Who knows about backfeeding…..

jrnbj | Posted in General Discussion on October 19, 2006 05:29am

perhaps one of the resident electrical gurus can answer this…
necessity being the mother of invention, I’m back-feeding my panel via a double male end extension cord to the utility outlet at the furnace cut-off switch J-box…
yeah, I know I should have a proper disconnect switch, and no, I’m not running the whole 1/2 of the panel, just the furnace, fridge, & a utility outlet in the kitchen…
I got to wondering if I could back-feed through one of my exterior outlets (so I could use one of my short, heavy gauge cords, and not have to run the longer cord through the abandoned dryer vent where it is now.
Thing is, the outlet is GFI, & I wonder if, the generator being a floating ground, the GFI would trip.
Back of my mind, I also wonder what, if any, risk I have given that, even though the main disconnect is off, when (someday soon, please God!) National Grid gets the juice back on, there is still maybe some common ground path between the service in, the panel, & the generator.
(For anyone about to lecture me….hey, my neighbors have light gauge extension cords strung across the street, in the dark, with pretty frequent car traffic….I figure I’m being safe in comparison)

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. pm22 | Oct 19, 2006 06:09am | #1

    This is totally wrong.

    Please don't do it.

    ~Peter

  2. TomMGTC | Oct 19, 2006 06:16am | #2

    You will probably wish you had not posted this.

    Don't backfeed it. Period. Get a proper switch put in. This is very dangerous for the linemen. Disconnect the furnace fom the panel completely and run it off the generator, run a good duplex cord from the genset to the kitchen to power the fridge and whatever you need the outlet for.

    Tom

    Douglasville, GA

  3. plumbbill | Oct 19, 2006 06:25am | #3

    OK I wasn't gonna say anything,but I can't help myself.

    Every electrical guru in here are gonna ask-----you friggin nutz?

    I know what will work & what ya can get away with---- still wrong & illegal----- so I won't go into that.

    Go to home desperate or blowes & get a panel disconnect---- these are specificly for this application & there not that expensive.

    Or the cheaper route----- put your furnace on a pigtail & run a cord to the kitchen witha splitter on the end of it.

    Cheaper safer & it's only for emergency times right.

    When asked why is there four engines on a 747------ "cause we couldn't fit six" a Boeing engineer

    1. Scott | Oct 19, 2006 07:11am | #4

      This has got to be either a troll or Darwinism unfolding before our eyes....<!----><!----><!---->

      <!----> <!---->

      Neither is pleasant; both can be instructional.

       

      Please prove us wrong, Mr. J.

      <!----> <!---->

      Scott.

       

      Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

      Edited 10/19/2006 12:15 am by Scott

      1. jrnbj | Oct 19, 2006 07:33pm | #11

        Those who can't improvise, freeze.......

        1. TomMGTC | Oct 19, 2006 07:57pm | #15

          It really ain't that hard to pigtail the furnace and run a cord to the kitchen.Tom

          Douglasville, GA

  4. User avater
    maddog3 | Oct 19, 2006 01:01pm | #5

    go here...
    http://forums.taunton.com/tp-breaktime/messages?msg=68066.1

    ...it may help.....I hope !!

    Square D makes an interlocked breaker KIT for their QO panels and Homeline

    http://www.squared.com/us/applications/residential.nsf/unid/FD8CBE7A9E1445D085256D1A00538807/$file/GenIntKit.pdf

    .

    .

    .

    .Wer ist jetzt der Idiot

    ?

