (yes, 3/4 or better). OSB's nail retnetion isn't important with flooring or siding where the fasteners go into the underlying studs/joists.

  12. Mad_Dog | Oct 07, 1999 06:58pm | #25

    *
    Main reason T& G is not used on roofs: $. More to buy,
    harder to install. Clips work because not too much traffic
    up there and pigeons don't weigh that much. Also, how big
    would a tongue or groove be on half inch or (less?) diameter
    plywood/OSB?

    Bonnie, I do agree with Andrew and Skip that the strength of
    Plywood or even OSB for wall sheathing is unquestionably a
    bigger plus than any r-value gain or sealing help that you
    would get from foamboard. If you indeed have high winds,
    you'll have a lot less worry, and a lot less cracked or
    "moved" finish materials ie drywall.

    Yes a lot of builders are using OSB for floors but not this
    one. I don't even like it on roofs, the pigeonload
    notwithstanding!

    MD

    xxxxxxxxxx

    1. Bonnie_B. | Oct 07, 1999 09:11pm | #26

      *Adam S: Yes, I was planning to use a radiant barrier in the attic because I live in a dry desert climate and heat gain is the biggest problem. However, I also wanted to use a radiant barrier in some of the walls, especially walls facing south and west; however, I haven't figured out how to accomplish this task. I need to keep the a/c air in the house and try to keep the hot sun out of the house. Bonnie B.

      1. Bonnie_B. | Oct 07, 1999 09:20pm | #27

        *Rick: I live in the desert southwest, very hot with regular strong winds and lots of dust.The builders in my area use osb; however, I do not want an average house, I would like a well-built house. I will make a note of your advice on using plywood over osb. I plan to have brick siding with a cement tile roof, so the question is how to best attach these materials to the plywood, considering the high winds here.I wanted to use blown-in insulation rather than batts in order to fill all the cracks in the walls so that expensive a/c air does not escape. Bonnie B.

  13. Guest_ | Oct 08, 1999 09:54pm | #28

    *
    Bonnie: If you want something better than an average house and you plan to use a brick veneer you might want to check out a recent report regarding masonry wall failures. The report I read was in the Journal of Light Construction (Sept 99 issue) quoting one Clayford Grimm article in Southern Building (I have never seen that mag) and another Grimm article in The Construction Specifier. Even though you are in a relatively dry climate you may want to specify stainless steel brick ties. Grimm reports that common galvanized ties have rusted through in 10 years. The bulk of the JLC report on Grimms' findings have to do with the effect of windstorms on brick walls. Water and poor workmanship can combine to make a masonry wall much weaker than most codes anticipate. The workmanship issues include unfilled morter joints, using bricks that are too dry, over-sanded mortar, fat mortar joints and creating wall with bows. Add that to rusted out brick ties (remember a previous post that they should be fastened to studs) and brick walls over a certain height could end up crushing someone. I haven't had any experiences with this myself but thought you might want to look into it. BTW the JLC is hosting a building conference in Vegas on October 22 and 23 with a number of workshops and exhibitors booths. You may be close enough to drive there. http://www.jlclive.com Thor

    1. Guest_ | Oct 09, 1999 09:25am | #29

      *A detail on ply that doesn't get mentioned much -- the number of plies. 4-ply 1/2" plywood is much better than 3-ply 1/2", flatter and stronger. I have some 5-ply 1/2" that I ripped out in my basement; I keep it around for odd jobs where I can use its sturdiness. 4-ply is a couple bucks more than 3-ply, though lately prices seem to have gone up (be nice if they went down for a change).

      1. Guest_ | Oct 10, 1999 11:17pm | #30

        *Thor I thought Your post was interesting in light of a recent experience of mine. A house I was working on showed a sag in the lintel over the garage door. The new homeowner got a mason out for an assessment. The lintel was put in 1/2 assed but when they started to repair it the whole wall above showed brick ties that had rusted, in some cases in half, and there were several stress cracks along the wall. I've seen a lot of houses with these cracks and wonder if it is for the same reason. They rebricked that area but there are stiill three sides sitting there.

        1. Guest_ | Oct 11, 1999 12:43am | #31

          *Andrew; you've metioned 4-ply plywood before. I've never seen or heard of this, and I'm wondering if it is an American thing. My understanding of plywood is , it always has to be balanced (a core + even numbers of veneers, alternating in direction: 3, 5, 7, 9 etc.) Definitely for interior stuff,it has to be balanced to meet the specs of the millwork orgs (AWI in the US, AWMAC in Canada), and last time I looked at the Canadian Plywood Association, everything had to be balanced. Is this stuff for a specail application or something?

          1. Guest_ | Oct 11, 1999 05:11am | #32

            *I won't suggest I'm a plywood expert. The APA ("P" no longer means plywood) agrees with you that plywood "always" has an odd number of plies: http://www.apawood.org/products/plywood.html.However, I'm fairly confident of my ability to count to four. Some builders offer 4-ply as an upgrade, e.g. http://www.jadehomes.com/misc/9000upgrades.htm. It's nothing special, even Home Depot sells this stuff (you gotta look way up high to see it sometimes); I don't know if 5-ply 1/2" is still available in the states. The face plies are in the same direction as each other, I should pull some apart to see what's inside. Anyway, it is definitely superior -- the sheets are flat, significantly sronger, and hold nails much better. The interior ply on 3-ply is just garbage. I plan to use 4-ply -- at a staggering increased cost of about $50 -- on my roof.Anyone out there have thoughts on this? This came up quite while ago, in the archives.

