strange photocell light control failure

brucet9 | Posted in General Discussion on October 29, 2008 03:05am

OK sparkies, can you solve this one?

-Two adjacent 5-unit apartment buildings on separate electric meters.
-Photocell switches controlling walkway/stair landing fluorescents as well as sodium vapor lights in the alley ; total load about 600W on one and 1070W on the other.
-In service for 20 years; failed on the same day last week.
-Circuit breakers had not tripped.
-line voltage to both controllers reads 120V; voltage on load side of controllers 0V.

“OK”, I say to myself, “must have been a voltage spike from Edison that disabled the sensors.”

I bought two new 2000W controllers (http://www.amertac.com/), installed one of them, put tape over the light sensor window, and the lights came on, all except two, which I figured must have had burned out bulbs.

I then replaced the other sensor and its lights came on. Great, so I buttoned up the boxes where the connections were made and took off the tape and the lights went off just as they should.

I changed bulbs in two fixtures and taped the sensor to make it turn on, but nothing lighted, not even the lights that had worked before. I taped the other sensor and its lights did not come on either.

So, 20 years without problems, then simultaneous failures on different circuits fed by different meters. Replacement controllers work once but will not switch on again after the first test run. Amertac customer support has no idea; my problem is not part of her script. They say maybe out-of-box failure; return the units to HD.

Two identical failures following similar failures of the original devices suggests something other than out-of-box failure to me.

Any ideas?

BruceT
Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. MikeSmith | Oct 29, 2008 03:13am | #1

    those stupid lights 

     i've spent more time  fooling with those

    worst is when they're on a 3-way

    get call-back after callback... sensors... internal switches... time delay

    brrrrrrrr...  i hate 'em 

    Mike Hussein Smith Rhode Island : Design / Build / Repair / Restore
  2. User avater
    BillHartmann | Oct 29, 2008 03:25am | #2

    Open then up and see if you can see a failure mode.

    I would measure the voltage.

    And I would bypass then and measure the current.

    Could be poltergise.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. brucet9 | Oct 29, 2008 04:22am | #3

      "Open then up and see if you can see a failure mode."What would I look for, poltergeist droppings? What's in there, anyway, some sort of relay, I assume?"And I would bypass then and measure the current."I have a Fluke meter that can measure amperage, but what would you expect I might find? The 15A circuit breaker should limit amperage to below the 2000W service rating of the device. BruceT

      1. User avater
        BillHartmann | Oct 29, 2008 07:07am | #10

        The ones like that I have seen are fairly simple with a cadmium sulfide photocell and a bimetalic switch with small heater.http://en.wikipedia.org/wiki/PhotoresistorWhen the sun is out the resistance decrease and heats up the switch and it opens.When you first turn power on the heater is cool and the switch is closed for about 1-2 minutes. That is a way to the light during the day.But you need the power to be off 5-10 minutes for it to cool off.There is no "programing" on them.This is a spec for a CS cell. But probably nothing like the one in the unit.http://www.engineering.uiowa.edu/~ece195/2005/labs/pdvp9001.pdfTrying to think of the failure modes.If it tried to close on a extreme load the switch or terminals might be vaporized. Another possibility is that the CS cell shorted. I don't know if a voltage spike could do that or not.Common time inverse breakers will allow large amounts of current for short times without tripping. That is why you can run a 1 1/2 table saw on a 20 amp circuit. It might draw 80-100 amps on startup.You should be able to measure the resistance of the cell and of the heater if you can get it appart without destroying it..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  3. USAnigel | Oct 29, 2008 04:36am | #4

    Bypass the control unit with a switch and make sure all works. With the lights on check the voltage and currant flow, you might have a failing neutral causing the controllers to "pop".

    Try removing lamps, this should only effect currant reading, voltage should stay the same. This should help you track down the problem.

    1. brucet9 | Oct 29, 2008 05:46am | #6

      "...you might have a failing neutral causing the controllers to "pop"."Failing neutrals that suddenly showed up in two different circuits in separate buildings on separate meters?"Try removing lamps..."What is your suspected culprit? Why would defective lamps have caused the same problem at the same time on two different systems?That's why this thing baffles me. The cause would seem to be something that affects photocell controllers but not anything else and probably outside the house wiring systems since it occurs in two different buildings at the same time.BruceT

      1. DanH | Oct 29, 2008 05:54am | #7

        Like I suggested above, I suspect that a power glitch may have "programmed" the original controllers, and flipping switches may have done the same to the new ones.
        Corporation: n. An ingenious device for obtaining individual profit without individual responsibility. --Ambrose Bierce

      2. USAnigel | Oct 29, 2008 06:09am | #9

        I'm thinking along the lines of a common supply somewhere. Are these two buildings near to each other feed from different breaker panels?  I'm thinking bad connection somewhere causing a surge.