    1. jrnbj | Oct 19, 2006 07:30pm | #9

      Thanks for the interlocked breaker info..
      everyone else, get a grip.....
      The men trying to clear out the mess left by years of numbskull home-owners letting anything & everything grow up into the lines around here said, and I quote, we might come & pull your meter base, but for now, be sure you keep the panel main off....
      I am no longer amazed at how some of the people on this board let their urge to be know-it-alls interfere with common sense.....of course what I'm doing is not the correct way to do it, and when the situation clears up here, I'll set it up with all the bells & whistles...
      for the meantime, I've got power & heat, it's safe enough for temporary.....I guess all the other posters would let there wife & kids freeze & go hungry instead...sheesh

      1. User avater
        BillHartmann | Oct 19, 2006 07:50pm | #13

        Common sense also includes such time has considering what happens if some some trips over the cord and pulls out the hot male end.Or the power is restored and someone closes the main breaker in the excitement without disconnecting the generator. Or realizes that they need to disconnect the generator, but starts with the male end.And that person might be your wife or older children. Or the furnace stops in the night because the generator ran out of gas. Wife kicks you out of bed and you are still 2/3 asleep. So you try the main breaker first and leave it closed. Then realize that the generator is not run and you refill it and start it.

        1. jrnbj | Oct 19, 2006 08:11pm | #17

          Common sense also includes such time has considering what happens if some some trips over the cord and pulls out the hot male end.....Cord's not run were anyone's gonna trip over it...Or the power is restored and someone closes the main breaker in the excitement without disconnecting the generator. Or realizes that they need to disconnect the generator, but starts with the male end....If "someone" is in my house messing with this besides me, I hope they get a good shock....And that person might be your wife or older children.Nope...they're well trainedOr the furnace stops in the night because the generator ran out of gas. Wife kicks you out of bed and you are still 2/3 asleep. So you try the main breaker first and leave it closed. Then realize that the generator is not run and you refill it and start it...Nope...unlike my neighbors, who run a 5000W generator 24/7, keeping the rest of us up at night, we shut down overnight.....

        2. User avater
          carloa007 | Oct 19, 2006 08:18pm | #18

          In your situation, I would probably do the same thing. Obviously its not ideal, and your well aware of that, so no need to beat a dead horse.

          I wouldnt go through the GFI outlets as any fluctuation by the generator will probably cause them to trip.

          Personally, I would tape off the main, ( and not a little piece of scotch tape) a serious piece of tape that must be removed in order to actually move the breaker, with a note DO NOT TOUCH

          I would backfeed 220 from generator through an electric dryer or other 220 outlet. Turn off all the breakers you dont need. And check that the ones you do, dont get too close to the amp rating on the generator.

          Good luck. Hope you get your power back soon.

      2. JohnSprung | Oct 19, 2006 10:54pm | #29

        > .....I guess all the other posters would let there wife & kids freeze & go hungry instead...sheesh

        No.  I'd run extension cords from the jenny to the essential loads.  Furnaces here are all plug-in, not hard wired.   

         

        -- J.S.

         

      3. brownbagg | Oct 19, 2006 11:38pm | #31

        I guess all the other posters would let there wife & kids freeze & go hungry instead...sheeshwhile you dont need it, go get the coreect lockout switch so you can have it safe when the next power failure.

        1. sledgehammer | Oct 20, 2006 12:19am | #32

          Surprised no one mentioned the neutrals potential on a poorly grounded system.

          Plenty of white wires have killed the uneducated.

      4. renosteinke | Oct 20, 2006 07:54am | #36

        Do not let you passion overrule your good sense. There is a lot of good reason- based upon bad experience- that put "lie" to all those clever handy man things- things like double male end cords for backfeeding. If you've pulled the meter, and cut your feed wires.... then, by all means, connect directly to your panel. I would suggest doing it correctly, though. As in, bigger wire, connected directly to the feed lugs of the panel. Your generator makes electricity. The Power Company makes electricity. That's all they have in common. There is no way for your generator to be making power at exactly the same volts, hertz, and in time with the PoCo generator. If it is possible for these two different "flavors" to meet each other, they will. The results are usually quite spectacular- either your panel explodes, sending molten metal and shrapnel everywhere.... or your generator does. That little breaker on the generator isn't going to impress the PoCo one bit. How do you keep this from happening? Very simple: USE A TRANSFER SWITCH. These things are proven designs, that keep the two from ever meeting.... while allowing for a smooth changeover from one to the other. The risk to line personnel is very real. Linemen do get hurt, or killed, every year ... by folks doing just what you propose. Should that happen, you can expect felony charges to be placed. This is one time where you need to consider that, just maybe, you're heading down the wrong path.

