Who owns the wires in the meter box?

| Posted in General Discussion on June 1, 2008 02:28am

Yesterday I replaced the breaker panel in my goddaughter’s house.  I pulled the meter and opened up the meter box to tie in the temporary power lines and found a surprise. 

The wires from the transformer come in through a buried conduit and terminate in the box in a set of lugs.  The two hots show heat damage and the neutral is out of the lug completely, but still resting against it. 

I wasn’t touching that side of the box, and had a good day’s work ahead of me, so I decided to not mention it until my work was done.  When I was done replacing the breaker panel I told her what I had seen in the meter box and we discussed how to get it fixed.  If we knew for sure that Exelon was responsible for those connections we would have called them and had them take care of it right away.  But, if she is responsible for those connections we didn’t want to pay the Saturday evening emergency rate for the repair. 

In case it matters, we’re in Pennsylvania.

Thanks!

Doug

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. VAVince | Jun 01, 2008 02:37pm | #1

    Call the power Co. NOW

  2. Oak River Mike | Jun 01, 2008 02:47pm | #2

    I agree with VAVince.  Call the power company.  I might he hesitant to tell them YOU pulled the meter as around here they get upset with folks for doing that as we have alot of folks do it to steal electricity.

    But call them to have that issue looked at.

  3. DanH | Jun 01, 2008 02:51pm | #3

    For overhead service in some cases the HO owns the wires to the top of the mast. (In other cases the PC owns the wires all the way to the breaker panel.) Hard to see how the PC doesn't own the wires in question in this case, though.

    It is an ironic habit of human beings to run faster when we have lost our way. --Rollo May
    1. User avater
      BillHartmann | Jun 01, 2008 04:44pm | #4

      And in somecase you provide the PVC and the POCO will do the wires.In other you provide the PVC and pull the wires and maintace is up to you. And in other after installed the POCO will maintain them. The last 2 are probably more likely on runs past their standard service distances.There are all kinds of combinations.But no matter who is responsible the wires the POCO will end up comming out anyway as they need to shut off the power..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      1. diydude | Jun 01, 2008 05:56pm | #5

        All,

        Thanks for the advice so far.  She and I have discussed telling Exelon how she was sitting on the deck today (it's a beautiful day by the way) and how she heard sizzling and smelled something funny around that corner of the house, and that the meter box was warm.  I told her that kind of call will get them out within an hour. 

        -Doug

        1. Davo304 | Jun 02, 2008 06:15am | #15

          I reside in the Northern Panhandle of West Virginia. Allegheny Power is our provider.

          They provide you free of charge with the meter box and socket. I am responsible for installing the wires up to the weatherhead and they make the connection. I am 100% responsible for the feed from the lugs running to my panel box inside my house.

          Typically, you contact the power company and set up an appointment. They arrive and disconnect the power at the weatherhead  drip loop. You pick up a new meter box and socket at a local electric supply store after giving them a confirmation number that the power company assigned you. You then go ahead and run your new wiring up the mast , and/or into a new panel box or whatever you had planned to do.

          An power co inspector will come by later that day to inspect whether your wiring meets their codes (2 ground rods, certain box height requirements, etc). They do not inspect the actual wiring in the homeowner's panel box...just the wiring from the meter to the box, and the wiring up the mast.  Most will ask to check out the panel box, and I always let them...but they will tell you straight forward that their responsiblity ends with the main lug connections, and they have no real authority to inspect actual wiring of circuit breakers.

           Once the inspector is satisfied....and after  having to pay the inspector $150 for the visit, they will tag the meter box with a decal sticker that lets the linemen know they can re-hook up the service . The lineman arrives later that same day and then re-hooks the power, plus he/she installs the actual meter back in place, closes the box and installs a special metal tag plate ( seal).

          If you knowingly cut that seal to work on the meter box yourself, and are caught doing so...that's a $10,000 fine in our area.

           

          Davo

           

  4. alwaysoverbudget | Jun 01, 2008 05:59pm | #6

    around here the meter box is the homeowners problem. i know i just paid 600 for a new meter socket  that had corroded. larry

    if a man speaks in the forest,and there's not a woman to hear him,is he still wrong?

    1. DanT | Jun 01, 2008 06:14pm | #7

      We deal with 2 different power companies in my area and in both cases you own it to the mast above ground and to the pole below ground.  Meter box too.  DanT

    2. Clewless1 | Jun 01, 2008 07:03pm | #9

      You usually own the meter BOX ... but the wires may be the power company's problem (and responsibility). If it is underground service ... the power company usually pulls the wire and makes the connection ... making the connection their responsibility, I think.

