Scott | Posted in General Discussion on April 5, 2007 08:07am

Some of you will remember my post last week about a stinky kitchen drain in this thread:

http://forums.taunton.com/n/mb/message.asp?webtag=tp-breaktime&msg=88000.29

The setup looked like this:

View Image

A number of you replied, and IMO this is the best aspect of forums like this: A problem is stated, a diverse array of opinions are discussed, and a course of action emerges. In this case big Shouts Out are in order for Mike Hennesey and McDesign (If I recall correctly, thanks to everyone else too).

In this case the solution is simple: build a parallel trap for each drain, not in series. No more stink. Like this:

View Image

Works like a charm.

Thanks.

Scott.

Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.â€


Edited 4/5/2007 9:54 am by Scott

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    Matt | Apr 05, 2007 02:21pm | #1

    I might be wrong - someone will correct me if I am, I'm sure :-) - but I think what you have done by adding the second trap is add another fixture unit to the equation and thereby overloaded the 1 1/2" pipe that goes through the bottom of the cabinet.  Or at least it looks like a 1.5" pipe.  I know this doesn't make total sense, but from my limited understanding of plumbing code, I think that is the case.  Not saying it is necessarily a problem, just trying to spark some controversial :-) conversation.

    1. User avater
      BillHartmann | Apr 05, 2007 03:49pm | #3

      This has come up in the past.And IIRC others have said that it was not legal. But mine has been like that for alsmot 30 years without any problem. And I have seen many others like it.But - "but I think what you have done by adding the second trap is add another fixture unit to the equation and thereby overloaded the 1 1/2" pipe that goes through the bottom of the cabinet. Or at least it looks like a 1.5" pipe."I don't buy it at all.No units have been added. NO change in flows have been done. In both cases you have 1.5" tail pieces being combined into a common 1.5" pipe into the DWV. No more, no less.The problem, IF ANY, has to do with the venting of the two traps.
      .
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      1. User avater
        Matt | Apr 05, 2007 11:54pm | #18

        I believe 2 traps need a 2" waste pipe.

    2. GregGibson | Apr 05, 2007 04:13pm | #4

      You're right, Matt, and I'm sure he's exceeded the allowance for that size box.  This a common problem.  People think they can cram all kinds of drains, pipe, tubing, valves into just any sized box.  The drain line will have to be de-rated.  They have special box entenders for this application.

      Greg

      1. User avater
        BillHartmann | Apr 05, 2007 04:47pm | #5

        What kind of BOX are you talking about..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. rasconc | Apr 05, 2007 04:52pm | #6

          I believe he is tongue-in-cheeking an electrical reference.

          Bob

          Edited 4/5/2007 9:53 am ET by rasconc

        2. GregGibson | Apr 05, 2007 07:06pm | #10

          Sorry, Bill.  I forgot the wink.

          ; > )

           

          Greg

      2. DanH | Apr 05, 2007 06:13pm | #8

        Yeah, you gotta worry about overheating.
        So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

  2. User avater
    BossHog | Apr 05, 2007 03:00pm | #2

    I don't know squat about plumbing.

    But I appreciate it when someone posts back to let us know how things turned out. I hope you'll keep us posted on whether or not this solves the problem.

    Always Forgive Your Enemies. Nothing Annoys Them More.
  3. bobtim | Apr 05, 2007 05:58pm | #7

    My take on the situation:

    I think the 2 traps as configured are code compliant, no increse in fixture units.

    The dw discharge location will help scour or clean the drainline, thereby cutting down or eliminating oders.

    It's tough to tell from the pictures, but the traps look to be 2" and the house drain line at the back corner looks to be 1 1/2". I always thought that drains could not be reduced in diameter. (the only exception I know of is 4" to 3" for toilets right at the sweep). If this is a optical delusion- my apoligies.

    1. Scott | Apr 05, 2007 06:57pm | #9

      >>>It's tough to tell from the pictures, but the traps look to be 2" and the house drain line at the back corner looks to be 1 1/2".No, it's a 'delusion' as you say. It's all 1 1/2". I'm going to check my code book today about the fixture unit issue.Thanks,Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

    2. rez | Apr 05, 2007 07:31pm | #12

       View Image

      Parolee # 53804

      1. Geoffrey | Apr 06, 2007 03:05am | #23

        rez..you da man!!  my eyes thank yee!!

                                                           Geoff   

        1. rez | Apr 06, 2007 03:40am | #26

          ya, but now you can see the spiderwebs on the vent pipe.View Image

          Parolee # 53804

          1. User avater
            Matt | Apr 06, 2007 04:09am | #27

            Ok - ya got me!  That's a pretty obnoxious .gif!