        1. DanH | Oct 20, 2006 01:50pm | #39

          "There is no way for your generator to be making power at exactly the same volts, hertz, and in time with the PoCo generator. If it is possible for these two different "flavors" to meet each other, they will. The results are usually quite spectacular- either your panel explodes, sending molten metal and shrapnel everywhere.... or your generator does. That little breaker on the generator isn't going to impress the PoCo one bit."Actually, if you're extraordinarily lucky the two generators will "sync up" and everything will be happy. Not something you should count on.And, of course the (much) bigger danger is that you'll accidentally back-feed the power line, creating a hazard for the linemen. Despite the fact that it's "perfectly safe if you know what you're doing", linemen die due to this. All it takes is one "aw sh!t".
          If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          1. gtmtnbiker | Oct 20, 2006 09:27pm | #51

            I totally agree that one should use a transfer switch but shouldn't linemen take proper precautions to use insulated tools & gloves, etc. Since the risk of backfeeding is always present, they should work as if the line is always live.

            I take similar precautions when working on my own house even though the main breaker off.  I always work as if the wire is still live.

          2. DanH | Oct 20, 2006 09:57pm | #52

            So you never touch a bare wire?What I suspect you mean is that you always check the voltage on the circuit, and, maybe to be doubly sure, short hot to ground and watch for a spark (and the sound of the breaker tripping).Linemen will do much the same, I suspect, and will usually short all the lines together while working on them. But there are always the exceptional cases: They check but then the wire becomes hot a few seconds later; a grounding wire isn't making good contact; or, just like anyone, they screw up.And it's not even a hazard limited to the linemen. For instance, your neighbor's drop broke loose from the pole in an ice storm and is laying across your driveway. It's clearly disconnected, so you pick it up, only to discover that your neighbor has a genset he's backfeeding.

            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          3. sledgehammer | Oct 21, 2006 01:17am | #56

            Why yes, linemen do test the line... but what if he's testing it while you're gassing up the generator?

            Horrible accidents are usually a result of multiple stupid errors that happen in sequences that can't be imagined.... and no mater what, dead is dead.

             

             

          4. jrnbj | Oct 21, 2006 01:29am | #57

            you mean I should turn off the generator to gas it ;-)Point taken about multiple errors leading to catastrophe...seems it takes teamwork to screw up big time....

          5. gtmtnbiker | Oct 24, 2006 04:49am | #61

            I wasn't referring to linemen testing the lines and then working on them as if they had no power. I'm referring to them working as if the lines were live by using insulated gloves & tools and etc.

             

        2. brownbagg | Oct 20, 2006 02:10pm | #41

          this one aint hard. nobody complaining about backfeeding, just get a tranfer switch, thats all, dont mess with the meter. power co will put in jail for that. Just get a transfer switch, simple. and then backfeed all you want.

    2. jrnbj | Oct 19, 2006 08:19pm | #19

      Just curious, what is an interlocked breaker....(if it sees back feed, it locks out?)
      And, on a similar note, what's the difference between a panel disconnect switch and the main 150A breaker at the panel feedOther than having a lockout tag capability, isn't the panel main acting as a disconnect?BTW, for those of you who are sure I am dangerous to myself & others, I learned a healthy respect for electrical systems working on an old passenger liner with an 8 foot tall by 15foof wide DC distribution panel....whose sole safety feature was a grab rail at waist level in front it
      Lots of big knife switches, threw nice arcs in operation....DC 'll fry you fast...

      1. User avater
        BillHartmann | Oct 19, 2006 08:31pm | #20

        It is not an interlock breaker.But rather separate device that interlocks to breakers. It is a mechanical device that will only allow one of two different breakers to be closed at once.I am not sure what all types are available. But I think that typically they are not used with a separate main breaker. But with a backfeed breaker to the bus with the 2nd breaekr directly oposite. BTW, backfeed main breakers and the backfeed generator breakers also need special kits that have hold downs on them to get the breaker from being removed or working lose."And, on a similar note, what's the difference between a panel disconnect switch and the main 150A breaker at the panel feed"I am not sure of the context.The service entrance to the house has to have two features. A method of disconnecting power to the house and overload protection. In many cases that is one device and it is the main breaker in the panel.But in some installations the main disconnect is on the outside by the meter. In that case typically a breaker is used for both the switch and overload. But in some cases a plain switch is used along with fuses.

