Switched duplex outlet

richardi | Posted in General Discussion on June 20, 2007 02:44am

Hello –

I thought I read that a switched duplex outlet will have a minimum amount of current running through it even when the switch is off.  Is that true?

My garbage disposal trips my GFCI circuit breaker as soon as I plug it into the the switched receptacle.  Is it time for a new disposer?

Thanks,

Richard

 

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. pm22 | Jun 20, 2007 03:43am | #1

    Your GFI breaker may have been wired incorrectly. The neutral for the circuit goes to the breaker and not the neutral bus bar. The curly white wire goes from the GFI breaker to the neutral bus bar to complete the circuit.

    If your neutral wire goes directly to the neutral bus, the GFI will only see the hot going out and nothing coming in on the neutral side and will immediately trip due to this gross imbalance.

    As for whether a switch will allow a slight current through: it better not.
    However, certain evil occupancy sensors will use the ground as a return path and will use a slight amount of juice to operate their stupid electronics.

    ~Peter

    1. User avater
      SamT | Jun 20, 2007 03:46am | #2

      Well, that was as clear as mud.SamT

      Praise the Corporation, for the Corporations' highest concern is the well being of the public.

    2. richardi | Jun 20, 2007 03:52am | #4

      Peter -

      Thanks for the reply.  The GFCI breaker was/is wired correctly; the black and white to the load and neutral connectors, respectively, on the breaker and the pigtail to the ground bar.

      Richard

       

      1. BryanSayer | Jun 28, 2007 12:47am | #17

        I had a GFCI breaker that just did that. The slightest load on a dedicated circuit tripped it. We just had to replace it.

        1. richardi | Jun 28, 2007 04:26am | #18

          I originally thought it was the breaker, too.  So I replaced it and I still had the immediate tripping problem which I traced to be the disposal dying and an incorrectly wired switched outlet.  I've fixed the outlet and will replace the disposal tomorrow night.

          Thanks for your post.

  2. User avater
    SamT | Jun 20, 2007 03:49am | #3

    1) Better be false, or you have a bad switch.

    2) Plug something else into the outlet and see what happens. Use a lamp, then a toaster or coffee pot.

    SamT

    Praise the Corporation, for the Corporations' highest concern is the well being of the public.

    1. richardi | Jun 20, 2007 03:58am | #5

      SamT -

      Thanks for the reply.

      The switch works for a light and/or a radio.  The garbage disposal trips the GFCI even witht the switch off.

      Richard

       

      1. User avater
        BillHartmann | Jun 20, 2007 06:03am | #6

        " on the breaker and the pigtail to the ground bar."It should not be connected to the ground bar, but rather to the neutral bus.But if this is a main panel then the ground bus is the neutral bus is the ground bus."The switch works for a light and/or a radio. The garbage disposal trips the GFCI even witht the switch off."The neutral is connected to the ground inside the disposal.It might be an internal fault.But check the cord connects and specially look for an stray "wiskers" of the stranded cord wire that might be sticking out or a nicked insulation..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. richardi | Jun 20, 2007 12:54pm | #7

          Bill -

          Thanks for the reply.

          This just started happening last week.  I check all of the outlets on the circuit until I discovered the fact that just plugging the disposal into the switched out tripped the GFCI breaker.  I suspect that the disposal is dying after 16+ years.  If I have to remove it to check the wiring, I might as well replace it and hope I get 16 years from the new one.

          Richard

          1. jtee | Jun 20, 2007 08:47pm | #8

            RichardThe fact that the disposer causes a trip with the switch open is very suspicious, unless, of course, the switch is defective. Plugging an appliance into an open (i.e. switch off) circuit should never cause a trip; if it does, something is wrong somewhere other than at the appliance.In a correctly wired circuit with the switch open, current would have to be flowing through the neutral which is (or should be) grounded at the panel, to ground at the disposer. Current doesn't flow without voltage, so one end or the other would have to be energized. I suppose in a poorly grounded panel the neutral could float high enough to cause the trip, but it wouldn't be my first guess. One thing that could cause such a situation is if the circuit were wired with the switch in the neutral instead of the hot (stupid, but it happens). Then there would always be voltage to drive a bit of leakage current in the disposer and cause the GFCI to trip.If you just replace the disposer with one that has less leakage current, you may just be re-masking the underlying problem. I suggest you get a qualified person to check it out.

          2. DanH | Jun 21, 2007 12:14am | #9

            Wrong! A neutral-ground short can cause a GFCI trip, even with the switch off.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          3. edlee | Jun 21, 2007 12:40am | #10

            Yup, I've seen it quite a few times.  Don't know why, but that's how it is.

             

            Ed

          4. jtee | Jun 21, 2007 01:06am | #11

            Only if the neutral (more properly referred to a the "grounded conductor") is at a high enough potential to cause 4-6 mA to flow when grounded at the disposal, since, as I'm sure you know, a GFCI works by detecting a current imbalance of 4 to 6 mA between the hot and neutral. In a normal simple circuit this should not be the case. Of course, all kinds of abnormal situations can and do occur, some dangerous, some not, but, to me, a trip caused by plugging into an open circuit is a situation that warrents a closer look. Better safe than sorry.

          5. User avater
            BillHartmann | Jun 21, 2007 02:29am | #12

            The GFCI has a 2nd sense coil that induces a 120 hz signal and will detect a N to G short without any "external current".http://www.codecheck.com/gfci_principal.htm.
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          6. DanH | Jun 21, 2007 04:14am | #13

            As Bill said, there's a second coil that creates a potential in the neutral line. This causes imbalanced current to flow if there's any downstream short between neutral and ground, even if there's no actual load.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          7. jtee | Jun 21, 2007 04:59am | #14

            I guess I didn't read the original question carefully. I thought the GFCI was a receptacle with a switch was in front of it, in which case there would be no power to drive the circuit that detects a neutral to ground short, but in reviewing the question, he did say GFCI breaker. My bad.

          8. richardi | Jun 27, 2007 08:44pm | #15

            Thank you (and every else) for providing helpful information.

            I justed wanted let you all know that the switched outlet was indeed wired incorrectly!  I replaced both the recepticle and the switch with 20 amp ones since it is a 20 amp circuit with 12/2 romex.  I even marked the 'hot' white wire.

            Now I can tackle the disposal; a Waste King model with a 10-year warranty that was given a favorable recommendation by Consumer Reports. 

            Thanks again one and all...

            Richard

             

          9. jtee | Jun 27, 2007 09:42pm | #16

            Richardi,

            Thanks for "closing the loop" on this issue. So often we never find out if our remarks were on the money or out in left field.

          10. MikeHennessy | Jun 28, 2007 03:47pm | #19

            "I replaced both the recepticle and the switch with 20 amp ones since it is a 20 amp circuit with 12/2 romex."

            Just for future reference, you can put 15A outlets on a 20A circuit if there are more than one outlet on the circuit.

            Mike HennessyPittsburgh, PA

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Custom Built-ins With Job-Site Tools

From building boxes and fitting face frames to installing doors and drawers, these techniques could be used for lots of cabinet projects.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Podcast Episode 691: Replacing Vinyl Siding, Sloping Concrete, and Flat vs. Pitched Roofs
  • FHB Podcast Segment: Roofing on Commercial vs. Residential Buildings
  • Preservation and Renewal for a Classic
  • A Postwar Comeback

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data