Sub-panel grounding

truck8 | Posted in General Discussion on August 15, 2006 04:46am

I am setting up a 39′ camper on a permanent foundation and electric subpanel. Here is my electric set up.  3 wire underground feeder 2/2/4 to a subpanel outside the camper. Subpanel has ground/neutral bonded and a #4 copper to a ground rod, and 2 50 amp breakers. This feeds 2 factory installed 50 amp subpanels in the camper which have separate ground/neutral (not bonded). These were designed to be plugged into 2 separate 4 wire receptacles at a camp site.  What to do in these panels? Do I bond ground/neutral or leave as is? Thanks

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. brownbagg | Aug 15, 2006 05:14am | #1

    2/2/4 not legal

    2/2/2/4 legal

    1. DanH | Aug 15, 2006 05:19am | #2

      Is it possible that this could be interpreted as an "outbuilding", meriting its own ground and bonding strap?
      If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

      1. User avater
        BillHartmann | Aug 15, 2006 06:15am | #3

        I saw a similar discussion a while back on a different forum.They say that the code reads separate Structure not building. But I have no looked it up.The discussion in that case was the meter and a disconnect was on a pedistal some distant from the home.The home was a separate structure from the pedistal so that it could be treated as a main panel.

      2. JohnSprung | Aug 15, 2006 10:06pm | #5

        The criterion for a separate building is that it's more than 5 ft. from the main building. 

         

        -- J.S.

         

        1. DanH | Aug 15, 2006 11:44pm | #6

          The question is whether the situation under discussion should be considered a "subpanel" or not. If it must be considered a subpanel then 3+1 cable is needed and no bonding in the panel. If it can be considered to be a separate structure then only 3 wire/no ground cable is needed, but a ground electrode system must be installed and the neutral-ground bond strap must be installed in the panel.I don't know the answer in this situation, where the "building" is a trailer pedestal.Beyond that, there likely are some special paragraphs in the Code regarding trailers ('scuse me -- modular structures), though for consistency they're no doubt buried in some unrelated section.

          If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          1. brownbagg | Aug 16, 2006 01:47am | #7

            a seperate structer is five feet and nothing metal connecting each bldg, no tv coax, no telephone wire, no carport, awning walkways. but also local inspector required everything south of meter is sub panel, no matter if in a seperate bldg or not. and all subpanel gets 4 wires. the seperate bldg requires a ground rod but netrual and ground cannot be bonded.

          2. DanH | Aug 16, 2006 04:44am | #11

            Simply being south of the meter doesn't force something to be treated as a subpanel (in the sense of not having a bonding screw). In fact, the code appears to REQUIRE that a separate building have it's own grounding electrode system AND be bonded to the "grounded" (neutral) conductor. (And, by implication, not be bonded to the incoming grounding electrode.)Unfortunately, the code section that applies here (250.24 in my ancient copy of the NEC) is fairly difficult to interpret.

            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          3. User avater
            BillHartmann | Aug 16, 2006 02:05am | #8

            There is an NEC section on mobile homes. But I have never looked at it and don't know the RV would fit that or not.That is why I did not bother replying to the question.

  2. Brooks | Aug 15, 2006 09:14pm | #4

    I don't think the sub-panel outside the camper should have the bridge in place. And certainly 2/2/2/4...
    -- Brooks

  3. truck8 | Aug 16, 2006 02:46am | #9

    OK, I guess I left out a part of the set up. Sorry.  The 3 wire feeding the 1st sub-panel at the outside of the camper comes from a 100 amp main disconnect at the power pole and has separate ground/neutral. It then runs 80' to the camper.  Does this shed a different light on the question, and in my part of the country (very rural) where there is not much of an inspection on anything built, I guess I am not much concerned with code, but will it work safely. Thanks

    1. brownbagg | Aug 16, 2006 02:54am | #10

      till its burns down

      1. truck8 | Aug 16, 2006 06:08am | #22

        Why would you see it as unsafe?  When the detached structures main panel is supplied by a feeder that has no equipment grounding conductor run with that feeder, from the main structure to the detached structure (as in my case), then the neutral bar and equipment grounding bar must be joined or married together as one entity. Article 250-32-B-2 & 250-102-E  The neutral bar must be married or joined together with the metal of the panel box and also the equipment grounding bar. Article 250-32-B-2.