      2. Stuart | Oct 19, 2006 08:36pm | #21

        "Just curious, what is an interlocked breaker....(if it sees back feed, it locks out?)"

        It's actually two circuit breakers, one for the main and one for the generator, that are mechanically interlocked so that only one can be energized at a time.

        To the original poster: I agree with all the others...sure, backfeeding has been done many times before and no one got hurt, but that doesn't mean it's safe or legal.  For us electrical types here on the board, it would be foolish (and a big violation of our professional ethics) to even suggest otherwise.

        1. brownbagg | Oct 19, 2006 09:19pm | #23

          backfeeding has been done many times before and no one got hurt, but thatthree power guy got killed during katrina from generator backfeed. people die every year because of this.

          1. jrnbj | Oct 19, 2006 09:25pm | #26

            yep, but I'm not responsible for that......

        2. jrnbj | Oct 19, 2006 09:20pm | #24

          Well, being the original poster, I am in agreement with you...it's not something I'd expect anyone to OK....I understand that.It's a bit like my gas stove....when the power goes out, it locks out, because it has Pizeo-electric ignition, & some lawyer decided the risk from someone turning the gas on without being smart enough to LIGHT A MATCH was too much....
          God save us from the people who try to keep us idiot proof.....those are the folks messing with Darwins' mechanism for keeping the species healthy.....It's kind of hard to buy an interlocked breaker when HD is in the dark like everyone else....

          1. User avater
            BillHartmann | Oct 19, 2006 09:28pm | #27

            "t's kind of hard to buy an interlocked breaker when HD is in the dark like everyone else..."I doubt that they have them.Might even be special order at the electrical supply houses.And again it is not an interlocked breaker. But an interlock to add to breakers.

            Edited 10/19/2006 2:32 pm by BillHartmann

          2. FrankDuVal | Oct 20, 2006 05:56am | #35

            True, but here your attempt at being a Darwin Award recepient will be the death of innocent people (linemen) and not the proper recipient of the award!Fewer linemen means longer time to restore your power....Frank DuVal You can never make something foolproof because fools are so ingenious.

          3. 43Billh | Oct 20, 2006 01:19pm | #38

            God save us from the people who try to keep us idiot proof.....those are the folks messing with Darwins' mechanism for keeping the species healthy.....

            THANK YOU!   THANK YOU!    THANK YOU!

            Yeah, backfeeding is dangerous and I would NEVER recommend it.

             And if my family was cold / hungry / dirty with no relief in site I would back feed my house with a generator!

             Does that make me an idiot? You decide.

              I have a plan in place for just that type of situation. As for me, I'll pull the meter and beg forgiveness when things are back to normal. My house will be warm and I won't kill a lineman.

            jrnbi makes a decent point about idiot proof and keeping the species healthy.....

            Some people don't even want kids to play tag any more!

            Considering Less that ideal conditions

            I would be willing to bet quite a few of you guys would do what was necessary to keep your family comfortable.

             

      3. User avater
        Dinosaur | Oct 19, 2006 09:11pm | #22

        Bro--

        If your main breaker isn't equipped with lock-out tabs for a padlock (many are), why don't you just physically pull the main breaker right out of the service panel? Seems to me that should isolate your gen-powered system from the network completely and prevent any impetuous or unconsidered re-connection.

        (You could also remove the meter yourself, although you'd likely have to explain to the power company later why their seal is missing....)

        PS--Shut down/disconnect your generator before you do either or both of the above, of course...and get a woodstove for next time.Dinosaur

        How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

        1. jrnbj | Oct 19, 2006 09:24pm | #25

          Hey, good to hear from you....haven't tuned in to your situation with the boy for some time...hope it's going as well as possible...I'd pull the main breaker, but while I don't mind installing breakers with the main off, I wouldn't be installing the 150A main with the feeds hot....contrary to what some folks might think, I do know when to call in the real electricians...Were you hit by the ice storm in Quebec a few years back?

