Roof vents, part deux

peteshlagor | Posted in Energy, Heating & Insulation on July 7, 2007 02:21am

Here in Denver, someone’s turned up the heat lately.  We’re running betwixt 95 & 100 over the past several weeks.  Reminded me that I had the same issue last year and wanted to get more insulation upstairs cause even the 14 SEER ac I had put in a couple of years ago has a tuff time fighting off the PM heat buildup.

So’s the insulation sales shark comes by today.  His sales pitch (after examining the house, roof, & attic) focuses upon the roof ventilation of this 12 year old former Parade of Homes place.  Gets me to crawl up in the attic with him (all trusses) and examine all of the soffit and up high roof vents.  Says his calculations indicates I need 6.5 sq ft of ventilation space both for the up highs and for the soffits.  (2400 sq ft house)

There were 4 mushroom roof vents visible from outside.  And a 6 x 12 soffit vent every 6 to 8 feet.  From the inside of the attic, we discover 2 of the 4 mushrooms are not even cut open from the inside and oneof the other’s has 1/2 of it’s 6″ x 6″ square opening covered by a framing 2×4.  So’s I really has 1.5 times 6″ square or 3/8’s of a sq ft of up high ventilation  ( I need 6.5 sq ft).  And looking around at the soffit vents from the inside show only two have light coming thru.  So’s they’re blocked or not cut open either.

At 9 am, it was hot up there!

Anyhow’s, he says they don’t do the vent work.  But he’ll be happy to come back and blow in another 12 inches of white fiberglas on top of the 12 I’ve already got (that isn’t packed down).

Winter protection is not the most important issue with the insulation in this climate.  It can be -15 one day and 70 the next in February.  So I’m more focusing upon the heat issue.

The sales shark tells me he would recommend a powered roof vent to replace one or more of those mushrooms as well a cutting open the soffit vents.

The question being, of these low profile roof models I see when googling the topic, which manufacturer have you’se guys had the best success with?   And how do I calculate the CFM need?  I’m assuming I should avoid the ones offered by Home Desperate.  Are there consumer reports articles that survey roof vents?

 

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Lansdown | Jul 07, 2007 03:28am | #1

    I put in a powered roof vent, because I have a square hip roof and couldn't get a ridge vent in and I hate the cake pans. I got mine from a roofing supply house and it seems quite robust and does the job. It was humming away all day, I have it set to come on at 95 degrees.

  2. DanH | Jul 07, 2007 04:45am | #2

    Several problems with power vents. One is that they tend to have a limited lifetime -- maybe 3 years -- before the motor goes out.

    I'd suggest you get a roofer to install ridge vent (assuming you don't have a hip roof with very little ridge), and get someone to cut in several new eave vents.

    If you get insulation added, you need to make sure that the eave vents aren't blocked. Some insulation guys are careful about this, some aren't.

    So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin
    1. peteshlagor | Jul 07, 2007 06:01am | #3

      Hip roof with ceement roof tiles.  I'm not aware of a ridge vent that works with those.

      The lifespan of those motors are that short, huh?

       

      1. DanH | Jul 07, 2007 06:30am | #4

        Yeah, the lifespan is short. Make sure the unit is easy to access.
        So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

      2. User avater
        CapnMac | Jul 12, 2007 01:49am | #20

        The lifespan of those motors are that short, huh?

        Yeah.  What the product literature does not tell you is that those hours of run time add up fast.  3000 hours sounds a long time--but 10-12 hours a day is only 272 days, or about 9 months.  That's only three years if your attic only gets to 95º for three months the year.  (Not mine, mine will hit 95º at least once a day from about March through October; since 5 June, it's not gone lower than 86º.)

        So, in my climate, you get maybe one season before the bearings seize up or the insulation on the windings melts (can happen at 130º)--all for the cost of running that motor 18-20 hours a day, call it 1.8KWH every day for a long stretch.Occupational hazard of my occupation not being around (sorry Bubba)

  3. User avater
    BillHartmann | Jul 07, 2007 08:48am | #5

    The Forida Solar Institute has done dones of research on heat through roofs.

    And they have had several reports in JLC.

    Everytime I go to FSI website they move things around so I can't point out the research.

    But you can't ventalate heat out of an attic unless you have so much venting that you have a screened porch, not a roof.

    Radiant barriers and the emissivity of different types of roofing had a big affect.

