subpanel disconnect

johnnyd | Posted in Energy, Heating & Insulation on August 25, 2003 09:48am

I am serving two subpanels from a Square D main entrance panel (I would call it a “distribution panel” or “DP#1”) that has facilities for breaker and “pass-though” connections. These are both de-energized with a single 200 amp breaker.

So I am serving one subpanel (SB#1) in the main entrance building with a 100 amp breaker in DP#1, and another subpanel (SB#2) in a remote building with a three conductor underground cable connected to the pass-though lugs and terminating in an identical distribution panel (DP#2)currently mounted on the remote building where the connection to (SB#2) is made.
Am I clear so far?

I need to completely de-energize the underground cable and DP#2/SB#2 because I am adding an addition to the remote building which will require excavation in the area where the cable runs. I will also need to re-locate DP#2 when construction is finished.  I will be able to serve temporary power to the remote building via extension cords from the main building (~50 feet).

So the question is: In the main distribution panel the two hot wires are bolted to the pass through lugs. No problem, I can de-energize those with the 200 amp entrance breaker OFF and then remove the wires from the lugs and tape them off. But the neutral is bolted to a lug up at the top, between the two always-hot lugs coming from the meter. DO I NEED TO DETACH THE NEUTRAL? Seems like I can leave that be because there is no way that neutral will ever be energized with the two hot wires detached.

By the way, this whole setup was installed by a licensed electrician with adequete wire sizing etc. and inspector has approved.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    SamT | Aug 25, 2003 10:18pm | #1

    I would disconnect the neutral and tape all three wires together and position them so the would pull out easily in case the excavator hooked the underground wires/conduit.  then I would remove the conduit nut from that run.

     It is not unreasonable to think that a backhoe could pull the whole DP#1 off its' mounting.

    SamT

    Be Brave, Be bold.
    Do Right, Do Good.
    Don't lie, cheat, or steal.
    Especially from yourself.

    1. User avater
      johnnyd | Aug 25, 2003 10:41pm | #2

      Glad I asked! Although he will have a helper (might be me!) to pull the wire up as he digs.

      What size hex tool should I get to loosen that lug screw?  It's a recessed hex screw.

      Maybe I should get a whole set.

      1. User avater
        SamT | Aug 25, 2003 10:57pm | #3

        Muh man, you're gonna have to get the electric compny involved with this to pull the meter since there is no disconnect at that level.

        Samt

        Be Brave, Be bold. Do Right, Do Good.Don't lie, cheat, or steal.Especially from yourself.

        1. User avater
          johnnyd | Aug 25, 2003 11:12pm | #4

          But the hot wires I need to disconnect are connected to the pass-through lugs on the downstream side from the main breaker, which I can turn OFF.  It's just the neutral that's up at that level.  Looks like the lugs up there are designed (protected on each side from the hot lugs) so you could get a tool in to loosen the hex screw on the neutral without pulling the meter. That's one of the reasons I have this set-up...so I could disconnect myself when I needed to move DP#2. 

          That proximity is what makes me want to leave it be, and why I haven't gone ahead and detached already.

          I could be wrong, though...just don't want to be dead wrong.

          1. User avater
            SamT | Aug 25, 2003 11:34pm | #5

            OK.

            I don't know the size allen you'll need, but.

            Go find a new panel at the store and measure it.

            You should be able to find an appropriate tool at a large electrical supply house, get a pair of rubber electricians gloves, wear rubber boots and have at it.

            Just remember that I'm probably just a smart alek 12yo stealin' time at my daddy's computor and you do this at your own risk! I am not responsible for anything!!!!!

            SamT

            Be Brave, Be bold. Do Right, Do Good.Don't lie, cheat, or steal.Especially from yourself.

          2. User avater
            johnnyd | Aug 25, 2003 11:44pm | #6

            OK OK, thanks for the info and disclaimer.  So you're tellin me that the neutral is NOT hot, as I believe, and the only risk I'll be taking is getting sloppy with a tool too close to the hot lugs? Oh and then moving that big stiff wire around in there. 

            Maybe I'll get the electrician out to do this after all.  Thanks.

          3. User avater
            SamT | Aug 26, 2003 12:29am | #8

            Maybe its hot, maybe its not... depends. its supposed to not be hot, I can tell you that.

            Since you are going to get an electrician, I'll admit to being a little older tha 12yo.