          2. Guest_ | Oct 11, 1999 06:04am | #33

            *Cesil, just don't bang them tight. It does requre a little more finesse, but once you get used to it, it's actually easier.And be sure to leave the 1/8th on the sides too!And yes, space the osb roof panelts too, both ways. The clips will not space it enough, you gotta kick it with your foot and staple it in one motion.blue

          3. Guest_ | Oct 11, 1999 06:07am | #34

            *Thanks for the reply Gene.Next question: if this is not passing codes, why are the local inspectors allowing us to use the metal braces, and foam?And some of these guys are the pickeiest people that I've ever encountered! We're not out in hicksville. They attend conferences, seminars, and read all kinds of code type literature to come up with new ways of torturing us oldtimers!But metal t braces always pass!blue

          4. Guest_ | Oct 11, 1999 06:09am | #35

            *They say there sizedfor spacing, but I've never senn any that acrually were.blue

          5. Guest_ | Oct 11, 1999 07:10pm | #36

            *Thanks for the info, Andrew. I wasn't doubting you, I've just never seen it.

          6. Guest_ | Oct 11, 1999 07:15pm | #37

            *Be glad to send you a piece! I wonder what the Post Office would think of a plywood scrap with an address and a stamp on it? I'd have to write "do not bend" all over it...

          7. Guest_ | Oct 14, 1999 12:56am | #38

            *Not to be an alarmist or accused of being Chicken Little but I would have a tough time sleeping (at night or on the job) if I had "seen a lot of houses", had at least a suspicion that a masonry wall MIGHT crush somebody and I had done zilch. Perhaps a copy of one of those magazine articles could be handed to Ms. Unsuspecting Homeowner and prevent a tragedy. Send one to your local building inspector--wouldn't it be great to show THEM that a higher standard should be required? The article I read (JLC) said that SS ties were REQUIRED on walls over a certain height in Canada, Sweden, Germany & Switzerland. In what part of the country have you seen these problems (could be expansive soils or some other problem)? Thor

          8. Guest_ | Oct 15, 1999 07:15pm | #39

            *Thor over the years I've seen a lot of houses with what we call stress cracks. This was my first experience of seeing a probable cause and effect. Many houses get pointed up and I had come to the conclusion, perhaps erroneously, that this was a given. Now I'm not sure. Masonry is usually set on an adequate foundation and tied in other ways besides the ties. I don't know how emminent the danger is. Seems like this would have come out by now. Look at the scramble with EIFS houses. Next stop? Stainless steel nails for all exterior sheathing? Skip

  14. Bonnie_B. | Oct 16, 1999 03:56am | #40

    *
    Thor: Interesting idea. . . the use of stainless steel ties. I had not questioned the bricklayers about the ties, but I did check and found that stainless steel ties are available locally. (Cost: $.05 vs. $.01 for galvanized) I am aware, however, of some problems with brick veneer walls due to poor workmanship.

    I did find the Journal of Light Construction on the Internet and so I could possibly get the back issue with Clayford Grimm's article about masonry wall failures. I am very interested to read about the effect of windstorms on brick walls.

    Your referral to the Journal of Light Construction proved to be unusually useful to me, since this month's issue featured an article on insulation and moisture problems for cooling climates, information which is incredibly scarce.

    I decided to build my own house so I could make all these construction decisions myself. Bonnie B.

  15. Guest_ | Oct 17, 1999 03:31am | #41

    *
    Bonnie,

    Since you're using brick for siding, the only thermal bridge will be the ties. There will be
    an air space between your wall exterior and the brick interior.

    With 2x6 walls and blown in insulation, you shouldn't really need the RFBI thermally
    speaking. From a structural standpoint, you'll have a strong outer skin of brick to
    absorb much of the wind, so with bracing at the corners, you don't really need to worry
    about using plywood.

    Unfortunately you've gotta use one or the other...

    shop price for your wall sheathing and make sure it's well wrapped with 15# felt prior
    to brick installation. Brick ties should definitely be nailed to studs. The strength
    difference between a crappy mortaring job and an excellent one can be as much as
    60%. Don't skimp on the contractor.

    I've never done a blower door test on blown-in fiberglass vs dense packed cellulose
    but from what I've read about the two materials, it seems that cellulose is the way to
    go. It does need to be dense packed (2.5 psf I think?) or it will settle over time.

    Where in New Mexico? I lived in Jemez Springs for a winter once...