    Don't know how difficult it would be to add a radiant barrier to you roof.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. DanH | Jul 07, 2007 03:51pm | #6

      > Don't know how difficult it would be to add a radiant barrier to you roof.It's basically just a big tinfoil had. Everyone here knows how to do those.
      So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

      1. MikeSmith | Jul 07, 2007 04:06pm | #7

        me... i'd ignore the additional venting.. especially with cement tiles and a hip roof.. the venting is going to do nothing for your roof ( cement tiles  )  and will not lowe3r the  attic temp. enough to notice

        i'd add 12" of cellulose on top of your white fluff.. keep looking until you find a cellulose guyMike Smith Rhode Island : Design / Build / Repair / Restore

        1. peteshlagor | Jul 07, 2007 04:21pm | #8

          I asked about cells.  This firm does it also.

          The shark said, "never to put cells on top of fiberglas.  You can put fiber on top of cells, but the weight difference of cells on top causes excess compaction and inhibits the performance of the underlying fiberglas."

           

          So tell me why the ceement tiles (besides being dark grey and a heat sink) will make a powered vent useless?

          It seems to me that ANY form of removing this superheated air out of the oven over my living area will provide positive benefits.

          Are you suggesting that these tiles will continue to gain more heat than the vents are able to remove?

           

          As far as radiant barriers, wouldn't these have to be applied on top of the roof deck prior to laying the tiles?

           

          As far as another approach to this issue, would spraying foam on the underside of this roof surface provide relief?

           

          1. reinvent | Jul 07, 2007 04:55pm | #9

            The shark said, "never to put cells on top of fiberglas. You can put fiber on top of cells, but the weight difference of cells on top causes excess compaction and inhibits the performance of the underlying fiberglas."Like choped FG has any performance worth talking about.As far as radiant barriers, wouldn't these have to be applied on top of the roof deck prior to laying the tiles?No and in fact if you apply it to the under side of your roofing you should have an air gap of around 1". Not for ventilation but because the barrier will just let the radiant energy pass thru if it is in contact with the roof. Imagine you have an old radiator wraped in tin foil. It will still heat the room, the heat energy passes right thru the tin foil. But if you had a sheet of tin foil held an inch or two away from the radiator it would reflect alot of that heat energy back.

          2. User avater
            BillHartmann | Jul 07, 2007 05:20pm | #11

            "No and in fact if you apply it to the under side of your roofing you should have an air gap of around 1". Not for ventilation but because the barrier will just let the radiant energy pass thru if it is in contact with the roof. Imagine you have an old radiator wraped in tin foil. It will still heat the room, the heat energy passes right thru the tin foil. But if you had a sheet of tin foil held an inch or two away from the radiator it would reflect alot of that heat energy back."Not exactly.The radaint barrier can be in direct contact with the tile or sheathing.It just needs 1" air gap on ONE SIDE. And the down side is better as the dust won't settle on it.The confusing part is that is just not the radiant reflectivity that comes into play.Materials that are highly reflectively are also low emssisive. That is that don't radiate radiant energy when heated.So in the case of an under roof radiant barrier with the air gap away from the roof it is the emisivity that is coming into play.The FSI used show some school science experiments and one of them showed exactly this..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          3. reinvent | Jul 07, 2007 05:24pm | #12

            OK not disagreeing with you but his roof is already in place.

          4. peteshlagor | Jul 07, 2007 06:01pm | #13

            And I got a nest of trusses on the inside.

            Again, is this a possible application for foam?

             

          5. MikeSmith | Jul 07, 2007 04:57pm | #10

            couple things.. 1st .. compacted to what ?

            that fluffy shid has so many air passages thru it , it's pretty useless.... so compactiong it is only going to help

            when we were still using fiberglass, we' d only buy the high density for our walls

            typical standard was  R-11 for a 2x4 wall... you can also get R-13 friction fit  and now you can get R-15 ... so ... what does the fluff do for you .....he's blowing smoke

            2d....

             "super heated air"  is not that superheated..... if you exhaust  120 deg air, what is it replaced with  ?   100 deg ?....... 90 deg ?

            how much energy does it cost you to  run a power vent ?  and what does it do ?

            well, first off.. it costs a  lot of KW... and where is it getting it's air from ?

            is it sucking  the air in from the soffits,  in from the mushroom vents ?... or is it sucking air conditioned cool air out of the  house right thru that fluff you have lying in your attic ?

            truth is ...... it's moving air along the path of least resistance ... what ever that is

            whole house fans... power vents.... for the most part are just crap... can you set up a system  that sucks cool air out of an earth tempered tube under the house.. moves it thru the house to cool .... then exhausts it thru the attic to further cool the attic ?

            no, huh ?...... thought so

            you have a tract house... from your own inspections  they took short cuts..left many  paths for air to move thru

            your best bet is separating  the hot attic from the cool conditioned living space ... vents and power vents don't do that... only insulation does

            cellulose is a radiant barrier.. fiberglass is not... most radiant barriers are snake oil..