          1. User avater
            Dinosaur | Oct 19, 2006 10:11pm | #28

            Were you hit by the ice storm in Quebec a few years back?

            Yes, we were: No power for 4 days, and we only got it back then because we had an 'inside connection'--my bud is a Hydro-Québec linesman, and he twisted his dispatcher's arm to bump our sector up the priority list a bit seeing as my wife was pregnant at the time. Many areas waited 2 weeks; some on the South Shore went for 7 weeks.

            This house runs quite acceptably for up to a week with no electrical power. There are a few things I'd add to the infrastructure in order to weather a longer haul, though, one of which is a small propane heater for the basement (the woodstove is on the main floor and there's no easy way to circulate the warm air downstairs).

             

            As for putting your 150A breaker back in once the power comes back on, do it before you plug the meter back in. Seems to me that plugging in the meter while the circuit is live should be less hair-raising as it's designed for that.

             Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

          2. User avater
            BillHartmann | Oct 19, 2006 10:57pm | #30

            The meter is not really designed to be a switch.You want to make sure that the main breaker is off when replacing it.

          3. User avater
            Dinosaur | Oct 20, 2006 06:40pm | #48

            The meter is not really designed to be a switch.

            You want to make sure that the main breaker is off when replacing it.

            A good point, Bill. I have a Snap-on screwdriver around here somewhere with a nice notch burned into the shaft which testifies to the truth of that....

             

            Obviously, the simplest solution to isolating the house from the grid would be if J's main breaker had lock-out ring tabs on it, so he could physically padlock it in the off position. My ITC box has that; all commercial stuff I've seen have it too.Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

          4. jrnbj | Oct 20, 2006 06:45pm | #49

            I haven't looked, but in my old neck of the woods, the Power Co. had a tamper tag on the meter.....

          5. User avater
            Dinosaur | Oct 20, 2006 06:52pm | #50

            Yeah, they would likely have that, which would mean explanations at some later date. Could cost ya if they decided not to believe your explanation, too. Not real good....

             

            You sure you don't have lock-out tabs on that breaker? Or some way to padlock the panel shut with the main breaker thrown to the off position?  That would eliminate the likelihood of somebody throwing it back on without thinking.Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

          6. jrnbj | Oct 20, 2006 11:31pm | #54

            Just came back inside....it finally stopped raining enough to go out & cut up the 100 year old apple tree into smoker wood....sigh. My 6 yr. old daughter was helping me (no, I don't let her use the chain saw ;-) ) until she got too sad...it was her favorite climbing tree.
            Good idea re locking cover, but no such luck it's a Siemens main, no padlock hasp....too bad
            Things get back to normal, I'll see about getting a manual transfer switch...can't spring for much more right now, the wife just got laid off, & I don't have any hotel work lined up this fall....it's looking like winter'll be tough this year...Mom's got stage four cancer, daughters'
            diabetes doc got accused of child molestation by a teen psych patient who's been stalking him, throwing 400 families who depend on the doc into turmoil....hope all the crap that can happen, has, cause I've had enough for now....

          7. User avater
            Dinosaur | Oct 21, 2006 12:00am | #55

            ....hope all the crap that can happen, has, cause I've had enough for now....

             

            I say that every morning, bro. What a friggin' life it can be sometimes....

             

            Hang tough. I'll look around here in the reclaimed electrical parts and see what I can turn up. I don't remember scoring a gen-set switch, but ya never know. There's all kinds o' crap in those crates....

            In the meantime, be effin' careful and use LOTS o' duct tape in multiple layers....Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

      4. User avater
        maddog3 | Oct 20, 2006 10:05am | #37

        ..." what is an interlocked breaker...."I would just re-iterate what others have said. it's merely a mechanical linkage between two opposing breakers.... If I understand your other question, yes , the panel main is a disconnect, but of course you are aware that breakers do not like being opened under load, .

        .

        .