    Dan

    1. Guest_ | Oct 19, 1999 08:15pm | #42

      *BonnieI highly recommend plywood or OSB over rigid foam board. It give a better nailing surface for your exterior siding and adds to the structural integrity of the house. On all the homes I build, I push for Icynene foam for insulation. It costs a little more, but it seals all the gaps, crevices, etc. that never seem to get insulated and let air in and there is no thermal bridging. The payback is about 2 1/2 years in savings on your utility bill. A house we finished 6 months ago was 1150sf, total electric and their highest electric bill was $72.00 (this is in the OKC area.) I believe the web site for Icynene is icynene.com.Vince

      1. Guest_ | Oct 20, 1999 05:39am | #43

        *How much do you pay for the Icynene in $ per sf per inch? My perception is that it is more than a little more expensive compared to fiberglass or cellulose or even foam sheets. Was quoted $1.75 sf for 2x6 rafter depth here.

        1. Guest_ | Oct 25, 1999 08:55pm | #44

          *AndrewThe local dealer here charges $1.30 - 1.40 sf. The up front cost is more for the icynene, but here are some of the advantages other than the cost savings in the long run:* Four functions in one; combines the functions of building wrap, poyvapor/air retarder, caulking, professional air sealing and insulation.* Time saving; a 3000sf home can be insulated in one day.* Insulates and air seals at the same time* No sound or order transfer* Eliminates major causes of building envelope problems; controls air leakage around doors and windows, roof decks and wall joists, I-beams and soffits.* Virtually eliminates air-borne moisture movement, providing an effective barrier to air and moisture movement under wind pressure.* Eliminates moisture entrapment; resists water absorption and wicking.* Eliminates special air seal/vapor treatment; i.e. house-wraps, tapes, sealed electrical boxes, heated plenums and the frames involvement in installing an air barrier.The heat flow reduction through 3.5 inches of icynene is 92.2%, through 5.5 inces is 95%.Again, I'm not an icynene dealer, but they have me sold on it and it is the insulation I prefer and recommend.Vince

          1. Guest_ | Oct 25, 1999 09:02pm | #45

            *For that typical 3000 sf house (17% of starts now are 3000+ according to NAHB), what kind of check would you be writing to the insulation people? 15k? (Just getting a sense of scale.)Thanks for sharing your experience. Getting the whole house done in one day must be EXTREMELY attractive, esp. since you're getting much more than the typical sloppy fg installation. I discussed with our Icynene installer the possibility of 2-3" of icynene over cellulose blown behind Tyvek for the roof to save a few $. R-30+ Icynene is VERY expensive. (Semi-cathedral roof, we're trying to escape ventilation and Icynene is an approved method here.)

          2. Guest_ | Oct 25, 1999 09:57pm | #46

            *AndrewJust got finished rough framing a 3,500sf home with 9 & 10 ft sidewalls and approx half the house had a cathedral ceiling, 17ft inside (floor to ridge was 22ft). Homeowner went with icynene and his bill was $9,700.00. He had the underside of the roof sheathing sprayed rather than above the ceiling. The pitch on the roof was 9/12. The earlier house was approx 1,200 sf with a 6/12 pitch roof, 8ft side walls, gable ends and it cost $3,200. It is total electric and her highest electric bill was $72.00 this past summer.Vince

          3. Guest_ | Oct 26, 1999 04:14am | #47

            *Thanks! Numbers make it easier to grasp.

          4. Guest_ | Oct 26, 1999 06:11pm | #48

            *Dan. It depends on the type of corner bracing. Wood corner let-in bracing is a NO no. Better method is two full 4'x 8'sheets of plywood, OSB or whatecevr the code allows, in each corner, installed vertically. The Uniform Builing Code (UBC) requires additional bracing every 25 feet of wall length.Tp prevent cellulose settling blow-in at 3.5 lbs/cubic foot density. GeneL.

          5. Guest_ | Oct 26, 1999 10:04pm | #49

            *Vertically! That's what I've heard. But why why why? I assume it has to do with nail pullout strength? See confusing thread entitled Rick Tuk "Sheathing Direction?" 10/26/99 6:15am

          6. Guest_ | Oct 28, 1999 11:27pm | #51

            *andrew d et al. Keep in mind that regardless of plywood orientation, a plywood panel supported at all eldges is always stronger than panels with some edges unsupported.If you do not block your exterior walls at the 4-foot mark, then you must apply the sheathing vertically if you wish the highest shear value. Otherwise apply the sheathing horizontally. Note, however, that this rule does not apply to roof sheathing. This is because roof sheathing is subjected to loads that are both parallel and perpendicular to the long direction of the plywood. To get greater shear value, increase the plywood thickness or nailing. Hope this helps. GeneL.

  16. Bonnie_B. | Oct 28, 1999 11:27pm | #50

    *
    I can't decide whether to use rigid foam sheets or plywood (or both) as exterior sheathing. I live in an area of very high winds year-round, so plywood sheathing seems like a good idea. Plywood sheathing also would provide a good nailing surface for the brick ties, since the exterior will be brick.
    On the other hand, rigid foam insulation apparently prevents thermal bridging and adds extra R-value. The structure of my house will be 2x6, with fiberglass blown-in insulation. I live in the southwest, so my concern is not heating, but reducing the air conditioning load.

    Or would I be foolish to use both materials?

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Picture-Perfect Pergola

Built from locally sawn hemlock, this functional outdoor feature uses structural screws and metal connectors for fast, sturdy construction.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data