  4. xMike | Apr 05, 2007 07:28pm | #11

    It looks great, Scott, but why does it make a difference? It's not obvious to me why two traps in parallel limit sewer gas to the sink any better than one.
    Is it possible that you simply replaced a cracked line when you did your refit?
    Mike

    1. User avater
      BillHartmann | Apr 05, 2007 07:45pm | #13

      I think that there are two differences. One is DW connection on the tail piece. The other is fixing the negative slope IF THERE WAS..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      1. User avater
        SamT | Apr 05, 2007 07:58pm | #14

        ditto datSamT

        There are three kinds of people: Predaters, Prey, and Paladins. For the life of me, I can't see why Prey feels safer from predators by disarming and emasculating Paladins.

      2. User avater
        CapnMac | Apr 05, 2007 07:59pm | #15

        One is DW connection on the tail piece. The other is fixing the negative slope

        That's my bet, too.  The old connection allowed some quantity of stagnant water, from any source, to sit in the untrapped side.  And "grey water" has a very short smell "lifespan" at the best of times. So, the entire line from d/w to drain was open, too.  Now, that's all isolated from open air by the new trap.Occupational hazard of my occupation not being around (sorry Bubba)

    2. Scott | Apr 05, 2007 09:12pm | #16

      The problem wasn't sewer gas from beyond the trap, it was stinky junk building up in the horizontal pipe furthest from the trap. The addition of the second trap means that the only pipe before the trap is the tailpiece; no more tailpiece --> elbow --> DW drain --> horizontal before the trap.As for negative slope, nope, I had checked and rechecked that with a level. There was at least "half a bubble" of slope.It works great now. I just need to crack the code book to check up on it.Thanks all,Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

      Edited 4/5/2007 2:14 pm by Scott

      1. rez | Apr 05, 2007 09:30pm | #17

        It works great now. I just need to crack the code book to check up on it.

        snort* Now that's funny right there!

        Parolee # 53804

      2. philarenewal | Apr 06, 2007 12:28am | #20

        If your plumbing inspector hassles you for some reason about the dfu's, ask him to count the number of faucets that serve that one double bowled sink.  One kitchen sink = 2 fixture units in my code book.  There's no separate section for a double bowled sink equalling any more (at least where I am).

        Only problem I can see is what happens if someone were to use only one side of the sink out of habit and the "uphill" trap could get dry.  One fixture = one trap where I am so that might become an issue. 

        "Let's get crack-a-lackin"  --- Adam Carolla

        1. DanH | Apr 06, 2007 01:42am | #21

          Fill the space with cleaning products, toilet brushes and plunger, watering cans for houseplants, etc. No one will ever check.
          So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          1. User avater
            Matt | Apr 06, 2007 01:58am | #22

            Take another look at his pics.  Actually, I'm thinking the origin of the stinky drain is that the food strainers don't work very well in the bottom of the cabinet.  ;-)  

          2. VAVince | Apr 06, 2007 03:27am | #24

            I am going to tell the inspector!  Yep , I will call in tomorrow.  Yep I will tell!  This guy is in big trouble!

          3. dovetail97128 | Apr 06, 2007 03:37am | #25

            Just an observation , well and a question too. If his new setup were reversed wouldn't the Dw and sink suck the water out of the upstream trap and leave it dry due to suction?

            Actually won't this happen if he drains a full bowl of water out of the first sink in line ?

  5. User avater
    Matt | Apr 05, 2007 11:55pm | #19

    What's your take on having 2 traps feeding into one 1 1/2" waste pipe?

    1. plumbbill | Apr 06, 2007 05:35am | #28

      It's against the code, & very early in my career I found that out the hardway by having to repipe 85 kitchen sinks in a fire damage apt complex we repiped.

      Now in reality it probably won't be a problem, & like most things codes tend to be overkill & side with being safe than sorry.

      Code wise you would use a "continuous waste" system

      WASTE_PIC

       “When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

      1. rich1 | Apr 06, 2007 08:02am | #29

        And the stinky stuff ( bacteria ) can and do build up in vertical pipes.