            " staple this to the underside of your rafters "  ..... "lay this over  your attic insulation"

            forgeddaboutit..

            best bet.... get an energy audit to come out and do a blower door test... air seal.... then add  add 12" of cells to your fluffy base

            roofs are vented because the asphalt shingle mfr's thought they could blame someone else for reduced life

            current thinking is vented roofs are overrated... not worth the effort and expense

            we do FULL soffit vents and continuous ridge vent on  all our houses....once by conviction that it was helping... now only because code requires venting .. and if we're going to vent, then we want to do  it right... right means balanced and controlled

            your cement tiles don't care how hot they are.. they are going to live the same life-span no matter..

             and yes... the power vent  is not going to  appreciably lower their temp...

            and most of the reduction in attic temp is going top be because your are sucking airconditioned air out of  your house into the  attic

            but, hey, whadda i no ?

             Mike Smith Rhode Island : Design / Build / Repair / Restore

          6. DanH | Jul 08, 2007 04:24am | #14

            Cellulose on top of the FG will likely actually enhance the performance of the FG (which otherwise is doing virtually no good). Besides, what difference would it make to impact the FG performance, given that the existing FG is inadequate anyway?
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          7. peteshlagor | Jul 08, 2007 04:49am | #15

            Within the scope of this project, the wife wants me to have the air ducts cleaned.

            Would it be worth considering to have the duct vacuum truck suck out the fiberglas and have the whole thing reblown with cells?

            I'm still wondering about foaming the roof deck as a radiant barrier...

             

          8. DanH | Jul 08, 2007 05:04am | #16

            It would probably cost more than it's worth to suck out the FG. Just blow cells over the top of it.I really don't know enough about foam to say whether it would be a good idea in your situation. I'm guessing, though, that since you have a nominally open attic, insulating the roof deck isn't a big winner.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          9. seeyou | Jul 08, 2007 05:06am | #17

            Would it be worth considering to have the duct vacuum truck suck out the fiberglas and have the whole thing reblown with cells?IMHO, no. The mingling of the two might up the performance of the FG. FG is not evil. It just doesn't work as well as the pink panther would have you think.http://grantlogan.net/

             

            Sometimes, when I lie in bed at night and look up at the stars, I think to myself, "Man! I really need to fix that roof."

          10. User avater
            shelternerd | Jul 09, 2007 07:07am | #18

            <<best bet.... get an energy audit to come out and do a blower door test... air seal.... then add add 12" of cells to your fluffy base>>I agree with Mike. the blower door test and air sealing are essential. After that is all taken care of go with the cellulose over the fiberglass. I don't think this is a good place for foam. And I'm not sure having the ducts cleaned is such a great idea either but if the wife says do it the upside of arguing with her is non-existent. ------------------

            "You cannot work hard enough to make up for a sloppy estimate."

          11. peteshlagor | Jul 12, 2007 12:22am | #19

            Ok, the energy audit is scheduled for Friday.  $350.

            Talked with the BI also.  His over the phone suggestion was simply add cell over the fiberglas.       Agreed that there was insufficient venting, but seemed unconcerned about resolving the issue in favor of the added insulation.     Said, "yeah, a power vent could help."

            We'll see what the report says.

             

          12. peteshlagor | Jul 26, 2007 05:30am | #26

            Well, I'm still waiting for the auditor's report.  Maybe tomorrow.

            In the meantime, I've been discussing this with my BIL whom is a researcher at one of the top solar energy manufacturers.  He in turn has been spreading it around his other researchers.

            The topic of, "is there a way to utilize this heat rather than simply blow it off" has creeped into the discussion.

            They respond on the basis of the laws of thermodynamics.  (I never studied that stuff in school.)  But in essence, they point out that even though we get freaked about how high the temperature is in a poorly vented attic out here in Denver, there really isn't that much heat.  They comment the trapped heat itself acts as a radiant barrier - to a degree - which limits the further buildup.

            A couple of mechanisms have been tossed about.  The Ericsson engine principal seems interesting.  If there were a way to use that externally heated engine to move air, a powered vent would be created, but not take a power source or use an electric motor.

            And then the "drinking bird" phase change principal...  could this motion propel some form of  bellows?

