The number of 220V outlets in my shop is rather meager. Currently only one 220V machine can be used at a time and I would like to add a dust collector that is powered by a new circuit. (As long as circuits are being added, it would be nice to add a couple of spares.) The original panel is 200A but all the breaker slots are occupied. I would like to add a second set of breakers next to the existing panel; however, I’m not sure if I should power the new panel directly from the same entrance wire. Remembering the statement that breakers are meant to protect the wire; I’m assuming that the 200A service cable should ‘protect’ the entrance cable. Is that accurate? If so, should I just hook the second panel into a sizeable breaker on the first panel?
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
The FHB Podcast crew offers expert advice on choosing the right insulation for the roof of a small, balloon-framed home.
Featured Video
SawStop's Portable Tablesaw is Bigger and Better Than BeforeHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
First check to see if your panel will accept "half-size" breakers. These are generally only available for 120V circuits, but using a few could free up slots for some 240V circuits.
There are several ways you could connect a second panel, either subpanel or "main" panel, depending on the circumstances. The most straightforward is, as you suggest, to install a large 240V breaker in the original panel and power the subpanel off of that. In that case the subpanel generally does not need a separate "main", so long as it's reasonably close to the first panel.
Thanks for your insight. Regarding the half-sized breakers, I've heard that they were somehow inferior to the full slot breakers? If it matters, the service entrance panel is a Square-D.
They are not quite as "robust", no doubt, but if they're "listed" for your panel (always double check that your specific panel is listed for them) then they've been through some pretty rigorous testing at UL et al. (Also make sure that the "max circuits" rating for your panel isn't exceeded -- it's usually about 10 more than the number of slots, for panels that accept the half breakers.
There are (or were, last I looked) half-size breakers for many Square-D panels.
Thanks again!
The answer is "It depends." Nice, huh?
If you really only need to add 1 additional 240 circuit, I would consider shuffling the existing breakers and buying skinny breakers if your panel will accept them - some Square D's do, others do not. This may free up enough space to add the needed additional circuit.
The sure thing cure is to remove the existing 240 breaker which feeds your shop and using those 2 poles to power a sub-panel - could be right next to your existing main panel or removed by some distance - whichever is most convenient.
By adding a sub-panel you will satisfy your immediate need and provide for future needs.
Bear in mind that skinny and/or piggyback breakers are sold at a premium price because they are "problem solvers". You may incur less cost in the long run by adding a sub-panel.
If I was adding a sub-panel - I would just nibble the bullet and add a 100A sub-panel with 20 poles and be done for the duration - future needs? no problem.
Smaller subpanels are also available - or you can use a main breaker panel and use that as a sub-panel, remove neutral bonding and possibly add a ground bar - frequently I can buy a 100A panel equipped with a main breaker (sometimes with a few "free breakers" included) cheaper than a 100A main lug panel. Big box stores do strange things......
Stick with Square-D QO style breakers - Square-D Homeline style maybe not so great.....
Jim
All good advice...
If it were me,I think I would pull the existing 220 breaker and replace with a 60 amp breaker feeding a new subpanel, sounds like 60 amps might meet your needs and the wire size for that isn't too awfull hard to work with or expensive (#6 or 8 ?? I dont recall).
Remember that the neutral and the ground wires should NOT be bonded together in the subpanel. You will have to purchase a separate ground bar for your subpanel.