      2. Scott | Apr 06, 2007 08:08am | #30

        >>>Now in reality it probably won't be a problem, & like most things codes tend to be overkill & side with being safe than sorry.Thanks, PB, I was hoping you'd drop by. The drain definitely works well and doesn't stink any more. I'm currently reading about hydraulic load, fixture units, and pipe sizing. I think it conforms with our code (BC, Canada) but will report back asap.Rez.... rolfing.....Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

      3. User avater
        Matt | Apr 06, 2007 02:12pm | #31

        >> It's against the code, & very early in my career I found that out the hardway by having to repipe 85 kitchen sinks in a fire damage apt complex we repiped. <<

        Why is it against code?

        And... I didn't quite get the purpose of the link you posted.

        Edited 4/6/2007 7:15 am ET by Matt

        1. plumbbill | Apr 06, 2007 03:26pm | #33

          Sorry about the link I just googled continuous waste pics here's the link to the pic http://www.labgeardirect.com/images/aero/aero-drain-s-21.jpg

          Chapter 10 of the UPC the end of the very first paragraph of the chaptor 1001.1

          "Not more than one trap (1) shall be permitted on a trap arm"“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          1. bobtim | Apr 06, 2007 05:38pm | #34

            88161.34 in reply to 88161.32 

            Sorry about the link I just googled continuous waste pics here's the link to the pic http://www.labgeardirect.com/images/aero/aero-drain-s-21.jpg

            Chapter 10 of the UPC the end of the very first paragraph of the chaptor 1001.1

            "Not more than one trap (1) shall be permitted on a trap arm"

             

            Plumbill

            Don't you consider this application to have 2 trap arms, thereby making it code compliant.

            As a side note,  I'm not thrilled with the idea of 2 traps when 1 would suffice.

          2. plumbbill | Apr 07, 2007 03:12am | #36

            No, a trap arm goes from the trap weir all the way to the vent, then it becomes a drain not a trap arm.

            He shouldn't have had a "stinky drain" to begin with since the branch inlet was upstream of the trap.

            His fix of puting in a "branch tail piece" is standard for that application, but didn't need to add the second trap.

            The job I first spoke of where it was a costly mistake, we installed "double wye's" with two traps & a cleanout in the middle. It made perfect sence to us & looked good, but the anal retentave inspector made us change out every last one.“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          3. Jerry18 | Apr 07, 2007 07:33am | #40

            "we installed "double wye's" with two traps & a cleanout in the middle"Bill,Your description sound just like what I did. This hasn't had a final inspection yet, but I thought I did this correctly. Am I going to have a problem?Thanks,
            Jerry

            Edited 4/7/2007 12:38 am ET by Jerry18

          4. plumbbill | Apr 07, 2007 08:09am | #41

            Well that has two seperate traps with two seperate trap arms with a common vent.

            That is quite common for back to back fixtures, although not usually exposed under a sink, but the format is legal.

            Just one problem, & it's only if the inspector gets picky, or really knows the code indepth.

            When installing back to back fixtures there are two types of fittings used. A "san-cross" like you have in the pic, & a figure "5" fitting AKA a "fixture cross" which has more slope than a "san-cross" but not as much as a "double combo".

            San cross's when used for a back to back fitting it has to be atleast two pipe sizes larger--- so an example would be back to back lavs, lavs only require a 1.25" trap arm so a 2" san cross can be used, but a kitchen sink requires a 1.5" trap arm so 2 sizes bigger would be 2.5".

            Now they don't make a 2.5" fitting so you would need to increase to 3".

            But since technicaly since you don't have 2 fixtures it should be OK, but inspectors have the final say.

            FYI if you use a fixture cross you don't have to increase the pipe sizes.“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          5. Jerry18 | Apr 07, 2007 08:57am | #43

            "the format is legal."Well that's a relief - I guess you were describing something else when you spoke of the problem you had. "FYI if you use a fixture cross you don't have to increase the pipe sizes."Thanks for the education - I thought a san-cross was OK in this situation. If he catches it (and I doubt he will) I will have to squeeze a fixture cross in there. Increasing to 3" at this point would be out of the question. Would you happen to know why the increased slope of a fix-cross is required and how the increased pipe size with a san-cross negates that need? Not really seeing what they're after on this one.BTW, That mess couldn't go in the wall because the floor framing is recessed into the foundation wall and the walls sit on top of the foundation. I didn't have the foresight to cast the drain into the foundation, so it had to come through the floor. The vent goes back into the wall. (Tried to at least make it neat).Jerry

          6. plumbbill | Apr 07, 2007 06:25pm | #47

            The double "wye" we put in was horizontal going into the stub-out comming out of the back of the cabinet. That is also illegal, the 2 trap arm problem, & you can't put a double "wye" in horizontaly. When we got tagged for it the inspector just brought up the 2 trap arm violation though.