            But the most intriguing thought to improve the venting (remember I'm apparently unable to add much more in high vents due to the hip roof) is to build in a vented cupola.

             

            More to come.

             

          13. User avater
            CapnMac | Jul 12, 2007 01:58am | #21

            It seems to me that ANY form of removing this superheated air out of the oven over my living area will provide positive benefits

            Ah-hah!  The nub of it, indeed!

            It's mass.

            Your roof has mass; your roof, especially so, for being clay.  It's gaining somthing like 20-65W per square meter of solar energy per hour every hour there's light on it.  That's a lot of energy. 

            Ok, so lets get the hot air out.

            What are we replacing it with?  The ambient 90+º air?  Mind you, the roof mass, once it warms beyond ambient, will transfer heat to any air you run across it, too. 

            Materials scientist the the other day said it better than I could (least until I steal his phrase <G>)--venting a hot roof in Texas is like cooling an oven with with a fan white the oven is still on.  (Now, if one of those grants we shopped would just come through . . . )Occupational hazard of my occupation not being around (sorry Bubba)

  4. User avater
    Matt | Jul 12, 2007 05:56am | #22

    I say forget about the power vent - they use as much energy as they save.  If you want to increase your ventilation - which it sounds like you need to do, get some kind of passive vent.  Heck - I'd even go for a turbine vent before a power vent. 

    For that mater, call the original builder - regardless of the age of the house, and tell him to come cut out the 2 vents that aren't.  It was probably his roofer that messed it up, but it is still the builder's responsibility to check his sub's work.  This coming from a builder...

    As far as calculating the amount of ventilation you need, this is from the NC Residential code:

    Minimum area.

    The total net free ventilating area shall not be less than 1 to 150 of the area of the space ventilated except that the total area is permitted to be reduced to 1 to 300, provided at least 50 percent and not more than 80 percent of the required ventilating area is provided by ventilators located in the upper portion of the space to be ventilated at least 3 feet (914 mm) above eave or cornice vents with the balance of the required ventilation provided by eave or cornice vents. As an alternative, the net free cross-ventilation area may be reduced to 1 to 300 when a vapor barrier having a transmission rate not exceeding 1 perm (57.4 mg/s · m2 · Pa) is installed on the warm side of the ceiling.

    Obviously NC code doesn't apply to you, but the concept is still there. 

    Personally though, I like the idea of adding cells to the attic better, or in addition to...  As far as that thing about adding cells on top of fiberglass - that is the first time I've heard that.  I'd do it in my house if I had a problem.  I can see the guy's point, but the net gain would still be significant especially with the greatly reduced air leakage.

    We used to have this guy Freddie around here.  He had an energy audit/weatherisation  company and was very knowledgeable.  He always used to talk about abating (sp?) fiberglass.  Not that I agreed with that.  Actually he didn't last here because he couldn't deal with people with different opinions than his own :-)

    1. rasher | Jul 12, 2007 07:34pm | #23

      I was at Sherwin Williams the other day and they have a new product: Paint on radiant barrier. It's a silver-ish paint that I guess you apply to the underside of your exposed roof deck. The painters in the ad photo were both smiling, so it must work great...
      Anybody else know anything about this?

      1. DanH | Jul 12, 2007 07:48pm | #24

        Radiant barriers work, when the reflective side is exposed to an air space, but they don't work all that well in most cases. Especially when ventillation is poor, air will conduct more heat than will radiant transmission. And it's generally hard to tell how good of a "reflector" the paint is -- simply being silver colored doesn't tell you much.I can't imagine trying to paint that on my roof deck, even before the extra foot of cells was blown in. A 4/12 roof has a significant fraction near the eaves that can only be reached while laying on your back with your nose against the roof sheathing.
        So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

      2. User avater
        BillHartmann | Jul 12, 2007 08:34pm | #25

        Florida Solar Institue has done a lot of research on attics, roofing materials, insualtion, radiatain barriers and similar.They have a number of reports of radiant barriers. The last I looked at their website they radaint barrier paint was just listed in the footnotes as one type of radiant barrier. But gave no brands or how it compared to other materials..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Outdoor Lighting

Lighting up an exterior isn't just about ambiance— it's also about code compliance. Here is what the code says about safety and efficiency when it comes to outdoor lighting.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • A Postwar Comeback
  • With Swedish Arts & Crafts Precedent
  • Natural Simplicity
  • A Grand Rescue on the Coast

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • With Swedish Arts & Crafts Precedent
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data