        1. brucet9 | Oct 29, 2008 07:31am | #11

          The buildings feed from different Edison Co. meters.
          BruceT

  4. DanH | Oct 29, 2008 04:40am | #5

    Keep in mind that many of those units have a "secret code" -- if you switch them on and off rapidly two times it turns the light on in the day, eg, and on and off rapidly three times turns the light off at night.

    So try simply turning both units off at the breaker (or any switch ahead of the control) and leaving them off for a minute or two, to reset things.

    Corporation: n. An ingenious device for obtaining individual profit without individual responsibility. --Ambrose Bierce
    1. brucet9 | Oct 29, 2008 05:54am | #8

      This is not a porch light controller. There is no code on this thing. (http://www.amertac.com/)When it sees light, it switches the circuit off. When it sees no light, it switches the circuit on.I'm beginning to think space aliens are taking control. I may make little tinfoil hats for the controllers to block those cosmic signals.
      BruceT

  5. User avater
    Jeff_Clarke | Oct 29, 2008 09:09am | #12

    Not a sparky ... but I think I've found your problem:

    View Image

    1. brucet9 | Oct 29, 2008 09:17am | #13

      LOLBruceT

  6. DaveRicheson | Oct 29, 2008 04:34pm | #14

    http://www.amertac.com/content/products.nsf/Lighting%20Controls%20&%20Dimmers/Direct%20Wire%20&%20Commercial%20Controls/AT15BC/pAt15BC.htm

    Is that the one you purchased?

  7. BryanSayer | Oct 29, 2008 06:06pm | #15

    I can't help with your problem, but I'm wondering if you might be able to help with mine.

    Can you recommend a motion detector controller for two 500w halagen lights? I want dusk-to-dawn motion detection. I have had several units from RAB and they seem to last about two years. I'm not sure what is going wrong with them. I may switch to 300w bulbs.

    1. Clewless1 | Oct 30, 2008 03:16pm | #19

      You sure they are halogen and not HID? HID would have problems w/ e.g. motion sensor, halogen should not (I think). Halogen is a type of incandescent (non ballasted).

      1. BryanSayer | Oct 30, 2008 05:31pm | #20

        That is a good question. The light bulbs are those little tubes with the contacts on the end. The fixture has spring contacts. Like these:
        http://www.1000bulbs.com/4-in.-Double-Ended-Recessed-Single-Contact/So I take that to mean halogen. In part I got those because my work lights take the same bulb. If I need to replace the fixtures (yet again) I will, but these things are up about 20' and a pain to get to. So I want something that will keep working.

        1. Clewless1 | Oct 31, 2008 02:08pm | #21

          hmmm ... dunno. I THINK the halogen should be OK w/ a motion sensor. Couldn't open your link (i.e. it led nowhere). If the lamp has a pin/contact on both ends, I think that means it's a halogen. Ultimately a call the the lamp manuf tech rep may answer your question.

          Edited 10/31/2008 7:09 am ET by Clewless1

  8. DaveRicheson | Oct 29, 2008 07:36pm | #16

    Follow up on my first reply.

    I pulled the instruction sheet on an Intermatic photo cell. About the same as the one you installed.

    The trouble shhoting chart shows two possible cause:

    (1) photo control damaged by lightning or other high energy transient. (likley the cause of the first ones failure)

    (2) With high pressure sodium or mercury vapor you can be experienc the trouble from the end of-of-life failure of the lamp and/or ballast.

    A third possible is to high a line voltage. this would cause the photo cell to fail in the off mode.

    You replaced two hps bulbs, you said. You may have additional bulbs at the end of thier life or a ballast or sevral also reaching that point.

    1. brucet9 | Oct 30, 2008 09:31am | #17

      I replaced fluorescent Edison medium base bulbs. The HPS were still working.Where did you find the trouble-shooting info? All I found on their site was the same thing that came in the package; mentioned line voltage surges (failing in on, not off position) but nothing about HPS.BruceT

      Edited 10/30/2008 2:36 am by brucet9

      1. DaveRicheson | Oct 30, 2008 12:55pm | #18

        We have sevral different photo cell brands in our stock cabinet. The Intermatic was the closest one to what you have. I just pulled the instruction sheet out of one.

        The Intermatic fail on when line voltage is too low, according to thier trouble shooting chart.

        Had another thought. Is thier a lighting contactor on either or both of those circuits?

        We have them on most of out exterior lighting circuits. One or two of them are fused. If you have one, a blown fuse in the contactor circuite could be the problem.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Simple and Discreet Countertop Power

A new code-compliant, spill-safe outlet from Legrand offers a sleek solution for a kitchen island plug.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data