Guys,
I’m building an outdoor kitchen island which will sit on my deck. The island will be enclosed. I plan two 20Amp circuits — one circuit for the receptacles feeding the appliances (just grill ignition, lights and small refrigerator) and one circuit for the two open receptacles. I was going to use a single run of 12/3 wire. The wire will run under the deck and up into the island from below. Someone suggested the wire should be run through NM flexible conduit once it enters the island to protect it. I’m happy to do so if anyone feels it is necessary.
I’ve never wired an outdoor kitchen so any thoughts would be appreciated.
Thanks
Frank R.
Replies
What sort of GFCI protection are you planning?
Zackly what Dan asked.
12/3 sounds fine. As for protection, you could use BX (aromored) wire; or just slip flex armor over NMD where mechanical injury is a concern. (Don't forget your anti-short bushings at box connections)
For outdoors it seems like it would be better to use UF.
Yeah, I suppose. Seems like
Yeah, I agree. Seems like he's mostly concerned about mechanical injury, but there could be moisture issues too, so I'd agree that UL + Flex would be the ultimate solution.
Perfect - Thanks
Guys,
Perfect. I'll use UF in the flex. None of the appliances are hardwired, so I was just going to use GFCI receptacles all around because they are all accessible (through the access doors) and I don't want anyone trying to get to the breaker panel to reset a GFI breaker. I realize a small fridge will be on the GFI circuit -which is not the best for false trips -- but it is outdoors so I need the protection.
Thanks again everyone.
It would be nice if someone would chime in with any specific code requirements for such a layout. (My code book is about 25 years old and so out of date I won't even bother checking it.) At the very least you should make sure any metal framing or other major metal structure is well-grounded.
The code issues are pretty easy. He needs GFCI protected receptacles that are weather resistant, in use covers and the wire needs to be wet location rated. I think I would use 3/4" PVC (rigid) conduit to protect the wire and pull THWN. That gives you flexibility if you need something else later. It might be best to come up into a 4x4 J box inside the island and use dead front GFCIs in there so they are out of the weather and tail your receptacles off if them.
Help yourself and stop using the "K" word. This is a wet bar, not a kitchen. Then you can use one of the circuis for lights.
A kitchen requires 2 dedicated circuits serving the countertop but you could pick up a fridge and a stove igniter, just no lights.
>>>This is a wet bar, not a
>>>This is a wet bar, not a kitchen.
Hahaha....good idea. Heck, call it a culinary arts studio.
Thanks and one last question
Dan,
Thanks. Your plan sounds perfect. (Junction box to PVC conduit). One last question. The framing directly under/around the grill is metal -- the rest is PT lumber. Do I need to ground the framing under the grill or is that overkill if all of the receptacles/appliances are properly grounded? If so, can I just attach a metal box to part of the steel frame and ground the box?Any thoughts?
Thanks Dan.
FR
Hello,
I am building a outdoor kitchen island with metal studs. My question is a 2 part electrical one. I had some 12/2 UF-B wire left over that I am using. It will be wired to a 40 amp GFCI subpanel. The attached photo shows how I am running the wire, is this OK? If this works, what kind of electrical boxes will I need? Can I just use plastic one? I see a lot of videos that they just use MC and metal boxes for out door islands.
Thanks