        .Wer ist jetzt der Idiot

        ?

        1. brownbagg | Oct 20, 2006 02:06pm | #40

          yes , the panel main is a disconnect,
          But also what if somebody hooks the generator wrong, send voltage up the netrual instead. breaker wont help then, It does happen, daily.

          1. DanH | Oct 20, 2006 05:17pm | #42

            You can't really send juice back on the neutral, unless there's a major problem with the PoCo's stuff. At your service entrance and again at the pole, the neutral is tied to ground. You'll simply burn out the generator.

            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          2. Notchman | Oct 20, 2006 06:06pm | #43

            That's assuming the wiring is correct throughout the house.

            More than once, on remodels, where HO's have fiddled with the wiring, or added circuits, or replaced devices, I've found hots and neutrals are on the wrong sides on recepticals......here and there.

          3. DanH | Oct 20, 2006 06:10pm | #44

            But how would that cause problems out on the hi line, if the main breaker is disconnected?
            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          4. Notchman | Oct 20, 2006 06:12pm | #45

            It wouldn't.  I'm just pointing out that, sometimes, those neutrals are hot. (and the "hots" are not).

          5. Notchman | Oct 20, 2006 06:22pm | #46

            And I want to raise another issue that, if I hadn't seen it recently, I wouldn't even bring it up:

            I was doing a remodel in an older home last year that required some rewiring in an attic that we were converting to a studio.

            The electrician I had doing the wiring upgrade suggested we replace the meter box because it was old and showed signed of corrosion.  So I had him do that.

            A couple of weeks later, we started getting a trip on the 200A main in the house panel. Usually it was when the HO was cooking or running the clothes dryer or something.

            Yet lights would still be on in the basement....turns out the main breaker was bad and was bleeding through even when "off."

            Now, wouldn't that be a nice situation to be backfeeding a generator into?

             

          6. DanH | Oct 20, 2006 06:38pm | #47

            Of course, that scenario could occur with a proper transfer switch too.
            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          7. User avater
            maddog3 | Oct 21, 2006 04:21am | #58

            ...good point,

            I'm not the one hooking this up, and have not promoted his way of doing it ......and I think he knows that.

            .

            .

            .Wer ist jetzt der Idiot

            ?

  5. DanH | Oct 19, 2006 01:16pm | #6

    Why not get a start on doing it right? Install the outside connection you'd need for a transfer switch, even if you don't do the rest just yet.

    I'm pretty sure that backfeeding through a GFCI would have a high probability of tripping the GFCI, and the repeated tripping would be hard on the genset.

    For now put tape over the main breaker, with a sign saying "Don't turn on!!" Otherwise, when you're not there, some "friend" might turn it on for you (or you might do it in a sleep-deprived daze).

    If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison
    1. jrnbj | Oct 19, 2006 07:45pm | #12

      Good idea about the tape.....no one goes near the panel but me, & my friends are at least as bright as I am, but it's an extra safety measure until I can get a true disconnect in, instead of relying on the panel main breaker

  6. brownbagg | Oct 19, 2006 01:58pm | #7

    by backfeeding, you just killed a power company employee, working on the lines.

    1. jrnbj | Oct 19, 2006 07:31pm | #10

      No, the main at the panel's off....

  7. Sasquatch | Oct 19, 2006 04:44pm | #8

    Stupidity being the mother of death... Don't do it.

    double male end extension cord - bad idea anytime!

    I know I should have a proper disconnect switch - There's your answer, so you're not stupid, just not thinking it through.

    I got to wondering if I could back-feed - I wonder if, the generator being a floating ground - I wonder if, the generator being a floating ground...  Anybody doing this much wondering should consult a licensed electrician.

    there is still maybe some common ground path between the service in, the panel, & the generator...  That maybe could kill someone.

  8. User avater
    rjw | Oct 19, 2006 07:53pm | #14

    >>I figure I'm being safe in comparison

    Sorry, you've got them beat hands down for high risk.

    BTW, I teach a course in risk analysis for real estate agents and home inspectors.

    May I come over and take some pictures?

