Hi All, I have come across a situation I haven’t encountered before.
I need to insulate a ceiling in a western Pennsylvania house. I am planning to use a stone wool product that can give me an R-30 value in the 7 1/4″ deep space I have to work with. Above the ceiling is 1 1/2″ of iso foam with an R-10 value approx. giving me an R-40 value. Epdm rubber is on that.
So, there lies my situation. I am confident that the rubber is a vapor barrier (or better be). Should I still install a barrier on the under side of the ceiling joists? My feeling is that a barrier on both sides of the insulation is a very bad idea. Please share opinions.
Thanks All
Replies
Could you explain that existing roof a little better?
Thanks for caring. The area to be insulated is an addition. The ceiling joists are also the rafters witch are pitched at 1/2" per 12".
It was built this way to support a deck built on parrapets directly above that will accomidate a 2nd floor door 3" above the finished deck.. The walls are 2 x 6 and will have R-19 faced fiberglass insulation. The floor was built with 2 x 8's with a crawl space under it. The space is open to the basement on one side and not vented anywhere else. The floor will also have an R-30 insulation with a vapor barrier placed on the underside of the floor sheathing. BTW the area is about 9' x 14' with 8' walls. I hope this helps. Thanks
I think you are right to question the double vapor barrier. The only thing I would worry about is the moisture from the basement. How wet it is down there?
Any place that sells epdm will also sell "one way" vents to exhaust moisture that could potentially build up in this situation.
I think you need a vapor barrier.
Think about showers, boiling pots, and other sources of water vapor in the conditioned space. That humidity will migrate from the warm interior air into the cooler space beyond the insulation. At some point, the "dew point", it's going to condense and start to drip. During cool months the dew point is bound to be somewhere between the living space and the rubber membrane. Big problems down the road.
Better to install a normal vapor barrier right near the conditioned space to prevent future rot problems.
Absolutley no barrier.
The water vapor must have an escape path. If you put a vapor barrier there is no where the water that gets in there can escape, and the wood will be susceptible to rot.
How does the water get in??
It just does
Water gets into almost everywhere. It is nearly impossible to seal it out entirely.
It is a lot easier to successfully design and construct escape routes, than it is to design something that is truly water proof.