            The reason for the increased pipe size when using a san-cross is so that when draining a large flow it will have a better chance of going down the drain verses going into the other side branch.

            The fixture cross has more of a downward slope directing the waste down instead of straight across to the other side inlet, it is real similar to a double combo.

            But the double combo does not allow the venting action to happen since its' opening is below that of the side inlet, which could siphon the trap under the right circumstances.

            So that's why they introduced the fixture cross its' vent comes off the fitting above the bottom of the side inlets, if you go to this link from Tyler¯ on page 12 in the bottom right hand corner is a fig5 fixture cross. http://www.tylerpipe.com/utility%20catalog%202007/pg12-13.pdf

             “When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          7. Jerry18 | Apr 07, 2007 02:25pm | #44

            "But since technicaly since you don't have 2 fixtures it should be OK"...just thought of another potential problem. Would this be considered two fixtures or one?Thanks,
            Jerryhttp://forums.taunton.com/n/docs/docDownload.aspx?guid=4AB6AD5C-DAA6-4B42-87B4-C00131B6C4C3&webtag=tp-breaktime

            Edited 4/7/2007 7:28 am ET by Jerry18

          8. Jerry18 | Apr 07, 2007 02:26pm | #45

            Try again...

          9. plumbbill | Apr 07, 2007 06:28pm | #48

            No , still a single kitchen sink.

            When doing commercial kitchens the fixture count changes when multiple compartment with multiple faucets are used.“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          10. User avater
            SamT | Apr 07, 2007 07:06pm | #49

            When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works. Nigel Calder,  editor of New Scientist

            But they do show a high expertise in manipulating the public to achieve their own desires.SamT

            There are three kinds of people: Predaters, Prey, and Paladins. For the life of me, I can't see why Prey feels safer from predators by disarming and emasculating Paladins.

          11. ChuckW | Apr 07, 2007 10:00pm | #50

            Careful, that's Tavern Talk.:)

          12. Jerry18 | Apr 08, 2007 05:54am | #52

            Bill,Thanks for the explanation - looking at diagrams for both fittings, I can see what you mean. If the inspector doesn't catch it, do you think it is worth correcting. In case it might influence your answer - except for the tailpieces, everything is 2". Not to nitpick, just trying to learn, but this picture shows that although the sink is one piece, it is two bowls with two faucets. It still only counts as two FU's?JerryEdited 4/7/2007 10:55 pm ET by Jerry18

            Edited 4/7/2007 10:56 pm ET by Jerry18

          13. plumbbill | Apr 08, 2007 07:07am | #53

            No, I wouldn't fix it unless the inspector tagged it. Worst case scenario if you dump an extremely large amount of water down one bowl & the drain can't handle the flow it will just back up into the other bowl which is the same fixture.

            Yes your sink is 2 fu's, according to the UPC table 7-3 a residential kitchen sink is a residential kitchen sink, with or without a garbage disposal & or a dishwasher hooked up to it. I have put as many as 4 faucets on a residential kitchen sink--- standard hot/cold faucet, instahot, chilled glass filler, & a separate deck mount pot filler.

            Now if it was a commercial kitchen sink in a commercial building, then the rules change drastically.“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          14. User avater
            Matt | Apr 07, 2007 03:05pm | #46

            Question:  Is that black tube the dish washer drain?

            BTW - nice to see plumbing run neatly through the floor of the cabinet.  In the OP's pic, did you notice how the cabinet had to be chopped based on where the plumber had set his DWV.  I HATE that.

          15. Jerry18 | Apr 08, 2007 05:45am | #51

            Yes, that is the DW drain.Jerry

          16. User avater
            Matt | Apr 08, 2007 02:54pm | #55

            >> Yes, that is the DW drain. <<

             

            Does it at some point go up to the very top of the cabinet - nearly touching the bottom of the counter top, or is there an "air gap" somplace in the line? 

            BTW - like I said at first, my knowledge of plumbing code is pretty weak, but I'm 90% sure our local plumbing inspectors would accept the 2 P-traps and the 2" drain pipe - that based on what I have seen them pass before - many times.

          17. Jerry18 | Apr 09, 2007 07:00am | #56

            "Does it at some point go up to the very top of the cabinet..."Matt,Thanks for your input on the two traps and the polite question about my DW drain. :-) There is no air gap and the drain line does not loop up to the underside of the counter top near the sink, but it does behind the DW, so I should be OK. Correct?Jerry

          18. User avater
            Matt | Apr 09, 2007 02:12pm | #57

            Yes - you should be OK

          19. ChuckW | Apr 06, 2007 10:21pm | #35

            Hey Bill,

            What do you do with a garbage disposal in a dual sink?  The waste would shoot into the second sink.