    Please leave the door unlatched, you might not be able to answer it by the time I get there.

    You might want to be sure everyone in the family can remeber these numbers:

    9
    1
    1


    Youth and Enthusiasm Are No Match

    For Age and Treachery

  9. BarryO | Oct 19, 2006 07:57pm | #16

    hey, my neighbors have light gauge extension cords strung across the street, in the dark, with pretty frequent car traffic....I figure I'm being safe in comparison

    But your neighbor hasn't set up conditions where a POCO worker may get killed one day.  If the Service Disconnect is ever inadvertantly switched on, you end up backfeeding the transformer, which puts HV on its input terminal.

    Set up a "foolproof" switch or interlocked breaker.  Otherwise, if a "worst case" situation does happen, you're probably going to jail.  'happened here in Oregon a few years ago, when a firefighter got killed from a blaze that was started by a non-permitted furnace.

  10. Geoffrey | Oct 20, 2006 03:40am | #33

    ANYONE who is as positive about their ability to never slip up, as you are, is just an accident WAITING to happen, you just never know when! My condolences to your wife and kids!!

                                       Geoff

    1. Notchman | Oct 20, 2006 04:30am | #34

      I've lived most of my life in relatively remote rural areas, where power outages are not uncommon several times in a winter....from a few hours to several days.

      I have a decent genset now, with transfer switch, but most of my life (nearly 60, counting childhood), we survived without a generator.

      But, regardless of where you live, you should have some kind of an emergency plan to provide for the problems with isolation from the electrical grid, a water system, refrigeration, heat, etc.  That means storable food, jugs of water, kerosene lamps and flashlights w/extra batteries, a propane stove or a barbeque unit for cooking and heating water, extra clothes and blankets, etc. (ven Manhatten, NYC has had power outages).

      This doesn't mean you have to be a member of LDS or a survivalist....a basic set up for being isolated in an emergency for even a month will take up very little room and won't cost a great deal.  You seem to be responsible about training your family, so getting them up to speed on how to safely use and care for survival equipment is pretty straightforward.

      If you want to run a generator on the cheap for refrigeration, lights and whatever else floats your boat, you can accomplish that with a pigtail from the generator, with the output side of the pigtail sporting a receptical box for 115V and/or 220 into which you can plug in and energize individual appliances.

      But, for us knuckle dragger country bumpkins, the dangers of backfeeding with a generator were explained to us before I was even in High School.

      If you're committed to the generator back-up, I suggest you hire an electrical contractor and have a full house backup genset and emergency panel installed in your home.

      I've built several rural custom homes in the last few years that had 13K backup generators installed.....generators are much less expensive than they were just a few years ago and a good 11k or 13K unit with an Onan or Honda engine is pretty affordable.  Cost of installation will, of course, vary with the configuration of your electrical service and distribution, but it may be an desireable alternative to getting someone hurt or killed.

       

    2. jrnbj | Oct 20, 2006 11:15pm | #53

      And you are living proof of the well known fact that people are notoriously unable to clearly analyze risk/reward situations...
      I'm not fool-proof, but I've spent 30 years in the trades with nary an accident.....and plan to keep that record going for the next 30

      1. Geoffrey | Oct 21, 2006 04:38am | #59

        I wish you the best of luck at that!  only problem is you are doing something you KNOW is dangerous and wrong!!.... and the ones with the most to lose are not in the decision making loop! (your family and the other outside potential victim(s) like a linesman)

                              Geoff

        1. jrnbj | Oct 21, 2006 07:27pm | #60

          My family is in the loop, as is the lineman-read through the thread to see his comment....
          I don't KNOW it's either dangerous or wrong...
          it would be dangerous if I had no idea what I was doing....
          it would be wrong if I did it because I couldn't pay my electric bill, and if I don't prepare better for next time

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Guest Suite With a Garden House

This 654-sq.-ft. ADU combines vaulted ceilings, reclaimed materials, and efficient design, offering a flexible guest suite and home office above a new garage.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump
  • Insulation for Homes in the Wildland Urban Interface
  • An Impressive Air-to-Water Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data