            SamT

            Be Brave, Be bold. Do Right, Do Good.Don't lie, cheat, or steal.Especially from yourself.

          4. Len | Aug 25, 2003 11:49pm | #7

            It happens to be the largest one on the allen key set. 3/8" I believe. A rubber handle T wrench is the best for this.

            Please be very careful.

            Len

  2. 4Lorn2 | Aug 26, 2003 04:39am | #9

    I would cut the neutral and the hot, after turning off and double checking that they really are off, near where they come into the panel. From what I gather the entire feed will need replacing so there is little sense to taking the time to save the extra length of the hots and taking time to tape them off. I might wrap a few turns of tape around the lot coming in if length remained but often cutting them off at just an inch or two is quickest. Makes sense to insulate any lengthy tails to prevent fireworks if they wander but stubs, especially when they are soon to be replaced with the new feed, are generally well behaved. When the new feed is pulled in pulling the old stubs out will be easy. 

    I might be tempted to keep one intact, I like to use the ground, if present, to have something to help pull in the new feed. The ground is likely to be thinner and more pliable so it is easier to use as a pull wire.

    The scrap hot tails, after cutting where they enter the panel, I would remove. The neutral I would leave alone if: 1) there are neutral lugs available to receive the new feed. 2) if the abandoned neutral tail is not in the way or likely to wander. I would take care to insulate the tail where the cut was made as this end is most likely to drift into live busses or otherwise get into trouble but tucked neatly into a corner of the panel I think it is a minimal concern. If at some later date the meter was pulled removing this piece would be simple but presently it would not be my priority.

    When and if you remove the neutral line going to the out building from its lug make dead sure you do NOT disconnect, damage or otherwise compromise the neutral connection to the panel. In some cases both cables will be under a single lug necessitating loosening the lug. Make sure you remake the connection from the meter. The integrity of this connection is the most important of the three coming from the meter. Loosing a main neutral connection allows voltages to drift. Fires are sometimes a result.

    1. User avater
      johnnyd | Aug 26, 2003 04:24pm | #10

      Thanks for your input.  Perhaps I was not clear in explaining this project...let me try again. 

      The feeders in the the main entrance/Distribution Panel # 1 (DP#1) only need to be disconnected so I can move DP#2.  So this is temporary until DP#2 is remounted and new connections made at the end of the original but somewhat shorter cable.  This is the cable that is currently running from DP#1 underground supplying the remote (~50 feet) building.  This is the cable that needs to be moved during construction, and it will be re-used once construction is complete.

      I don't have a problem with detaching anything in DP#2 once it is completely de-energized, moving and re-mounting the panel, or in re-making those connections. Once the cable is detached from the panel and removed from the conduit, it will be coiled safely to the side until the addition is framed and sheathed.  This will be sevral months.  It will NOT be energized until it's complete.

      Meanwhile, during construction,I still need power in the main building, so will need to turn the circuit breaker back on once I'm done with the disconnect.

      My question is with the neutral feeder that provides the neutral for DP#2.  It is connected to the main neutral lug at the top of DP#1 between the two hot lugs for the feeders from the meter.  I would like to leave that alone for three reasons: #1...Why mess with the integrity of the all-important neutral connection from the meter,  #2...that lug is awfully close to the two always-hot lugs to be poking around in there with a tool, #3...it won't have any current carrying potential once the hots are disconnected, taped and tucked away.  The hots are easy because they are bolted to the pass-through strips/lugs at the bottom of the panel, which can be de-energized via the main breaker.

      Does that make more sense?

      Thanks again.

      Edited 8/26/2003 9:28:30 AM ET by johnnyd

      1. marv | Aug 27, 2003 12:16am | #11

        IMHO -

        Any neutral wire that requires an allen wrench of any size, should only be removed by someone who knows what he is doing! 

        How 'bout sending us a picture.

        1. User avater
          johnnyd | Aug 27, 2003 03:47pm | #12

          I agree.  I checked with the inspector, who is familiar with this setup, he said go ahead and leave the neutral connected.

          Thanks, all for your advice.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Mortar for Old Masonry

Old masonry may look tough, but the wrong mortar can destroy it—here's how to choose the right mix for lasting repairs.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations
  • A Closer Look at Smart Water-Leak Detection Systems
  • Guest Suite With a Garden House

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data