            I plumbed mine with two traps too to stop that mess. 

          20. plumbbill | Apr 07, 2007 03:15am | #37

            Depending on configuration, we mainly use a continuous waste set up of some sort either a center outlet or an end outlet.

            The "T" that joins the two together will have a diversion plate inside it of some sort.

            More common on pvc ones than brass.

            My DMIL has two traps, but also has two stub outs under the sink.“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

      4. Scott | Apr 07, 2007 03:51am | #38

        Hi Again PB.So I dug out my trusty code book and can't find anything that outright prohibits two traps. For those who are interested, here's an excerpt:1) Except as provided in Sentences (2), (3), (4), and (5), and in Article 7.4.5.2, every fixture shall be protected by a separate trap.2) One trap may protect
        (a) all the trays or compartments of a 2- or 3-compartment sink,
        (b) a 2-compartment laundry tray, or
        (c) 2 similar single compartment fixtures located in the same room.blah blah blah.... sentences 3, 4, and 5 go on to talk about one trap may protect multiple floor drains, shower drains, and other details unrelated to this. There is no mention of one trap per trap arm. I don't see anything that says you can't provide a trap for each fixture.However, one of the previous posters mentioned that fixture units may be an issue. Our code does indicate that 1.5 FU's (don't you love that acronym) are the limit here. Oh well.....BTW, the smell is gone.Thanks all,Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

        1. plumbbill | Apr 07, 2007 06:34am | #39

          I'm gonna guess that's from the IRC.

          Here in Wa state the IRC is not adopted for plumbing, & electrical it is for enverything else though IIRC.

          The code I quoted from is the 2003 UPC with the updated amendments.

          As far as fixture units you're OK, cause the sink FU's over ride the trap fu's.

          The only time a trap is counted for fixture units is when it is used for an indirect waste recepticle.“When politicians and journalists declare that the science of global warming is settled, they show a regrettable ignorance about how science works.” Nigel Calder,  editor of New Scientist

          1. Scott | Apr 07, 2007 08:25am | #42

            Thanks, I hope I can return the favor.All the best,Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

  6. eleft | Apr 06, 2007 02:15pm | #32
    The outlet of the trap is lower than the sink drain connection on the stinky drain, this could have allowed the water to siphon  from the trap.
     
    al
  7. toolbear | Apr 08, 2007 09:42am | #54

    Very pretty work there under the sink.  So clean and well-lit.  So unlike mine.  Even looks like the angle stops are solid brass vs. The Usual Junk.

    I replaced my rotting collection of brass kitchen drains with 1.5" ABS.  You might find that you can screw a 1.5" adapter onto the drains and run 1.5 all the way up.

    I have Fernco 1.5-1.5 connectors at the stub-out and under the drains so I can just back off the clamps and remove the whole assembly when there is a problem.  This has worked so well that all the sinks now have something similar.  No more leaking compression fittings.  No more cheesey thin white tubes.

    The ToolBear

    "Never met a man who couldn't teach me something." Anon.

  8. MikeHennessy | Apr 09, 2007 02:50pm | #58

    Regarding feeding a double-bowl sink and a DW into a 1-1/2" drain -- that's always been approved by my inspectors. (Haven't checked the code, though.)

    Only one comment on your revised setup. It looks to me like you fed your one trap into the horizontal with a horizontal Tee. That would get nixed -- should probably be a wye.

    Check out the photo in post #41. Methinks that's the "kosher" way to do it.

    Mike Hennessy
    Pittsburgh, PA

     



    Edited 4/9/2007 8:17 am ET by MikeHennessy

    1. Scott | Apr 10, 2007 06:21am | #59

      Hi Mike.>>>Check out the photo in post #41. Methinks that's the "kosher" way to do it.Yes, I'd have to agree that that setup would flow better, but I've got the problem of a rough-in that is way off center of the sink cabinet (darn plumber! and my plans even showed millwork!). You may have noticed my cabinet-ectomy work in the pics; there's no room for a wye. Nonetheless, it seems to work really well. I even dumped big pots of water down both sides at once. No issues.Thanks though, you're the first to notice that.Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Simple and Discreet Countertop Power

A new code-compliant, spill-safe outlet from Legrand offers a sleek solution for a kitchen island plug.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data