        If there is no grounding electrode system serving the detached structure (as in my case) then you must install a new grounding electrode system as described in Article 250-50. (as in my case).  If you know something that I don't, please let me know. Thanks

    2. DanH | Aug 16, 2006 04:47am | #12

      You say "3-wire" and you say "separate ground/neutral". Enumerate the wires.

      If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

      1. Joe Sullivan | Aug 16, 2006 05:20am | #13

        Guys:Last week I had a conversation with a master electrician in Michigan who has worked on the code. He said that code does require an equipment ground, hence, 4-wire for 240 power. I didn't ask him, but was under the impression that the grounding bus is only bonded to the neutral wire at the main box, and at other locations, if there is a grounding electrode, it is just that, ground. According to them as knows, to reground the neutral at a separate building can cause real problems.Anyway, I am not an electrician, just a guy with barns and outbuildings who trieds to get advice to do it right. If I am confused, I'd like to hear about it.J

        1. User avater
          BillHartmann | Aug 16, 2006 05:31am | #15

          JoeWhat he said is not absolutely true. That is unless MI has modified the NEC in that area. I understand that WA has.But the code allows for 2 cases.If there is no other metalic connections (such as water pipes, tv cable, phone) between the two structures then the sub-panel in the 2nd structure can be treated as a service enterance with only 3 wire feed and the neutral bonded to the ground.Now a 4 wire feed and unbonded neutral is more flexible for future needs and as I said some place always require it. But not in the NEC.There are also some special grounding rules for animal barns, but I really don't knwo what they are.

          1. Joe Sullivan | Aug 16, 2006 05:44am | #19

            Actually, Bill, my conversation with the master electrician was in connection with animal barns.  Someone o this website warned me, and I talked with the electricial as a result of the warning.  Seems under the wrong circumstances, a regrounded neutral can result in shocked or dead livestock on concrete floors.  I am not the best one to try to eaplain this, but perhaps whoever warned me in the first place will chime in.

            However, he strongly advised me to change out the present 3-wire 240 feed to my garage and workshop, and I thought he said code called for it.

            In any event, code or no code, four conductors is a better way, if not a required way, wouldn't you agree?

            J

          2. DanH | Aug 16, 2006 06:06am | #21

            "When two or more buildings are supplied by a grounded system from a single service equipment [ie, meter], each building shall have a grounding electrode connected to the ac system grounded circuit conductor on the supply side of the building disconnecting means.This appears to say that the building ground should be bonded to the neutral ("grounded conductor") in the building's panel. There's no mention of a separate grounding conductor. The diagram in the section shows three buildings with no ground wire between, only hot/hot/neutral.There is an EXCEPTION to the above, in that buildings without livestock are permitted to have the fourth (ground) wire and forgo the grounding system (though the ground wire must still be bonded to any pipes, etc, in the building).

            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

        2. DanH | Aug 16, 2006 05:44am | #18

          There is a definite exception for outbuildings. When and how it should be applied is the fuzzy issue.
          If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

      2. truck8 | Aug 16, 2006 05:24am | #14

        Separate ground/neutral is at the power pole/meter/100 amp main disconnect location.  From there 3 wires 2/2/4 run to sub panel.

        1. truck8 | Aug 16, 2006 05:31am | #16

          Sorry on that last post. My error. Ground/neutral are bonded at main panel. 

        2. User avater
          BillHartmann | Aug 16, 2006 05:32am | #17

          That is fine for you appliacation.But I don't know anything about mobil home connections so I will not comment past the panel.

        3. DanH | Aug 16, 2006 05:50am | #20

          Well, first off there would be some question whether #4 is adequate for a neutral in a #2 circuit.That question aside, it sounds like you should install a grounding electrode system at the pedestal and treat the incoming cable essentially like a service entrance, with bonding screw installed on the panel. This would appear to be in compliance with code, absent something to the contrary in the trailer section of the code.But this is a fuzzy area.

          If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madisonqu

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Eichlers Get an Upgrade

Performance improvements for the prized homes of an influential developer who wanted us all to be able to own one.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels
  • FHB Podcast Segment: Hand Tool Sharpening Tips
  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data