      I'm no electrician, though ... just a wannabe

      1. brownbagg | Jun 01, 2008 07:50pm | #10

        here the power company gives you the meter box, they own up to meter and you take over from meter to house. except doing storm damage it stop at the mass

        1. diydude | Jun 01, 2008 08:28pm | #11

          If nothing else, it's interesting to read where the different utilities around the country place the line of demarcation. 

          -Doug

  5. renosteinke | Jun 01, 2008 06:48pm | #8

    YOU pulled the meter? Who broke the seal?

    PoCo can handle this. In many places, this connection is also made by the electrical contractor.

    Either way - get it fixed NOW. Doing without power is not unreasonable. Especially with that neutral loose, you are at a very real risk of damaging electrical appliances,

  6. BilljustBill | Jun 01, 2008 09:40pm | #12

    In the past, you could break the seal on the meter as long as you called them when you were finished.

    Now, they have a "Fine" of over $100 for doing that.  You have to call AHEAD of breaking the seal to prevent the fine.

    Severak months ago, I was operating under the old rules and called them to tell about a disconnect by pulling the meter.  The lady was nice, but bordered on getting huffy.   I finished the work and was telling them I broke the seal.  She said, "Well, this time there won't be a fine, but...." 

      Funny how it was such a big problem, but with those new radio frequency meters that let the meter readers come by the house and read the meter from 150' away, the broken seal has never been replaced....

       Get those loose connections fix ASAP....;>)

      Bill

  7. User avater
    IMERC | Jun 02, 2008 01:48am | #13

    poer company...

     

    Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming

    WOW!!! What a Ride!
    Forget the primal scream, just ROAR!!!

  8. User avater
    Haystax | Jun 02, 2008 05:29am | #14

    In my experience the homeowner provides the meter box, conduit, weatherhead and wire and the power company will hang the loop from the pole and install the meter, usually they will replace or repair the meter loop wires if there is ever a problem from the transformer to the meter itself. It is always a good idea to install provide a little more wire than necessary in a new install and loop the extra couple of feet of wire in the box in case of future repair from lightning of burned conductors/claws

    In underground installations, the power company will usually provide at a substantial cost the service wires to the meter if it is mounted on the side of the home or at a transformer base close to the home and then you are on your own from there. From the meter to the residence or point of use is referred to as "secondary" and you are responsible for installation and maintenance. It is possible to adjust the "taps" in order to bump voltage to account for line loss in the secondary line but not all utilities go for this and you end up with a lot of line loss and pay for power you don't really use as a result.

  9. User avater
    IMERC | Jun 02, 2008 08:55am | #16

    should have said....

    wires in... power company....

    wires out... the HO...

    some power companies stop at the weatherhead...

     

    Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming

    WOW!!! What a Ride!
    Forget the primal scream, just ROAR!!!

    1. DaveRicheson | Jun 02, 2008 12:59pm | #17

      Doesn't make much differance who owns what.

      The POCO still needs to be called for the corrective measures need at the meter base.

      They need to pull the fuse link at the transformer, so the fix can be completed while it is dead.

      Anyone working it hot needs to comply with NFPA 70E, including the POCO.

      1. User avater
        IMERC | Jun 02, 2008 09:19pm | #18

        that's tellin me... 

        Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

        WOW!!! What a Ride!Forget the primal scream, just ROAR!!!

        1. RobWes | Jun 02, 2008 11:58pm | #19

          Well for another twist...

          Power Co owns it if the HO wants a utility owned service. In this case they own to the meter but your (I was) responsible to the weatherhead and for it's replacement when it was ripped down by a large tree.

          In my new house (same power co.) I chose a customer owned feed. They own the transformer and the pole at the end of the drive 345 feet away. I own the from the connections (including the Burndies) down the pole, all pipe, sweeps, and wire, meter socket and 6X6 posts to the last outlet in the house. It was much faster and cheaper than waiting for them to design and build.

           They didn't even inspect the trench. The local tech said if I wanted a substandard job it was going to be my own fault. When they energized it, all the pole crew wanted was the main shut off. They did look at my install and he admitted he never saw anything like it and walked away. That's a no bs story.

          1. jrnbj | Jun 03, 2008 12:13am | #20

            "They did look at my install and he admitted he never saw anything like it and walked away. That's a no bs story."Ahhh, you're gonna leave us hanging here, then?

          2. User avater
            IMERC | Jun 03, 2008 01:08am | #21

            we can take that at least two ways....

            lets take the more fun way... 

            Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

            WOW!!! What a Ride!Forget the primal scream, just ROAR!!!

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels

Listeners write in about fireplaces and ask questions about sharpening hand tools, easier wiring upgrades, and fixing cedar siding.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels
  • FHB Podcast Segment: Hand Tool Sharpening Tips
  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data